Anyone else having a hard time getting a hold of warranty replacements from
Schneider for the Xantrex GT series inverters?
What are they doing as far as warranty replacements? Waiting for bad ones
to come in so that they can fix them and send them out again?
I've got a customer who has bee
double-insulated tools in the U.S. that do
not require a ground wire.
Bill.
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Marco
Mangelsdorf
Sent: Friday, October 01, 2010 11:09 AM
To: 'RE-wrenches'
Subject: [R
Bill B. wrote the following:
Ungrounding the array requires additional fusing and disconnects, but the most
significant difference is that the module wiring and all external cable must be
PV Wire/Cable. Therefore only modules with PV Wire/Cable can be used in these
systems. You must confirm
I'm looking for an old (as in late 1990s vintage) PM-60 48V charge
controller, the kind that Pulse/Connect Energy used in their PC 250 load
center.
Please to contact me off-list if you might have one in good working order
lying around somewhere.
Thanks,
marco
_
A 30-year-old PV installer fell to his death back in April at job site in
CA. He backed off of a roof accidentally and was not wearing any fall
protection.
I have the official report of the accident, but the "multi-state
full-service solar provider" that has "approximately 650 employees" was n
Check this out.
Four series strings of mods on a same plane roof feeding a larger Sunny Boy
or Fronius inverter.
Four #10 conductors for the ungrounded, fused (at the inverter) conductors.
And for the grounded conductor, a single, common, larger conductor from
those four strings.
So ins
One point of clarification regarding SunPower Corp. and WEEBs having just
had communication with them today on this subject.
SunPower has yet to officially approve/sign off on the use of WEEBs with
their metal-framed modules.
They have been exploring the issue but have yet to give their seal of
a
What is your no. 1 preferred PV module manufacturer and why?
I'm not looking for a dissertation, but a sentence or two.
And while I'm at it, how about inverter manufacturer as well?
I'll tabulate all the answers for those interested.
Thanks,
marco
__
I believe that there's a section the code that states that a residence shall
have a minimum 100A service.
Can anyone tell me where that is?
Thanks,
marco
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.o
There are two situations one can find when working on three-phase AC
systems: a clockwise or counterclock phase rotation.
Is it correct to assume that a CW rotation would be color-coded (for
120/208V) from left to right black-red-blue while CCW rotation would be,
say, red-black-blue?
Or whe
By golly you're right, Dick. Thanks.
What's weird is that this particular 2 1/2" LB could not handle more than
4/0 conductors. I guess that it wasn't made by T&B.
marco
Marco,
--- You wrote:
I looked at the Thomas and Betts spec sheet kindly supplied by Ratico on
their LB offerings and there
uns intact. I'm looking at an upcoming
installation where I would like to use 1-1/4" EMT, but will need 1-1/2"
conduit bodies to be ok with wire fill.
-Hans
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ma
Anyone know where I could go to find out the max conductor sizes that
threaded Al. LBs can handle?
I learned the hard way that a conduit of X inches that can handle conductors
of a certain size does not necessarily mean that a LB of the same diameter
can handle the same size conductors.
Tha
Anyone know where to go for reconditioned 3-phase kWh meters (other than
Austin International)?
Thanks,
marco
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches
I've been looking hard to see what manufacturers produce this kinda elusive
#10 THHN/THWN-2 wire.
United Copper Industries (Texas) does. I have a handy spec sheet from them
that I can email anyone who's interested.
marco
___
List sponsored by Home Po
Finding that wire in these here parts is pretty much impossible.
Can any of my CA. brethren/sistren provide me any leads on wholesalers in
either northern or southern CA. that carry #10 THWN-2 wire?
Thanks,
marco
___
List sponsored by Home Po
When calculating the voltage drop from a PV array to the inverter, what's
the most common accepted practice? To use the Isc X 1.25 or 1.56 as the
multiplier?
Thanks,
marco
___
List sponsored by Home Power magazine
List Address: RE-wrenches@list
Anyone have any line on some MC4s or have some, even a paltry quantity, that
they're willing to part with?
Thanks,
marco
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.
In my experience as well the Xantrex GT line of inverters has been fraught
with failures with one site having three failed buggers until I had had
enough and switched to a comparable SMA product.
marco
I am replacing some GT 3.0 multiple times. Though Xantrex pays the labor,
this is still a
, LLC
PO Box 657
Petaluma, CA 94953
Cell: 707-321-2937
Office: 707-789-9537
Fax: 707-769-9037
_
From: Marco Mangelsdorf
To: RE-wrenches
Sent: Tue, May 18, 2010 11:13:02 AM
Subject: Re: [RE-wrenches] MC 4 connectors
Have you ever tried to get a return phone call from Multi-Conta
Have you ever tried to get a return phone call from Multi-Contact in
Petaluma?
