Re: [RE-wrenches] Discover AES explosion!

2024-05-03 Thread Starlight via RE-wrenches
Hi Michael, For 11 years I’ve been in the Li battery business. We formerly designed and installed over a hundred Li battery based systems, mostly mobile installations but UPS and off-grid as well. Since 2018, we no longer do installations. Currently we sell our own Li-ion brand with many

Re: [RE-wrenches] Cable sizing for high current modules? NEC interpretation/guidance?

2023-11-08 Thread Starlight via RE-wrenches
Choosing a higher insulation rating for the wire will increase current capability, if that works in your case. Larry Crutcher Starlight Solar Power Systems On Nov 8, 2023, at 10:06 AM, George McClellan via RE-wrenches wrote: Team; With the move to larger cells, some modules have an Isc

Re: [RE-wrenches] Magnum problem

2023-10-31 Thread Starlight via RE-wrenches
Sorry Dan, I meant Ron. On Oct 31, 2023, at 11:08 AM, Starlight via RE-wrenches wrote: Dan, Since you are using 120Vac for the source, did you connect to just 1 AC input; AC1 or AC2? You can not parallel same phase to both inputs or damage may occur. Have you measured the generator

Re: [RE-wrenches] Magnum problem

2023-10-31 Thread Starlight via RE-wrenches
Dan, Since you are using 120Vac for the source, did you connect to just 1 AC input; AC1 or AC2? You can not parallel same phase to both inputs or damage may occur. Have you measured the generator frequency and voltage at the inverter input? Make sure to reduce the charge rate to 50% or less

Re: [RE-wrenches] 70-100 amp relay

2023-10-03 Thread Starlight via RE-wrenches
I'm sold on Gigavac quality. I’m not sure if they have the AC coil option. https://www.sensata.com/products/gigavac-power-contactors-fuses/gv-contactors Larry Crutcher Starlight Solar Power Systems On Oct 3, 2023, at 12:05 PM, jay via RE-wrenches wrote: Hi All, I’ve gotten approval from

Re: [RE-wrenches] Charger recommendations

2023-09-04 Thread Starlight via RE-wrenches
Iota DLS converters can be stacked in series. Using 4 of the 90 Amp in series will get you close. Larry Crutcher Starlight Solar Power Systems On Sep 4, 2023, at 4:16 PM, Ron Young via RE-wrenches wrote: Hi All, I am looking for recommendations for a standalone 48v high amp charger (min.

Re: [RE-wrenches] Inverter On/Off Switch use Outback FX

2023-07-13 Thread Starlight via RE-wrenches
They did not anticipate the use with Lithium battery chemistry which is mostly discharged at 12.7V, and that happens to be the fully charged resting voltage of lead batteries. Seems as though by now manufacturers should have increased the LBCO voltage range in the software. Larry Crutcher

Re: [RE-wrenches] High current dc combiner vibration

2023-06-29 Thread Starlight via RE-wrenches
You may already know but… Are your DC cables bonded together and twisted where possible to reduce magnetic fields? Higher the current and greater the loop area, the stronger the fields are. More parallel loops, the greater the combined flux = loud Hums. Larry Crutcher Starlight Solar Power

Re: [RE-wrenches] Lithium battery charge rate

2023-06-28 Thread Starlight via RE-wrenches
That makes more sense, Darryl, thanks for sharing that. Another good example, Jay. We do have batteries that can be charged at 3C but I have only designed one mobile medical unit with that capability. It required 2 50A shore power connections or could use the onboard 20kW generator. Makes lots

Re: [RE-wrenches] Lithium battery charge rate

2023-06-26 Thread Starlight via RE-wrenches
Hi Jay, For our LFMP and LFP batteries, it has never mattered. As long as current is flowing, the SoC is increasing and the voltage will rise until it reaches the CV set point. Typically cell balance occurs when a cell voltage reaches a set point where a load turns on across that cell.

