Re: [RE-wrenches] Tigo RSS Off Grid

2024-02-21 Thread Nick A Lucchese via RE-wrenches
Sorry Howie, I now see you were specifically asking about inverter/charge controller combo solutions. I should have caught that detail. Still seems as an easy workaround though if for some reason the inverter manufacturer failed to isolate the 12v output independent of the AC output LBCO.

Re: [RE-wrenches] Tigo RSS Off Grid

2024-02-21 Thread Nick A Lucchese via RE-wrenches
The 48v to 12v DC converter approach should be immune from the inverters LBCO since it lives on the battery side of the inverter/bus. I’ve done a few systems using Tigo’s without issue. The main concern is you now have a DC load attached to the battery output lacking DC load protection that

Re: [RE-wrenches] Tigo RSS Off Grid

2024-02-21 Thread Howie Michaelson via RE-wrenches
With the Sol-Ark (or other DC coupled inverter/charge controller combinations such as the Envy), will the system pass through solar power if the inverter has turned off on LBCO? If not, then these alternative methods for powering the RSD signal generators won't make a difference, correct? And does

Re: [RE-wrenches] Tigo RSS Off Grid

2024-02-17 Thread Ray Walters via RE-wrenches
I second using the 48v to 12 v DC DC converter.  I've had success with that, and avoided the issues Jeremy mentioned. Ray Walters Remote Solar On 2/17/2024 9:35 AM, Bradley Bassett via RE-wrenches wrote: I powered a MidNite LSOB transmitter from a Classic AUX, though the receivers didn't work

Re: [RE-wrenches] Tigo RSS Off Grid

2024-02-17 Thread bob--- via RE-wrenches
Hi Jeremy... The Classic AUX outputs will put out about 13 volts and allow up to about 200 mA maximum. That might be enough to power the transmitter. That is only about 2.5 watts so might not work directly. boB Docked at Trinidad/Tobago today.  Great sun here.  Have only seen one PV

Re: [RE-wrenches] Tigo RSS Off Grid

2024-02-17 Thread Bradley Bassett via RE-wrenches
I powered a MidNite LSOB transmitter from a Classic AUX, though the receivers didn't work with the Classic. The Classic is limited to 200ma output and the Tigo and APS transmitters are rated at up to 800ma input, so it might overload the Classic AUX output if they really do draw that much. I

[RE-wrenches] Tigo RSS Off Grid

2024-02-16 Thread Jeremy Rodriguez via RE-wrenches
Has anyone successfully used a MidNite Classic CC to power a Tigo Rapid Shutdown Transmitter in an off grid setting ? Specifically using the 12v Aux output to keep the PV circuits alive instead of relying on the inverter AC output to do this. Think of this scenario. Batteries reach LBCO,