Exactly, when we had problems most inspectors would let us swap out for standard breakers. I'd check with the micro manufacturer and see if they have one that's compatible but as Brian said they took that code requirement out of the 2017 NEC so I must have had my dates mixed up and it was in the

Re: [RE-wrenches] Micro inverter OCP

2019-04-26 Thread Jay
Hi Will, Sorry, didn’t mean too. Reading between the lines, once inspected the faulty breaker was somehow replaced with a normal one. And so to my question, at this point they are no known arc/ground fault backfeed approved rated breakers? Jay > On Apr 25, 2019, at 11:45 AM, Will White

Re: [RE-wrenches] Micro inverter OCP

2019-04-25 Thread Will White
Jay, You're triggering some serious PTSD with this question. When 2017 NEC came out Mass was the first state to adopt it and the inspectors started requiring arc fault breakers on the micro inverter branch circuits, we were using Enphase. At the time they didn't work, weren't really listed for

Re: [RE-wrenches] Micro inverter OCP

2019-04-25 Thread Nick Soleil
of Jay Sent: Thursday, April 25, 2019 7:15 AM To: re-wrenches@lists.re-wrenches.org Subject: [RE-wrenches] Micro inverter OCP EXTERNAL EMAIL - Use caution when responding, clicking, and/or downloading attachments. Hi all, For micro inverters, what OCP is available for ground fault ( or arc

Re: [RE-wrenches] Micro inverter OCP

2019-04-25 Thread Brian Mehalic
Is this in regards to 2014 NEC 705.12(D)(6)? This requirement was deleted in 2017. Brian Mehalic NABCEP Certified Solar PV Installation Professional™ R031508-59 National Electrical Code® CMP-4 Member (520) 204-6639 Solar Energy International http://www.solarenergy.org SEI Professional Services

[RE-wrenches] Micro inverter OCP

2019-04-25 Thread Jay
Hi all, For micro inverters, what OCP is available for ground fault ( or arc fault) for roof top mounted on a living structure? Thx Jay ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email