So in essence, you had the PV's connected directly to the inverter's DC battery 
connection point. What did the MPPT charge controller do without the battery as 
a buffer? Did the efficiency go up on the system without batteries to keep 
charged?

Todd


On Wednesday, October 21, 2009 10:12am, Darryl Thayer daryl_so...@yahoo.com 
said:

 I have been quiet because i have not done SI but I have done several 
 Outbacks. 
 One system is 12 OB GVFX 3648s on one battery bank of 600AH, the system will 
 run
 with less batteries, in fact I left the battery off for a month and did not 
 notice
 any loss of exported power to the grid. (this is 3 phase) (I had no grid 
 shutdown
 and did not need critical power)  the system would start and run everyday 
 without
 a battery.
 
 On the other end of the scale I have a Standalone house, using 2 OBs and the
 battery bank is 48 volts 3500 AH
 
 --- On Tue, 10/20/09, Glenn Burt glenn.b...@glbcc.com wrote:
 
  From: Glenn Burt glenn.b...@glbcc.com
  Subject: Re: [RE-wrenches] AC Coupled Re-visited
  To: 'RE-wrenches' re-wrenches@lists.re-wrenches.org
  Date: Tuesday, October 20, 2009, 2:13 PM
 
 
 
 
 
 
 
 
 
 
 
 
 
 
 
 
  SMA recently told me that the
  recommended Ah of the battery bank
  is related to the amount of PV and connected
  inverters.
 
  They recommended a 500Ah bank
  with a 5kW PV SB, and a 600Ah bank
  with a 6kW PV SB.
 
  100Ah to 10,000Ah are the
  supported capacities.
 

 
  I don’t believe you need
  to have a separate battery bank
  with two SI’s. I have been told they can share one.
  One SI is programmed
  as the master  of course they are data commed together
  so they can talk.
 

 
  -Glenn
 

 
 
 
 
 
  From:
  re-wrenches-boun...@lists.re-wrenches.org
  [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
  Behalf Of Mark
  Frye
 
  Sent: Tuesday, October 20, 2009 2:42 PM
 
  To: 'RE-wrenches'
 
  Subject: Re: [RE-wrenches] AC Coupled
  Re-visited
 
 
 
 
 

 
  Thanks Kent. And so I understand
  more clearly, in the case of 2 SIs
  as you describe, each SI has it's own battery bank, and
  the solar would be
  split between the two.
 
   
 
  Considering the charging capacity
  of the SI, what would you say is
  the largest battery bank size for each SI to insure an
  effective C
  value?
 
   
 
  Mark Frye
 
 
  Berkeley Solar
  Electric Systems
 
  303 Redbud Way
 
 
  Nevada
  City,  CA 95959
 
  (530) 401-8024
 
 
  www.berkeleysolar.com 
 
 
 
   
 
 
 

 
 
 
 
 
 
 
  From: re-wrenches-boun...@lists.re-wrenches.org
  [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
  Behalf Of Kent
  Osterberg
 
  Sent: Tuesday, October 20, 2009 11:10 AM
 
  To: glenn.b...@glbcc.com; RE-wrenches
 
  Subject: Re: [RE-wrenches] AC Coupled
  Re-visited
 
  In off-grid mode the Sunny Island uses
  frequency shift power
  control to reduce the output of the Sunny Boy inverters and
  thereby regulate
  the battery voltage.  At some frequency shift (+1, or
  2, or 3 Hz, I'm not
  sure) the output of the SB is reduced by 100%. 
  It's proportional so that
  1/2 as much frequency shift gives a 50% reduction in the SB
  output.  To
  keep clocks accurate, the Sunny Island later shifts the
  frequency a negative
  amount, but the SB inverters ignore that.  For a grid
  backup system, a
  RS-485 cable is required so the Sunny Island can activate
  (or deactivate) the
  frequency shift power control capability of the SB.
 
 
 
  You need to stack two SI inverters to get 240-vac, but that
  will allow you to
  have a 10-kW of grid backup power with up to 12-kW of
  solar.  If you need
  more, you can stack four of SI inverters.
 
 
 
  Kent Osterberg
 
  Blue Mountain Solar, Inc.
 