Rots of ruck..
Is Wieland a manufacturer of knock-off MC connectors?
marco
Marco:
Multicontact or Wieland.
William Miller
At 10:43 AM 5/18/2010, you wrote:
Content-Type: multipart/alternative;
Anyone have a good line on MC 4 locking connectors?
Thanks,
marco
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
Has anyone had any experience with the fairly new Solmetric Suneye 210
shading analysis tool?
Feedback and observations?
Or how about with their earlier version the Suneye 110?
Thanks,
marco
provision_highres_solar_logo2 with C-26351
Marco Mangelsdorf, President
69 Railroad
How about some clear definitions-for-dummies of 1) linear loads and 2)
non-linear loads?
marco
Marco:
Will non-linear loads be expected? If so, the neutral is considered to be a
current carrying conductor and needs to be counted. If no non-linear loads,
then the neutral is not counted.
Thanks for sending that link, William.
OK.let's try it from a different perspective.
When you're running, say, three three-phase hot conductors from point A to
point B with a neutral conductor, should that neutral be considered "current
carrying" from the perspective of more than three "cur
I have a disbelieving business partner who believes that the neutral
conductor in a standard 120/240VAC service is a current carrying conductor.
Could someone please disabuse him of that notion?
Thanks,
marco
___
List sponsored by Home Power
.com
360.510.0433
On Mon, May 10, 2010 at 11:36 AM, Marco Mangelsdorf
wrote:
I just don't understand why going over 20 percent of module nameplate to
nameplate inverter rating makes any sense.
I regularly see 120-130 percent of nameplate amperage coming off of the
array on our office du
I just don't understand why going over 20 percent of module nameplate to
nameplate inverter rating makes any sense.
I regularly see 120-130 percent of nameplate amperage coming off of the
array on our office due to edge of cloud.
So I have to disagree with Dana in this instance. I see this
Marco,
I have a revenue grade kWh meter on my 3 Enphase 175 system that is owned by
the utility (production based incentive in WA state) and the Enphase
monitoring reads about 6% over the revenue meter. This has been over a one
year period. I've been very pleased with the performance using eit
My biz partner has an Enphase system with BP Solar mods.
He believes that the web-based monitoring system may be reporting on the
high side as far as kWH performance over time.
That is, he suspects that what he's seeing may not be accurate.
Anyone out there have a similar experience?
Anyone have a line on a well-priced Solmetric Suneye 210?
The cheapest I've found so far comes to a bit under $1,900.
Thanks.
marco
provision_highres_solar_logo2 with C-26351
Marco Mangelsdorf, President
69 Railroad Avenue, A-7
Hilo, Hawai'i 96720
(808) 969-3281, 934-7462
For a high voltage DC junction box?
As in "touch these wires and die" or something similar?
Thanks,
marco
provision_highres_solar_logo2 with C-26351
Marco Mangelsdorf, President
69 Railroad Avenue, A-7
Hilo, Hawai'i 96720
(808) 969-3281, 934-7462 f
As in Enphase 190s, S11 version, with the MC3 connectors.
As in about 100 of 'em.
Anyone have any suggested sources?
Thanks,
marco
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & setti
anty deferred to the tire maker's warranty (for
tires), etc. Any similarity?
- Original Message -
From: Marco Mangelsdorf <mailto:ma...@pvthawaii.com>
To: 'RE-wrenches' <mailto:re-wrenches@lists.re-wrenches.org>
Sent: Sunday, April 25, 2010 10:02 PM
Subj
This thread brings up a very timely issue that I’m dealing with right now with
PV Power Purchase Providers. As an integrator providing turnkey PV systems of
X kW, I’m being asked to contractually agree to a minimum performance warranty
for said PV systems. I am EXTREMELY uncomfortable to any s
Pat,
Kicked your butts as far as lower output? If so, by how much on a
percentage basis?
On the Big Island of Hawaii, we've had a very active volcano doing its thing
since 1983. With the normal trade winds, the vog (volcanic smoke + fog)
gets blown south past the volcano, around the south
Very sad news about Hans.
Can anyone tell me who he was working for there in S.F. and whether he was
wearing any kind of safety gear?
Thanks,
marco
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Op
difference between a kW and kWh.
Thanks,
marco
provision_highres_solar_logo2 with C-26351
Marco Mangelsdorf, President
69 Railroad Avenue, A-7
Hilo, Hawai'i 96720
(808) 969-3281, 934-7462 facsimile
<http://www.provisiontechnologies.com> ww
high voltage unit is the 602, there are units available
from other manufacturers but they are a boat load of money and still require
prayer.
Bob
On Fri, Apr 16, 2010 at 6:31 PM, Marco Mangelsdorf
wrote:
Is the best one can do as far as high DC array voltage the Delta LA602?
