Re: [RE-wrenches] wrenches] Short Circuit Cell Damage

2012-09-19 Thread Drake
If you cut them one at a time, it won't hurt the 
cutters, but you can get a good shock. Cutting is 
not that difficult, but the stripping can be a bit dicey.



At 07:46 PM 9/18/2012, you wrote:

Content-Type: multipart/alternative;
boundary==_NextPart_000_00CC_01CD95D6.8DC9B940
Content-Language: en-us

If you cut them during the day, under sunlight 
conditions it can do bad things to the wire cutters.


Been there before,
Bob Ellison

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of john

Sent: Tuesday, September 18, 2012 1:43 PM
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] wrenches] Short Circuit Cell Damage

Mark,
   As far as cutting the jumper for us 
nightowls, it is easy.  Wait until dark.  The 
sun actually turns off every day!.
And for the new people on the block, polarity 
can still be determined after dark.  All you 
need is a microvolt to get polarity.


John
CV Solar
-Original Message-
From: benn kilburn mailto:b...@daystarsolar.cab...@daystarsolar.ca
To: RE-wrenches 
mailto:re-wrenches@lists.re-wrenches.orgre-wrenches@lists.re-wrenches.org

Sent: Tue, Sep 18, 2012 1:48 am
Subject: Re: [RE-wrenches] Short Circuit Cell Damage
Mark,
Shorting the string should not be an issue.
Unless you work at night, obviously there will 
be an arc when you cut the jumper, so remember 
to cover the whole string with an opaque 
covering beforehandÂ… I think I remember reading that somewhere?!?!
Or just be careful, try to do it when the 
irradiance is low (less current), separate the 
cut wires quickly and make sure you have left 
enough wire in the box so that you are not 
working with short (and energized) wires in a 
metal box. put a wire nut on one wire while you handle and terminate the other.


A safer method, if possible, would be to leave 
an easily accessible module interconnection 
un-connected until you have terminated the home 
run (+)(-), then go back and make the final module interconnection.


Cheers,
benn
DayStar Renewable Energy Inc.
http://www.daystarsolar.ca/www.daystarsolar.ca  *  Ph: 780-906-7807
Construction Electrician Solar Photovoltaic Systems Certified
Certificate # 0007S
HAVE A SUNNY DAY

On 17/09/12 9:50 PM, Mark Frye 
mailto:ma...@berkeleysolar.comma...@berkeleysolar.com wrote:


Wrenches,

True or False: In a nominal sort of grid tied situation with string Voc
at about 300 VDC and Isc at about 6 or 7 amps..It is OK to install
modules on a roof in the sun and short the pos and neg together
indefinitely.

In other words modules can handle operating at Isc continuously without
damage. It is only if you get localized shading AND a failed bypass
diode that damaging hot spot heating can lead to failure?

I am reviewing an installation manual that recommends completing the
home run by connecting the pos and neg of the string with a single
jumper cable, folding the cable on itself in order to push it through to
a j-box and at some point later on, cutting the jumper in the j-box to
terminate the pos and negs to the home run.

I am concerned both about maintaining the string in a short circuit
condition and cutting the jumper while energized.

Any thoughts?

Mark Frye
Berkeley Solar Electric Systems



___

List sponsored by Home Power magazine



List Address: 
mailto:RE-wrenches@lists.re-wrenches.orgRE-wrenches@lists.re-wrenches.org




Options  settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orghttp://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org



List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orghttp://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org




List rules  etiquette:

http://www.re-wrenches.org/etiquette.htmwww.re-wrenches.org/etiquette.htm



Check out participant bios:

http://www.members.re-wrenches.org/www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Eco Gen

2012-09-19 Thread Tom Duffy
Hi John

We've been having great service from Gillette Generators out of Indiana Greg 
Kolber is the rep he's very helpful

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of john
Sent: Tuesday, September 18, 2012 12:29 PM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Eco Gen

Wrenches

My trusted Kohler dealer recently passed away and now that I don;t have a good 
source of generators and service expertise to draw on, I am once again 
entertaining the thought of selling the Generac Eco-Gen.  Their PR makes it 
sound like they have a great new generator for the off-grid market.  I am 
looking for comments/ experience with the new generator.   I have always tried 
to have and use most of what I sell but I already have two generators at home 
that work great.  I have several new off-grid customers asking me for 
suggestions.  I also have an aging Kohler 8.5 (2300 hours- but running very 
well) ) on a mouintaintop transmitter I service which may need some help down 
the road. Any generator related comments appreciated.