 
 
 
 
  Glenn Burt wrote:
 
  Our installations of Sunny
  Islands (SI) with Sunny Boys (SB)
  have always used the recommended RS-485 communications
  between all units
  involved. This with reprogramming the SB’s to be able
  to switch to
  off-grid mode per the SI instructions allows a more
  integrated system.
 
  We have had problems with the
  OB PSX-240 and stepping up the 120
  to 240 for the crit load panel (where the SB’s
  connect) when the site has
  slightly high AC voltages. The SB pushes the existing ACV
  higher, then it goes
  out of UL spec  disconnects. Also the SB is now
  sensitive to imbalance on
  L1  L2 because of the neutral sensing – we had a
  customer where the
  SB was disconnecting due to this as well…
 
  I thought the freq shifting was
  to allow other non-SMA inverters
  to be controlled when batteries were full?
 
  Where is the SMA rep on this
  list?
 
  -Glenn
 
 
 
  From: re-wrenches-boun...@lists.re-wrenches.org
  [mailto:re-wrenches-boun...@lists.re-wrenches.org]
  On Behalf Of Kirpal Khalsa
 
  Sent: Tuesday, October 20, 2009 12:05 PM
 
  To: RE-wrenches
 
  Subject: Re: [RE-wrenches] AC Coupled
  Re-visited
 
 
 
  Greetings..it is my understanding
  that the Sunny Island
  coupled with Sunny Boys is able

Re: [RE-wrenches] AC Coupled Re-visited

2009-10-22 Thread Phil Undercuffler
Jeff,

How would the battery based inverter control the charge?  Most modern
control algorithms are based around some version of pulse width modulation
-- PWM.  You open the circuit for a tiny fraction of a second, and as the
battery voltage rises the open (off) pulses get wider, and the closed (on)
times get shorter.  To those of us living in meat time, it looks like the
current is magically tapering.

However, the GT inverter isn't a generator that can have loads unplugged and
plugged back in -- it's a current source.  *If *you could open the circuit
for a millisecond without tripping the anti-islanding protection, the
voltage on its output terminals would begin to rise as the BB inverter
tapered the current.  You may have seen a similar reaction if you've ever
measured the voltage on the PV side of an old-fashioned PWM charge
controller when the batteries near full and the charge controller begins to
regulate -- the voltage on the PV side begins to drift towards module open
circuit voltage.  Once the voltage on the GT inverter's output terminals
rose to the UL1741/IEEE high limit, the inverter would trip offline.

Therefore, the only practical way to regulate the charge is to either tell
the GT inverter to stop making power (ie, shut it down by forcing a
blackout), tell the GT to throttle back power output via communication (ala
Sunnyboy/Sunny Island RS485 and frequency shifts), or to divert that power
and absorb it doing some other work.  Per my other post, I now think this
latter solution is the better idea if you're going to mix brands.

Allan asked what would I recommend to accomplish this.  There's a couple
ways.

1.  DC diversion, using standard PWM controller and DC resistance load.
Advantages:  temperature compensated PWM charge regulation.  Disadvantages:
difficult to source and size diversion load, and you need to ensure the
regulation voltages don't interfere with normal charging and sell back
voltages.  I can share a good technical bulletin written by Morningstar on
sizing DC diversion loads, if you contact me off-list.  No magic bullet on
keeping regulation voltage out of the way of charging voltages -- it's
probably the one aspect that you will spend the most time getting right.

2. AC diversion, using relays driven by Aux Outputs and AC resistance
heaters.  I believe this is the most practical solution available today for
grid tie applications.  It's not PWM, but it's far more stable than 5 minute
off cycles.  Depending upon the brains driving your aux output, it's
probably temperature compensated.  AC heaters are commonly available in a
range of wattages and voltages, and they're dirt cheap.  Besides, it's AC
power that you're trying to absorb, so why make your BB inverter go through
the stress of having to convert that AC power to DC just to send it off to a
heating element?  If you want to get fancy and have multiple inverters
(therefore multiple aux outputs) in the system, you can do staged diversion
(1,000 watts of load come on at one voltage, an additional 2,000 watts comes
on .2v higher, etc).  Same complication of ensuring regulation voltage
doesn't interfere with normal charging and sell back voltages apply,
however.

