Wrenches, Jason
Midnight pv2 by panel, holds two breakers or as l recall fuse holders rated
for 600 vdc
Jerry
On Thu, Jan 18, 2024, 7:43 AM Jason Szumlanski via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> I am installing an EG4 off-grid 3k inverter for the first time, and the
>
quipment safety. If you don’t
> believe me, try running conductors to a roof-top air conditioning unit
> without conduit protection and see what your inspector thinks about that.
>
>
>
> I am interested in thoughts any of you may have on the above topics.
>
>
>
>
enches
*Sent:* Thursday, January 18, 2024 9:50 AM
*To:* RE-wrenches
*Cc:* Nick A Lucchese
*Subject:* Re: [RE-wrenches] Recommendation on DC Breaker
The Siemens HNF361RPV is worth looking into. Quite affordable and reliable
build quality without having to resort to Amazon. It first appears that
it’s
The Siemens HNF361RPV is worth looking into. Quite affordable and reliable
build quality without having to resort to Amazon. It first appears that it’s
limit is 250 vdc but the footnotes indicate 600 once going deeper into the
details. Obviously not a fuse though.
Nick
> On Jan 18, 2024, at
Thanks, all, for the quick recommendations. I believe an isolator like the
IMO is technically all that is needed since it is a current limited circuit
and OCPD shouldn't be required, but the manual calls for a circuit breaker.
That is probably just a semantics issue.
On the other hand, the 1000V
Jay,
I regularly use 1000 vdc rated, 20a breakers. You can buy them on Amazon.
They are din rail mount. 1,2 or 4 pole.
Daryl
On Thu, Jan 18, 2024, 10:51 AM August Goers via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> I've used Midnite DC combiners in the past with good results.
I've used Midnite DC combiners in the past with good results. Since you are
over 150 VDC, I believe you'd need to select the 1000 VDC fuse holder(s)
for your application:
https://www.midnitesolar.com/productPhoto.php?product_ID=78_ID=9=4=p
August
On Thu, Jan 18, 2024 at 7:43 AM Jason
Correction: That was unadjusted Voc. Temperature-adjusted Voc is 316V.
Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
On Thu, Jan 18, 2024 at 10:42 AM Jason Szumlanski <
I’d use an IMO disconnect as you don’t have any current limitations.
I think sometimes things get lost in translation.
Jay
> On Jan 18, 2024, at 8:43 AM, Jason Szumlanski via RE-wrenches
> wrote:
>
>
> I am installing an EG4 off-grid 3k inverter for the first time, and the
> manual
I am installing an EG4 off-grid 3k inverter for the first time, and the
manual requires a DC circuit breaker on the PV input. It will be a small PV
array with adjusted max Voc around 280V @ Isc 10.6A.
I'm looking for a cost-effective DC breaker and enclosure for this purpose.
Jason Szumlanski