On Dec 17, 2015, at 11:55 AM, Ray Walters wrote:
...but as far as I can tell, every other storage chemistry has similar
characteristics: lower capacity at low temps, a high temp limit, non-linear
cycle life depending on DOD, Puekert's exponent relating capacity vs charge/
HI Ray,
I think you are right.
But for example, lithium have a really flat voltage curve, and then drop like a
stone. And mostly can handle extreme C/D rates with no issue.
VS
LA which have much more of a actual curve on voltage and extreme C/D rates
really impact capacity and wear.
And for
Hi Larry;
LFPs definitely have some internal resistance and therefore are subject
to Puekert's law, they just have an exponent that is closer to 1. Yes,
they also have a higher operating temperature, but it still has a limit.
My point is that if you develop software to better model FLA
With relays you can set the A/C up as a
dump load that will activate when the grid goes down.
At 06:59 AM 12/17/2015, you wrote:
I have a customer that has had AGM batteries in
the Caribbean for many years without any sign of
capacity loss, but...they air condition (?) the
room they are in,
as i understand it agm batteries are lead calcium. my personal experience has
shown me that lead calcium is THE battery for ups systems.
to reiterate previous emails about this:
i have two grid tied systems here at home, both with battery backup (outback
gvfx series) inverters. one has 1986
Jay,
And, and, and, indeed. There are SO many factors affecting battery life. With
some battery capacity monitors (like Blue Sky Energy IPN-Pro), you can see the
total kWh removed from a battery bank since it was installed. But that data
does not consider the non-linearity of the DoD/Cycle
I'm experimenting with a panel I built myself that is series'ed and
paralleled to produce a Voc of ~3.3 volts and ~10-12 amps which can be
alligator clipped to slacker 2V cells, leads running outside to a sunny
locale. It's certainly not the quickest/best solution but worth a try
in some
I have a customer that has had AGM batteries in the Caribbean for many
years without any sign of capacity loss, but...they air condition (?) the
room they are in, and they do not use any discharge, they are purely setup
as a UPS style system. Unless the power fails, all the power is exported,
and
Hi Larry,
I've talked to Ralph about adding temp comp and puekerts.
But he doesn't know think that it matters, I don't agree with him though.
http://bogartengineering.com/sites/default/files/docs/PeukertsComments.pdf
Jay
Peltz power.
> On Dec 17, 2015, at 7:26 AM, Starlight Solar
Hi Larry and Jay;
I totally agree, that taking into account charge and discharge rates,
DOD, and temperature, we should be able to more accurately model a
battery's lifespan. We already have temp sensors at the battery, so it
seems just a matter of software to do this. Also battery's
HI Todd,
Thats not my understanding.
VRLA batteris come just like FLA, cycling and non cycling.
I can’t speak to the non cycling as I don’t use them.
But cycling VRLA are lead/antimony, not lead calcium.
jay
peltz power
> On Dec 17, 2015, at 8:56 AM, toddc...@finestplanet.com wrote:
>
> as i
HI Ray,
yep agreed, the brain power is going towards Lithium. Thats what I would do.
Schneider also has a high temp shut down.
Not sure about OB, or magnum.
cheers,
jay
> On Dec 17, 2015, at 10:55 AM, Ray Walters wrote:
>
> Hi Larry and Jay;
>
> I totally agree, that
I didn't install it but it was well done, has three Sunny Islands and three
Sunny Boys. My only involvement has been to repair a breaker that failed,
and to service the generator.
On Thu, Dec 17, 2015 at 11:18 AM, Drake <
drake.chamber...@redwoodalliance.org> wrote:
> With relays you can set the
We recommend an EQ when there is a 0.02 SG differential on any one cell to the
rest of the pack, use a refractometer for SG readings, install watering systems
with a electrolyte port or water the battery bank ourselves, & do not do
systems without a charging power backup.
14 matches