Re: [RE-wrenches] Mate 3s with legacy FX inverters

2023-12-12 Thread Roland Shackelford via RE-wrenches
We have numerous systems, with no programing or Mate display issues, however the oldest FX series wont display correctly on Optics RE and wont allow remote programability through Optics RE. Roland Shackelford President / Owner NABCEP PVIP #091209-162 O 808.775.7410 | M 808.938.9239 | 45-487

Re: [RE-wrenches] Sol-Ark phantom loads

2023-11-03 Thread Roland Shackelford via RE-wrenches
Don, We have had this happen when you auto calibrate the CT's and the CTs aren't properly positioned to see exported energy from the Sol-Ark inverter. Couple other times it took several calibrations and messing with opening and closing the cts and double checking splices on extensions of CTS.

Re: [RE-wrenches] Sunny Island AC-Coupled system integration with Fortress E-Vault

2023-10-25 Thread Roland Shackelford via RE-wrenches
Hey Michael, Sorry to hear about your problems. We have gone through several SMA SI issues that can be very difficult to narrow down but found most of the time the issues are founded on miss understanding the affects that different set points have on the over all system operation. In your

Re: [RE-wrenches] Sol-Ark arc fault issues

2022-05-10 Thread Roland Shackelford via RE-wrenches
We have had the same issues in the past, their newest firmware seems to have fixed the issue. Mahalo, Roland Shackelford President / Owner Renewable Energy Services (RES), Inc. | www.renewablenergy.com | Mobile: 808-938-9239 | Office: 808-775-7410 | Fax: 808-775-7756 NABCEP Certified PV