Didn't they
Is the best one can do as far as high DC array voltage the Delta LA602?
Didn't they used to have a high voltage version of the LA302DC?
Thanks,
marco
provision_highres_solar_logo2 with C-26351
Marco Mangelsdorf, President
69 Railroad Avenue, A-7
Hilo, Hawai'i 96720
(808
Chris,
I've had one of my guys research this same question a while ago and the
conclusion was the as far as low-cost DAS systems, Fat Spaniel was the big
winner, as in under $1,000 which includes a year's worth of monitoring.
Cheers,
marco
Good Day Wrenches,
I'm looking fo
Anyone know who makes a 30-circuit combiner in a NEMA4 non-metallic or
stainless enclosure with a string-level monitoring capability?
Thanks,
marco
provision_highres_solar_logo2 with C-26351
Marco Mangelsdorf, President
69 Railroad Avenue, A-7
Hilo, Hawai'i 96720
(808) 969-3281, 934
Can anyone pass on a good website address that provides the means to
calculate DC line loss over distance?
The ones that I've come across don't allow for entering in whatever you want
as far as specified DC voltage.
Thanks,
marco
provision_highres_solar_logo2 with C-26
them.
On another subject, have any of you used the Schletter-brand mounting
hardware? Any comments?
Thanks,
marco
provision_highres_solar_logo2 with C-26351
Marco Mangelsdorf, President
69 Railroad Avenue, A-7
Hilo, Hawai'i 96720
(808) 969-3281, 934-7462 facsim
I heard that fellow Wrench Walt Ratterman is MIA in Haiti.
Anyone have any news?
marco
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-
I'm reading a piece on energy storage in the latest issue of Distributed
Energy mag.
The writer, Lyn Corum, repeatedly refers to the capacity of storage mediums
(thermal, compressed air, flywheel, battery) in kW and MW terms.
Heck, even my friends at Beacon Power refer to their flywheel sys
Are the Enphase 210s only compatible with the Sanyo mods?
Thanks,
marco
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrench
According to an article, written by a utility engineer on O'ahu, PF can be
worsened at the site where a substantial PV system is located.
If there is a poor or wavering PF due to an abundance of inductive loads at
a particular site, having a large inverter, in relation to the overall power
consump
Mr. Cinnamon's company, Akeena Solar, has accumulated over $48 million in
losses from 2006 through Q3 2009, according to public documents since
they're a publicly-traded company (http://ir.akeena.com/annuals.cfm).
He now apparently believes that he can turn a profit by commodifying PV
through h
r two
poles like the SMA Sunny Boys.
I'd appreciate any education on this.
Thanks,
marco
provision_highres_solar_logo2 with C-26351
Marco Mangelsdorf, President
69 Railroad Avenue, A-7
Hilo, Hawai'i 96720
(808) 969-3281, 934-7462 facsimile
<http://www.provisi
Our friends at SMA are taking today off.
Does anyone know what a "Disturbance-Shut Down" error message actually
means? According to the manual, it means "internal overcurrent
continuous."
But that really doesn't tell me much.
Thanks,
Marco
ProVision
_
Hence the need to be able to present objective, 3rd party-collected
performance data demonstrably showing the superior performance of one brand
over another.
marco
Marco:
Good point, but how does a consumer quantify the expected long term harvest
and reliability of a solar electric system?
The common metric for many consumers when considering a PV system purchase
is the $/watt cost of the installed system. This misleading metric allows
low-priced bottom feeders (those licensed and unlicensed contractors working
out of their garage or storage spaces) to clobber those of us who pay al
Can anyone think of a more brutal environment for a piece of electronic
equipment than under a solar module which day in and day out experiences the
elements and temperatures of 130+ plus F?
Despite any so-called accelerated life-cycle testing and estimated mean time
to failure probabilities, n
And REC Solar had HUGE recall earlier this year to the tune of tens of
millions of .
marco
No, IMHO.
A polycrystalline module is never going to be "top shelf".
First Quality would be Sunpower, Solarworld, Sanyo,
Check the new CEC module ratings. Apparently most modules were fur
"Canadian" Solar modules are most definitely made in China.
I guess they couldn't get away with branding "American Solar" and probably
didn't want "Mexican Solar." Heck, everyone likes Canadians. The "Strong
frame" is not very rigid and flexes too much like most Chinese modules.
- Original
I'm looking for some of those old-style fuseholders for the Pulse brand
combiner box.
I could use a half dozen of them.
Anyone have any out there that they would be willing to sell?
Thanks,
marco
provision_highres_solar_logo2_final
Marco Mangelsdorf, President
69 Railroad A
Mick,
I'll be very interested in what kind of response you get from Solarworld
since they're now twice removed from Siemens (Arco Solar to Siemens to Shell
to Solarworld).
