e-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of August Goers
Sent: Monday, October 15, 2012 12:38 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] center fed main panel and 120% rule
Kent, Brian,
It still seems like a grey area to me. I th
, 2012 12:07 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] center fed main panel and 120% rule
If you back feed at the end of the bus bar where the main is connected to
the middle of the bus bar, the back fed breaker cannot overload the bus bar
between the main and the back fed breaker,
If you back feed at the end of the bus bar where the main is connected
to the middle of the bus bar, the back fed breaker cannot overload the
bus bar between the main and the back fed breaker, but it would be
possible to overload the other side of the bus bar - it's being fed by
both the main a
Well the intent is so that no part of the bus bar is exposed to more than
its stated rating. With the inverter breaker at the bottom and the main at
the top there isn't any spot on the bus that is subject to the sum of the
main and the inverter breaker currents.
With a center fed panel, the secti
Hi Wrenches,
Here is yet another 120% rule question as it relates to center fed main
panels. 2011 NEC 705.12 deals with inverter point of connection and
705.12(D)(7) reads:
"*Inverter Output Connection.* Unless the panelboard is rated not less than
the sum of the ampere ratings of all overcur
5 matches