John Blittersdorf
NABCEP Certified Solar PV Installer tm
Central Vermont Solar  Wind LLC
104 River Street
Rutland, VT 05701

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Eco Gen

2012-09-19 Thread Allan Sindelar

  
  
John,
  I continue to have good service with the EcoGen. I managed to burn
  mine up in a fire in May, due to factors completely unrelated to
  the unit. Our homeowner's insurance covered full replacement, and
  I chose the same model again for my own home.
  
  This is the only Generac unit that I recommend, based on historic
  experiences of others. It's quite robust in design and build
  details. A limitation is that it's only currently available as a
  6kW unit, either straight 120V (default) or 120/240. Mine could
  run fine above altitude-derated maximum output, which is important
  with an Outback VFX inverter.
  
  It's a bit more expensive than Kohler's 8.5, and much less than
  the few water-cooled 1800 RPM units still made, such as Gillette's
  (I think).
  
  Allan
  
  


Allan Sindelar
al...@positiveenergysolar.com
  NABCEP Certified Photovoltaic
Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc.
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com



 
  On 9/18/2012 11:29 AM, john wrote:


Wrenches

My trusted Kohler dealer recently passed away and now that
  I don;t have a good source of generators and service expertise
  to draw on, I am once again entertaining the thought of
  selling the Generac Eco-Gen. Their PR makesit sound like
  they have a great new generator for the off-grid market. I am
  looking for comments/ experience with the new generator. I
  have always tried to have and use most of what I sell but I
  already have two generators at home that work great. I have
  several new off-grid customers asking me for suggestions. I
  also have an aging Kohler 8.5 (2300 hours- but running very
  well) ) on a mouintaintop transmitter I service which may need
  some help down the road. Any generator related comments
  appreciated.

John Blittersdorf
NABCEP Certified
Solar PV Installer tm
Central Vermont
Solar  Wind LLC
104 River Street
Rutland, VT 05701

  
  
  
  
  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




  

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Eco Gen

2012-09-19 Thread dan
I've been moving a fair number of Marine grade diesel units. but still prefer Kohler for the propane crowd. dbDan BrownFoxfire Energy Corp.Renewable Energy Systems(802)-483-2564www.Foxfire-Energy.comNABCEP #092907-44


 Original Message 
Subject: Re: [RE-wrenches] Eco Gen
From: Allan Sindelar al...@positiveenergysolar.com
Date: Wed, September 19, 2012 6:45 pm
To: RE-wrenches re-wrenches@lists.re-wrenches.org

 John, I continue to have good service with the EcoGen. I managed to burn mine up in a fire in May, due to factors completely unrelated to the unit. Our homeowner's insurance covered full replacement, and I chose the same model again for my own home.  This is the only Generac unit that I recommend, based on historic experiences of others. It's quite robust in design and build details. A limitation is that it's only currently available as a 6kW unit, either straight 120V (default) or 120/240. Mine could run fine above altitude-derated maximum output, which is important with an Outback VFX inverter.  It's a bit more expensive than Kohler's 8.5, and much less than the few water-cooled 1800 RPM units still made, such as Gillette's (I think).  Allan Allan Sindelar al...@positiveenergysolar.com NABCEP Certified Photovoltaic Installer NABCEP Certified Technical Sales Professional New Mexico EE98J Journeyman Electrician Founder and Chief Technology Officer Positive Energy, Inc. 3209 Richards Lane (note new address) Santa Fe, New Mexico 87507 505 424-1112 www.positiveenergysolar.com  On 9/18/2012 11:29 AM, john wrote:   Wrenches  My trusted Kohler dealer recently passed away and now that I don;t have a good source of generators and service expertise to draw on, I am once again entertaining the thought of selling the Generac Eco-Gen. Their PR makesit sound like they have a great new generator for the off-grid market. I am looking for comments/ experience with the new generator. I have always tried to have and use most of what I sell but I already have two generators at home that work great. I have several new off-grid customers asking me for suggestions. I also have an aging Kohler 8.5 (2300 hours- but running very well) ) on a mouintaintop transmitter I service which may need some help down the road. Any generator related comments appreciated.  John Blittersdorf NABCEP Certified Solar PV Installer tm Central Vermont Solar  Wind LLC 104 River Street Rutland, VT 05701  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

 ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org