Perfect. That's what I thought. No comments on the comm issue, so I assume
there is no issue.
*Jason Szumlanski*
*Fafco Solar*
On Sat, May 18, 2013 at 7:42 PM, Nick Soleil nsol...@enphaseenergy.comwrote:
Hi Jason,
You can do that, but will need to maintain the 15A limit of the M190s.
NABCEP Certified PV Installation ProfessionalT
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Monday, May 20, 2013 7:14 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Combining Enphase M190 and M215 on same
Jason,
The M190 requires using a 15-amp (maximum) branch circuit. As long as
the total current from both types of inverters doesn't exceed 12 amps
(80% of 15), there should not be a problem in mixing the inverters. The
combination you are proposing is only 8.6 amps -- it should be fine.
Hi Jason,
You can do that, but will need to maintain the 15A limit of the M190s. For
a single-phase, 240V application, with 3 M190s (3*0.8A = 2.4A,) you can
install up to 10 M215s.
On Sat, May 18, 2013 at 3:26 PM, Jason Szumlanski ja...@fafcosolar.comwrote:
Is there any reason I can't do
4 matches