I would have a hard time believing that any PV manufacturer is going to want
to take on the liabilities from two comp
_highres_solar_logo2 with C-26351
Marco Mangelsdorf, President
69 Railroad Avenue, A-7
Hilo, Hawai'i 96720
(808) 969-3281, 934-7462 facsimile
<http://www.provisiontechnologies.com> www.provision-solar.com
<>___
List sponsored
In order to get the 30 percent federal grant rather than the 30 percent ITC,
is there any requirement that the equipment used be American made?
Thanks,
marco
provision_highres_solar_logo2 with C-26351
Marco Mangelsdorf, President
69 Railroad Avenue, A-7
Hilo, Hawai'i 96720
(808) 969
To those of you who have installed PV systems in, say, the 2-4 kW range
using Enphase inverters, how would you compare the labor time and
installation materials (wire, conduit, hardware, etc.) to a standard system
design using a single inverter?
Longer? Shorter? More or less materials? If e
I second a lot of what Peter says. And believe that it ain't gonna get
nuttin' but worse over time as grid-tie PV becomes more mainstream. I think
it's pretty much inevitable that a serious fire or two or serious injury or
death or two due to incompetence and a poorly installed system is gonna
w
I'm seeing ~ $2.60/watt from a major Chinese manufacturer for a modest
volume purchase.
What are you all seeing as far as $/watt?
marco
Joel,
Since late last year we've been stocking the Yingli 175w single-crystal
modules. They seem dependable, haven't heard of any problems with them.
Earlier in
Travis,
Given the high cost for electricity here in Hawaii and both the federal and
state tax credits available here, we've had a pretty solid 2009 so far and
been at about the same revenue level as last year. We're a very small
market out here compared to other states. And we're starting to see
Compared to the first five months of last year, how would any of you who
care to respond compare your year-to-date sales in 2009?
Thanks,
marco
Marco Mangelsdorf, President
69 Railroad Avenue, A-7
Hilo, Hawai'i 96720
(808) 969-3281, 934-7462 facsimile
www.provision-sola
Any of you have experience with the new Fronius IG Plus inverters in the 8
kW to 12 kW range?
Good, bad, beautiful, ugly?
Thanks,
marco
Marco Mangelsdorf, President
69 Railroad Avenue, A-7
Hilo, Hawai'i 96720
(808) 969-3281, 934-7462 facsimile
www.provision-sola
Does anyone have any used, working SMA Sunny Beams that they'd be willing to
sell or know of any anywhere?
Thanks,
marco
Marco Mangelsdorf, President
69 Railroad Avenue, A-7
Hilo, Hawai'i 96720
(808) 969-3281, 934-7462 facsimile
<http://www.provisiontechnologies.com&g
I'd appreciate getting in contact with all SunPower Corp. dealers on the
List.
Please email me off-list.
Thanks,
marco
cid:image001.jpg@01C6D004.C865A8F0
Marco Mangelsdorf, Ph.D., President
Electrical Contractor License C-26351
69 Railroad Avenue, A-7
Hilo, Hawai'i 96720
In Hawaii, we have a lot of steel-framed buildings with z-bar steel purlins
supporting the metal roof. My attachment means of choice is using T-5
screws (#12 x 24 threads per inch). These buggers are self-drillers with a
carbon steel shank and drill point and stainless steel hex head cap with
rub
The renewed and expanded ITC..does that still maintain the 20-year max limit
to be able to claim that tax credit?
Thanks,
marco
cid:image001.jpg@01C6D004.C865A8F0
Marco Mangelsdorf, Ph.D., President
Electrical Contractor License C-26351
69 Railroad Avenue, A-7
Hilo, Hawai'i 96720
Peter,
Would a #12 2" self-driller with a carbon steel shank and stainless steel
hex head with attached washer do?
I use the T-5 Scots screws that I get from Dynamic Fasteners.
I use them to attach ProSolar al. mounting rails directly through roof metal
and into a 14g or 16g z-bar purlin.
(I use
I know that it's an oddball size, but I'm looking for a 300A indoor,
surface-mounted 120/240V distribution panel.
Anyone know of an available model and manufacturer out there?
Thanks,
marco
Marco Mangelsdorf, Ph.D., President
Electrical Contractor License C-26351
69 Railroad Avenue
Does anyone know if Fronius is actually shipping their higher output IG Plus
line? Do any distributors actually have some on their shelves?
Thanks,
marco
Marco Mangelsdorf, Ph.D., President
Electrical Contractor License C-26351
69 Railroad Avenue, A-7
Hilo, Hawai'i 96720
(808) 969-3281
Joel,
I've been either a participant or observer of the PV field/industry as long
as most greybeards in the field. And ever since my entry in the RE biz in
the 1970s, the promise from the touters of thin films has been: 1) their
product was going to revolutionize the industry, 2) their product
301 - 374 of 374 matches