3. Christmas Wish-list solution:  I've been trying to talk the guys at
Outback into creating a Diversion controller that can talk to the rest of
the system, provide temperature compensated PWM control of energy flow to a
diversion load, but most importantly know when grid power is present and
then stay out of the way.  That would ensure that there is no time where
you're buying AC power from the grid and dumping it to the heater, and it
eliminates all the gyrations of staggering voltage setpoints and hoping that
the multiple temperature sensors and devices will all play nicely under all
conditions.  Bonus points if it can work with AC or DC.  Extra bonus points
if it can work with any brand of equipment (wind or hydro, anyone?).
However, I'm just one voice in the wilderness -- if you would like to see a
solution such as this come to market, send Outback an email.  Let them know
Phil sent you ;-)

I think there is a lot of opportunity to add power reliability and stability
to traditional grid tie systems -- what we need is a way to do it easily and
effectively.  Here's to looking for a way!

Phil Undercuffler
Conergy



 -- Forwarded message --
 From: Jeff Yago jry...@netscape.com
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Date: Wed, 21 Oct 2009 19:53:11 -0700
 Subject: Re: [RE-wrenches] AC Coupled Re-visited
 There have been some good advice related to battery bank sizing and a
 better description of how Sunny Islands work with SunnyBoys, but I am afraid
 we are getting away from my original post that started this and that was:

 Since a battery based inverter has a battery charging section and all kinds
 of software control over the charging process when connected to the grid,
 why does the battery charging process go wild when the grid

Re: [RE-wrenches] AC Coupled Re-visited

2009-10-21 Thread Darryl Thayer
I have been quiet because i have not done SI but I have done several Outbacks.  
One system is 12 OB GVFX 3648s on one battery bank of 600AH, the system will 
run with less batteries, in fact I left the battery off for a month and did not 
notice any loss of exported power to the grid. (this is 3 phase) (I had no grid 
shutdown and did not need critical power)  the system would start and run 
everyday without a battery. 

On the other end of the scale I have a Standalone house, using 2 OBs and the 
battery bank is 48 volts 3500 AH

--- On Tue, 10/20/09, Glenn Burt glenn.b...@glbcc.com wrote:

 From: Glenn Burt glenn.b...@glbcc.com
 Subject: Re: [RE-wrenches] AC Coupled Re-visited
 To: 'RE-wrenches' re-wrenches@lists.re-wrenches.org
 Date: Tuesday, October 20, 2009, 2:13 PM
 
 
 
  
  
 
 
 
 
 
 
 
  
 
 
 
 SMA recently told me that the
 recommended Ah of the battery bank
 is related to the amount of PV and connected
 inverters. 
 
 They recommended a 500Ah bank
 with a 5kW PV SB, and a 600Ah bank
 with a 6kW PV SB. 
 
 100Ah to 10,000Ah are the
 supported capacities. 
 
    
 
 I don’t believe you need
 to have a separate battery bank
 with two SI’s. I have been told they can share one.
 One SI is programmed
 as the master  of course they are data commed together
 so they can talk. 
 
    
 
 -Glenn 
 
    
 
 
 
 
 
 From:
 re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
 Behalf Of Mark
 Frye
 
 Sent: Tuesday, October 20, 2009 2:42 PM
 
 To: 'RE-wrenches'
 
 Subject: Re: [RE-wrenches] AC Coupled
 Re-visited 
 
 
 
 
 
    
 
 Thanks Kent. And so I understand
 more clearly, in the case of 2 SIs
 as you describe, each SI has it's own battery bank, and
 the solar would be
 split between the two. 
 
   
 
 Considering the charging capacity
 of the SI, what would you say is
 the largest battery bank size for each SI to insure an
 effective C
 value? 
 
  
 
 Mark Frye
 
 
 Berkeley Solar
 Electric Systems 
 
 303 Redbud Way
 
 
 Nevada
 City,  CA 95959 
 
 (530) 401-8024
 
 
 www.berkeleysolar.com   
 
 
 
   
 
 
 
    
 
 
 
 
 
 
 
 From: re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
 Behalf Of Kent
 Osterberg
 
 Sent: Tuesday, October 20, 2009 11:10 AM
 
 To: glenn.b...@glbcc.com; RE-wrenches
 
 Subject: Re: [RE-wrenches] AC Coupled
 Re-visited 
 
 In off-grid mode the Sunny Island uses
 frequency shift power
 control to reduce the output of the Sunny Boy inverters and
 thereby regulate
 the battery voltage.  At some frequency shift (+1, or
 2, or 3 Hz, I'm not
 sure) the output of the SB is reduced by 100%. 
 It's proportional so that
 1/2 as much frequency shift gives a 50% reduction in the SB
 output.  To
 keep clocks accurate, the Sunny Island later shifts the
 frequency a negative
 amount, but the SB inverters ignore that.  For a grid
 backup system, a
 RS-485 cable is required so the Sunny Island can activate
 (or deactivate) the
 frequency shift power control capability of the SB.
 
