Hi wrenches,
I have a
question about sizing the main OCP breaker for a panel combining the output of
several true three-phase output inverters. To be precise - 10 of the Refusol
20kW, which connect to 480V/277 Y with a max output of 24.1 amps, each
inverter has a 3 pole breaker, line a, b, c
Subject: [RE-wrenches] Sizing 3 phase OCPD - main
Hi wrenches,
I have a question about sizing the main OCP breaker for a panel combining
the output of several true three-phase output inverters. To be precise - 10
of the Refusol 20kW, which connect to 480V/277 Y with a max output of 24.1
amps, each
16, 2011 11:43 AM
Subject: Re: [RE-wrenches] Sizing 3 phase OCPD - main
Rebekah,
If you knew only the power and voltage, then you would use the
root of 3 to determine the amps. But since you know the amps, you don't need to
use the root.
The second equation would be the correct
one