Re: [RE-wrenches] Battery balancers

2023-05-16 Thread Starlight via RE-wrenches
? Thank you, Chris On 5/15/2023 6:12 PM, Starlight via RE-wrenches wrote: > Jay, > > I started recommending the Victron battery balancer for all series and > series/parallel Li battery banks. It has eliminated trouble in some > problematic systems. If you reach a cell over-voltage i

Re: [RE-wrenches] Battery balancers

2023-05-15 Thread Starlight via RE-wrenches
Jay, I started recommending the Victron battery balancer for all series and series/parallel Li battery banks. It has eliminated trouble in some problematic systems. If you reach a cell over-voltage in the Kilovault BMS, it will block current flow, preventing the other series batteries from

Re: [RE-wrenches] Cell phone based relay control

2023-03-13 Thread Starlight via RE-wrenches
https://www.amazon.com/Solenoid-Control-Wireless-Contact-T-Mobile/dp/B07Q7PKW5Z?th=1 Larry Crutcher Starlight Solar Power Systems On Mar 13, 2023, at 12:47 PM, Jay via RE-wrenches wrote: Hi all Any recommendations for a cell phone controlled relay? Would be off grid. There is 12v already

Re: [RE-wrenches] PV and EMP

2023-03-09 Thread Starlight via RE-wrenches
Right Dave. The VooDoo of EMI filtering, lightning protection or EMP induced voltage reduction attempts are similar and governed by the inverse square law. How much energy and how close is it? You must properly reduce energy propagation at every point. I have seen very expensive protection

Re: [RE-wrenches] Fire fighters

2023-03-08 Thread Starlight via RE-wrenches
To all techies, what if a bleeder resister, similar to what is used on a capacitor, was in parallel with the PV strings or array? That should pull down any high voltage from a low illuminance light source. Larry Crutcher Starlight Solar Power Systems On Mar 8, 2023, at 2:13 PM, Darryl Thayer

Re: [RE-wrenches] Remote battery disconnects

2023-02-01 Thread Starlight via RE-wrenches
Have you (or any) installed surge suppression on the PV input side to clamp the open circuit voltage surge? Larry Crutcher Starlight Solar Power Systems On Feb 1, 2023, at 1:23 PM, William Bryce via RE-wrenches wrote: I can also backup what Jim has said, and have seen the same gear

Re: [RE-wrenches] Magnum 4024PAE Won't Charge

2023-01-19 Thread Starlight via RE-wrenches
Hello Drake, Since the relay board is functioning some times, I would more suspect (1) an intermittent controller board or (2) corrosion on the contact area of the header connection. They are relatively easy to change and not too expensive. One thing I would test first is to unplug the ARC

Re: [RE-wrenches] Low Frequency transformer off-grid inverter options

2023-01-13 Thread Starlight via RE-wrenches
Any new AC equipment connected and running during test? Scope the waveform during equipment start to see if the distortion is severe. I have seen a 300W load make a mess of a Magnum AC waveform. Larry Crutcher Starlight Solar Power Systems On Jan 13, 2023, at 11:48 AM, Mac Lewis wrote:

Re: [RE-wrenches] Low Frequency transformer off-grid inverter options

2023-01-13 Thread Starlight via RE-wrenches
Mac, What was the lowest voltage measured at inverter battery terminals during the inrush measurement? Larry Crutcher Starlight Solar Power Systems On Jan 13, 2023, at 11:33 AM, Mac Lewis via RE-wrenches wrote: Hello Wrenches, I have a new client that has ran a pretty decent wood shop

Re: [RE-wrenches] White Roof Temperature

2022-08-25 Thread Starlight via RE-wrenches
Perhaps this: https://jacobsschool.ucsd.edu/news/release?id=1094 Larry Crutcher Starlight Solar Power Systems On Aug 25, 2022, at 11:37 AM, Drake Chamberlin via RE-wrenches wrote: Hello Wrenches, A client installed a beautiful white standing seam roof. Suddenly their air conditioning