[RE-wrenches] THD

2020-11-25 Thread drake . chamberlin
Hello Wrenches, How much total harmonic distortion is acceptable for a generator feeding an inverter, house loads, etc. I'm looking at one that advertises less than 6%. From what I've been able to find on the internet, inverter generators are 3 to 5%. Does this jive with your experience?

[RE-wrenches] THD problem solved

2020-02-13 Thread William Miller
Friends: I was whining on this forum recently about an off-grid system that was tripping GFI and AFCI breakers and devices. The problem seemed to be related to high THD on the voltage

Re: [RE-wrenches] THD

2020-01-23 Thread Ray
My understanding is anything over 5% THD is getting to be a problem.  I've measured that high on grid here before.  Do you have any idea what harmonics this distortion is at?  Have you looked at it on an O scope?  What generator is this?  I've seen portable generators with terrible wave forms

[RE-wrenches] THD

2020-01-23 Thread William Miller
Colleagues: In a recent post about some AC GFI tripping problems, I mentioned I am measuring some high THD readings in certain scenarios—the highest being when the generator is charging at high percentages: Inverter only: 2.5% THD Gen Max: 19% THD Gen 5 Amps: 8% THD I measured the THD