2012-10-15 Thread Allan Sindelar
Funny, happened to us, too, some years back... six sets of 2V cell pairs in a 24V bank, with one case showing 0.05 volts DC, the difference in resting voltage between the two cells. We opened up the cover (the case was red, as I recall, Mick), disconnected the int

Re: [RE-wrenches] weak voltage

2012-10-15 Thread mark
I had one whole pallet of "famous brand" that were charged backwards.  The positive post (as charged) WAS painted red, but the plastic case "+" and "-" markings were by the wrong posts.   Before I realized the error, I installed 8 of these at a customer, going by the red painted post, not noticing

Re: [RE-wrenches] weak voltage

2012-10-15 Thread Chris Mason
Anything more than a few millivolts. On 10/15/12, mac Lewis wrote: > How much voltage drop indicates a problem? > > On Mon, Oct 15, 2012 at 8:13 AM, Chris Mason > wrote: > >> You should see a voltage drop across the connections if they are faulty. >> >> >> On Mon, Oct 15, 2012 at 8:54 AM, mac Lew

Re: [RE-wrenches] weak voltage

2012-10-15 Thread Kirpal Khalsa
Mick.we had this happen once too.Luckily it had already become standard procedure for us to check and notate voltage of each battery prior to connecting battery cableswe had installed 11 of the 12 batteries and the 12th battery turned out to have reversed polarity..While we didn't s

Re: [RE-wrenches] weak voltage

2012-10-15 Thread mac Lewis
How much voltage drop indicates a problem? On Mon, Oct 15, 2012 at 8:13 AM, Chris Mason wrote: > You should see a voltage drop across the connections if they are faulty. > > > On Mon, Oct 15, 2012 at 8:54 AM, mac Lewis wrote: > >> Hmmm, >> >> This had factory installed bussing. I will pull it o

Re: [RE-wrenches] weak voltage

2012-10-15 Thread Chris Mason
You should see a voltage drop across the connections if they are faulty. On Mon, Oct 15, 2012 at 8:54 AM, mac Lewis wrote: > Hmmm, > > This had factory installed bussing. I will pull it off and clean it up. > Thanks. I suppose that something like this be invisible to an Amp hr > meter. > > >

Re: [RE-wrenches] weak voltage

2012-10-15 Thread Bill Loesch
Mick, Thanks for sharing. Outstanding troubleshooting (particularly when done remotely). Bill Loesch Solar 1 - Saint Louis Solar On 15-Oct-12 8:24 AM, Mick Abraham wrote: Hello, Wrenchies~ Mac Lewis wrote about battery strangeness on the Sunny Island system for his clients. Here is a theo

[RE-wrenches] weak voltage

2012-10-15 Thread Mick Abraham
Hello, Wrenchies~ Mac Lewis wrote about battery strangeness on the Sunny Island system for his clients. Here is a theory to consider, Mac. I once bought a 48v string of >famous brand< two volt cells in which one cell had been loaded backwards into its case. When hooked up according to the +/- mar

Re: [RE-wrenches] weak voltage

2012-10-15 Thread mac Lewis
Hmmm, This had factory installed bussing. I will pull it off and clean it up. Thanks. I suppose that something like this be invisible to an Amp hr meter. On Sun, Oct 14, 2012 at 11:01 PM, William Miller wrote: > Mac: > > We had a similar problem with a large bank of IBE 2 volt cells. The > b

Re: [RE-wrenches] weak voltage

2012-10-14 Thread William Miller
Mac: We had a similar problem with a large bank of IBE 2 volt cells. The batteries had to be removed the same day they were installed and then reinstalled the next day. They sat outside for one night. The flags acquired an invisible but insidious corrosion that caused problems getting and

Re: [RE-wrenches] weak voltage

2012-10-14 Thread Chris Anderson
Call Dane Forsberg at SMA. Very knowledgeable. He helped me recently go through all the settings on my 8kw SI system. Sent from my iPhone On Oct 14, 2012, at 9:41 PM, mac Lewis wrote: Hi wrenches, About 2 months ago, we installed an off-grid Sunny Island System. Here are the specs: 8.82 kW P

[RE-wrenches] weak voltage

2012-10-14 Thread mac Lewis
Hi wrenches, About 2 months ago, we installed an off-grid Sunny Island System. Here are the specs: 8.82 kW PV SunnyBoy 8000 2 x Sunny Island 5048 Inverters 2490 Ahr SolarOne HUP batteries at 48V 30 kW Cummins Propane Generator We are having an issue that I am having a hard time figuring out. W