Re: [RE-wrenches] AC Coupled Tesla system

2022-04-28 Thread Chris Sparadeo via RE-wrenches
Hi William, Each Powerwall can accept 5 kW of continuous charge and 7 kW peak for 10 seconds. These values increase respectively with additional units (i.e. 10kW continuous for 2 units, 15kW for 3 etc). It’s my understanding that each unit can accept 7.6 kW of AC coupled PV. If PV is generating

Re: [RE-wrenches] AC Coupled Tesla system

2022-04-28 Thread Marco Mangelsdorf via RE-wrenches
Max rating of the Gateway2 is 200A. Regarding a generator input, you're correct, there's no means that I'm aware of to integrate a backup generator with the Tesla equipment that would interact with the solar and storage. marco On Thu, Apr 28, 2022 at 5:45 PM William Miller via RE-wrenches <

[RE-wrenches] AC Coupled Tesla system

2022-04-28 Thread William Miller via RE-wrenches
Friends: I have two questions about AC coupling Tesla systems: 1. Are there limits on how much power can be AC coupled through a Tesla gateway? Does it depend on the quantity of power-walls connected? 2. I understand a Tesla system does not have a separate generator input so if a