Here is an old 2001 posting from Bill Brooks...
William, Marco
Hey all,
I have a client who was off grid and is now grid tied and has [2] Trace SW
4024 Inverters. I realize the parameters are not the best for high
efficiency but the client is not into changing out to newer equipment.
Whom at which telephone @ Xantrex might be the best bet to talk to
To:
'RE-wrenches' re-wrenches@lists.re-wrenches.org
Date:
11/17/2009 02:56 PM
Subject:
[RE-wrenches] SW 4024 now grid tie
Sent by:
re-wrenches-boun...@lists.re-wrenches.org
Hey all,
I have a client who was off grid and is now grid tied and has [2]
Trace SW
4024 Inverters. I realize
Here is an old 2001 posting from Bill Brooks...
William, Marco, and Jeff C.,
Here is the method I found to be most effective:
INVERTER SETUP (MENU 9)
set to SELL
BATTERY CHARGING (MENU 10)
set ABSORPTION TIME to 0:00 on both machines.
set MAX CHARGE AMPS to 1 amp on both machines.
BATTERY