Re: [RE-wrenches] SW series fuse rating

2016-03-21 Thread Bill Hoffer
Rebekah I am not 100% sure but I think that there is often confusion between max fuse and max reverse current. When you list a module you request a fuse rating , in this case 4 A and UL will test it by applying a max reverse current of 1.75(max fuse rating) or 7 Amps with out a fuse to insure tha

Re: [RE-wrenches] SW series fuse rating

2016-03-21 Thread Rebekah Hren
Reverse current and max series fuse are not always the same, check out this Solar Frontier manual, pg 3: http://www.solar-frontier.com/eng/cs/groups/co_en_product/documents/document/mdaw/mdey/~edisp/c012760.pdf Rebekah Hren On Mon, Mar 21, 2016 at 3:58 PM, Kristopher Schmid wrote: > I just di

Re: [RE-wrenches] SW series fuse rating

2016-03-21 Thread Kristopher Schmid
I just did a class exercise using the upcoming sw290 for sizing conductors and OCPD and the calculation was such that a 20 amp fuse was needed (rounding up from Isc x 1.56). I hope that the maximum reverse current on the spec sheet is also the maximum series fuse rating. Kris On Mar 18, 2016 8:56

Re: [RE-wrenches] SW series fuse rating

2016-03-18 Thread Bill Hoffer
Jay I believe that is the same. I hate that they say it that way...very confusing. I think it comes from the way it is tested by UL. They reverse current at 1.5 times the fuse rating to insure the fuse size is correct (fuse plus safety factor). Bill On Mar 18, 2016 6:56 PM, "jay" wrote: > HI

[RE-wrenches] SW series fuse rating

2016-03-18 Thread jay
HI All, I was looking at the SW cut sheet. It doesn’t mention series fuse rating. It does mention “maximum reverse current” Is this the same thing? Or where would I find the series fuse rating. thanks jay peltz power ___ List sponsored by Redwood A