thanks all for the thoughts. Ended up replacing all breakers and the
controller and the problem has gone away. sent the controller back to
midnite and came back with no issues so we are assuming it was the breaker.
Daniel Tittmann
CTO
Greenwired
www.greenwired.com
dan...@greenwired.com
707-923-2
I might take a clamp on ammeter and check the Classic's battery side
current.
Then maybe turn ON the generator and see what happens to the current
on that line.
boB
On 11/6/2015 1:49 PM, Daniel Tittmann wrote:
there is a MNSPD 300 AC and a MNSPD 300 DC. are wired into the system.
this is
there is a MNSPD 300 AC and a MNSPD 300 DC. are wired into the system.
this is a new system. Has been happening since commissioning.
it is possible that the generator is charging during those morning hours as
there are likely morning loads, coffee pot, but not always as the customer
just went on
Good tip, and also prompts me to remind that a thermal camera will see a
lot of problems the eye cannot. We have a fluke thermal camera and I make
it a practise to survey a customer's electrical room prior to doing a
proposal, as identifying the overloaded components can help to avoid the
blame gam
Some years ago, we had a similiar problem with a 50 amp breaker nuisance
tripping, we over analyzed the problem and still could not prevent this
erratic issue, sometimes it would work fine for weeks - sometimes days apart,
sometimes on sunny days, sometimes on cloudy days.
In the end the answe
Allan, No, not suggesting to get rid of E-panels or wiring centers.
They aren't optimum though,
electrically speaking. My suggestion was more of a technical one
intended to illustrate a
way of wiring to reduce stress on (most) MPPT charge controllers. I
should not have said
it was a a good
boB,
I appreciate your contribution to this discussion, but it brings up
a couple of issues for me.
- You have suggested that "A good wiring practice these days is
to...wire the controller's
battery terminals close or right at the battery terminals." This
goe
On 10/29/2015 5:02 PM, Jay wrote:
boB,
Is the OCP still being used and does it work in both directions?
JAY
Peltz power
Hi Jay. Yes, the OCP you refer to is still there. This particular OCP
though is a hardware
fast OCP intended to protect the controller against large load surges on
the
boB,
Is the OCP still being used and does it work in both directions?
JAY
Peltz power
Sent from my iPhone
> On Oct 29, 2015, at 4:19 PM, "b...@midnitesolar.com"
> wrote:
>
>
> Larry, because these MPPT CC's are bi-directional (for efficiencies' sake),
> they can convert a large current
> a
Larry, because these MPPT CC's are bi-directional (for efficiencies'
sake), they can convert a large current
at the battery side to a smaller current at the PV side if not adjusted
right. Normally this is just taken
care of and reduced to a bare minimum by the controller watching the
voltages
After the Magnum Inverter/charger samples incoming AC power, they have a slight
delay before starting the charger. Then, they ramp up current slowly.
Even so, how will any current from any other source pass through the breaker
unless the Classic is presenting a load? I suppose something else co
This is probably not the breaker at fault. Could be, but just doesn't
seem like the only thing
I would suspect.
Do you know if the generator might be turning on and charging the
battery through the
inverters at this time in the morning ? Since you were talking about
the AGS it makes
me won
You don't want to drive for hours and hours to do something that might
not fix the problem.
Without knowing exactly what is happening, I would bring a spare Classic
and also a new breaker
which I think I heard we were sending you
If the Classic is plugged into the internet, there is the
Daniel,
Very strange problem.
While I agree that you should try replacing the 100A breaker, I doubt that
it’s the problem. Why would a breaker trip at low amperage in the morning,
but not trip at noon when the amperage is higher?
At early morning turn-on, the voltage might be too high, but
14 matches