Yes but how do you trigger fire raptor except by the fire raptor switch? It will take care of by manual control but what about 690.11? On Tue, Apr 19, 2022, 5:06 PM Jerry Shafer via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > You may want to look at fire raptor as a RSD option. > Je

Re: [RE-wrenches] Schneider XW MPPT 80/600 rapid shut down

2022-04-19 Thread Bradley Bassett via RE-wrenches
The Schneider RSD switch has a Tigo transmitter, which is no longer SunSpec compliant. SunSpec devices do NOT work. I know for certain that the APsmart devices do not work. Fire Raptors are very robust and might be a good choice for off grid where reliability is paramount. But they come with 6ft c

Re: [RE-wrenches] Schneider XW MPPT 80/600 rapid shut down

2022-04-19 Thread Jerry Shafer via RE-wrenches
You may want to look at fire raptor as a RSD option. Jerry On Tue, Apr 19, 2022, 9:42 AM jay via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > HI All > > I’ve got a project coming up that has specified a Schneider XW 80/600 > controller. > > Its going to need RS. > > Is the only produ

Re: [RE-wrenches] Schneider XW MPPT 80/600 rapid shut down

2022-04-19 Thread Darryl Thayer via RE-wrenches
I understand the complete Tigo line and any sun-spec MLPE will work, however, it also requires the RSD box from Schneider I don't have experience with any other than the firestop tigo On Tue, Apr 19, 2022 at 11:42 AM jay via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > HI All > > I

Re: [RE-wrenches] Schneider XW MPPT 80/600 rapid shut down

2022-04-19 Thread Bradley Bassett via RE-wrenches
AFAIK Or any of the variants of that like the dual input unit Brad Sent from my iPhone > On Apr 19, 2022, at 9:18 AM, jay via RE-wrenches > wrote: > > HI All > > I’ve got a project coming up that has specified a Schneider XW 80/600 > controller. > > Its going to need RS. > > Is the only

[RE-wrenches] Schneider XW MPPT 80/600 rapid shut down

2022-04-19 Thread jay via RE-wrenches
HI All I’ve got a project coming up that has specified a Schneider XW 80/600 controller. Its going to need RS. Is the only product still the Tigo TS4-A-F? thanks jay ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-w