Re: [RE-wrenches] Raceway Partitions or Barrier in Gutters

2021-02-01 Thread August Goers
Hi Mac, We use wireway "gutters" all the time. Our supplier mostly sends us Hoffman brand wireways and they also sell a barrier kit: Here is an example of a barrier and a 4"x4"x24" wireway, you'd need to spec out the dimensions you need for your project:

Re: [RE-wrenches] Raceway Partitions or Barrier in Gutters

2021-02-01 Thread Blake Gleason
Wire Loom/Split loom Blake Gleason, PE Director of Innovation & Technical Excellence Sun Light & Power On Mon, Feb 1, 2021, 2:37 PM Mac Lewis wrote: > Hello wrenches, > > What are folks using for raceway partitions to comply with 690.31(B) when > running AC/DC and batteries conductors through

Re: [RE-wrenches] Raceway Partitions or Barrier in Gutters

2021-02-01 Thread Dave Angelini Offgrid Solar
Not a day for me. I do not care if it is UL listed or not. The Schneider PDP is UL also. Not high reliability in my opinion! Especially at 600vdc as there is not disco that will fit in the load center or PDP that I would trust. We all have our requirements and they can easily exceed UL !

Re: [RE-wrenches] Raceway Partitions or Barrier in Gutters

2021-02-01 Thread Ray
On both Outback and Midnites's AC/DC Load centers, they just have separate areas, but there is no partition, or anything like that. They are UL listed.  I don't do GT, so I don't really deal with this issue outside of the E panel, but if it were me, I'd just zip tie the PV wires together, put

Re: [RE-wrenches] Raceway Partitions or Barrier in Gutters

2021-02-01 Thread Dave Angelini Offgrid Solar
I land 600vdc PV into the Mppt/Mppt's only. I never mix 600vdc with anything except SPD/disco ever! Just not that hard and for offgrid, standard practice for reliability. Same with 150vdc, I never get it into the PDP and disco it up stream form mppt. Dave Angelini Offgrid Solar "we go where

Re: [RE-wrenches] Raceway Partitions or Barrier in Gutters

2021-02-01 Thread William Miller
Solar 17395 Oak Road, Atascadero, CA 93422 805-438-5600 www.millersolar.com CA Lic. 773985 *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Mac Lewis *Sent:* Monday, February 1, 2021 2:38 PM *To:* RE-wrenches *Subject:* [RE-wrenches] Raceway Partitions

[RE-wrenches] Raceway Partitions or Barrier in Gutters

2021-02-01 Thread Mac Lewis
Hello wrenches, What are folks using for raceway partitions to comply with 690.31(B) when running AC/DC and batteries conductors through a common gutter? Is there a product or just something made by the installer? These multiport inverters make it difficult not to use a gutter and have a clean