Re: [RE-wrenches] EGC vs GEC, separately derived system

2012-11-29 Thread Jason Szumlanski
We typically run a #6 combined EGC/GEC on all residential systems just to keep it simple. The cost difference is typically negligible. We use irreversible C-crimps to combine the wires in a roof mounted junction box. *Jason Szumlanski* *Fafco Solar* On Wed, Nov 28, 2012 at 10:56 PM, mac Lewis

Re: [RE-wrenches] EGC vs GEC, separately derived system

2012-11-29 Thread Brian Mehalic
The separately derived issue aside, enphase inverters have an internal DC system ground and a marked point from which a DC GEC must be installed. Typically grounding is being done in the manner stated in 690.47(C)(3) - a single conductor as both the DC GEC and EGC, meaning it has to be the larger

Re: [RE-wrenches] EGC vs GEC, separately derived system

2012-11-29 Thread August Goers
Of *mac Lewis *Sent:* Wednesday, November 28, 2012 7:56 PM *To:* RE-wrenches *Subject:* [RE-wrenches] EGC vs GEC, separately derived system Hello wrenches, What constitutes a separately derived system? Would you consider a breaker tied enphase system a separately-derived system? Suddenly

[RE-wrenches] EGC vs GEC, separately derived system

2012-11-28 Thread mac Lewis