 
 
 You need to stack two SI inverters to get 240-vac, but that
 will allow you to
 have a 10-kW of grid backup power with up to 12-kW of
 solar.  If you need
 more, you can stack four of SI inverters.
 
 
 
 Kent Osterberg
 
 Blue Mountain Solar, Inc.
 
 
 
 
 
 Glenn Burt wrote:  
 
 Our installations of Sunny
 Islands (SI) with Sunny Boys (SB)
 have always used the recommended RS-485 communications
 between all units
 involved. This with reprogramming the SB’s to be able
 to switch to
 off-grid mode per the SI instructions allows a more
 integrated system. 
 
 We have had problems with the
 OB PSX-240 and stepping up the 120
 to 240 for the crit load panel (where the SB’s
 connect) when the site has
 slightly high AC voltages. The SB pushes the existing ACV
 higher, then it goes
 out of UL spec  disconnects. Also the SB is now
 sensitive to imbalance on
 L1  L2 because of the neutral sensing – we had a
 customer where the
 SB was disconnecting due to this as well… 
 
 I thought the freq shifting was
 to allow other non-SMA inverters
 to be controlled when batteries were full? 
 
 Where is the SMA rep on this
 list? 
 
 -Glenn 
 
 
 
 From: re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org]
 On Behalf Of Kirpal Khalsa
 
 Sent: Tuesday, October 20, 2009 12:05 PM
 
 To: RE-wrenches
 
 Subject: Re: [RE-wrenches] AC Coupled
 Re-visited 
 
 
 
 Greetings..it is my understanding
 that the Sunny Island
 coupled with Sunny Boys is able to taper charge in an AC
 coupled system as the
 2 inverters are able to communicate with each other and the
 Sunny Island alters
 the frequency input of the Sunny Boys and lowers the total
 output of the Sunny
 Boys to match the needs of the battery bankthis is
 SMA's method of not
 using their chargerthey simply alter the
 amount of available AC
 input into the AC to DC converter present in the Sunny
 Island.This logic is
 what

Re: [RE-wrenches] AC Coupled Re-visited

2009-10-21 Thread Jeff Yago
There have been some good advice related to battery bank sizing and a better 
description of how Sunny Islands work with SunnyBoys, but I am afraid we are 
getting away from my original post that started this and that was:

Since a battery based inverter has a battery charging section and all kinds of 
software control over the charging process when connected to the grid, why does 
the battery charging process go wild when the grid is down and the AC power 
is being backfed from a separate AC coupled inverter.  Also, why do we keep 
having to field wire and program an added power relay or a separate diversion 
load relay to prevent over-charging and destroying an AGM battery bank because 
the battery charging process suddenly has no clue how to charge the battery 
bank.

Yes, the Sunny Island varies frequency which will cause an AC coupled SunnyBoy 
to be faked out and drop off line to avoid overcharging the battery bank, but 
it seems to me this is all just software programming, so why can't any inverter 
manufacturer simply control battery charging no matter where the AC power is 
coming from?  Why can't grid tie inverters used in an AC coupled application 
have the software to recognize a full battery condition and stop charging 
without having to drop off line on an out of limit grid condition and then 
cycle through the 5 minute wait? 

I am not an electronics engineer, but I don't see where any hardware changes 
are required, just some added software to select during initial setup.  Many of 
you may not deal with battery based systems, but half of our systems are and AC 
coupled is a great way to avoid long low voltage DC wire run losses.   We 
select generator type from a setup menu, how about Press 1 for standard 
inverter setup, press 2 for AC coupling.

Jeff Yago

_
Netscape.  Just the Net You Need.
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC Coupled Re-visited

2009-10-21 Thread boB Gudgel

Jeff Yago wrote:

There have been some good advice related to battery bank sizing and a better 
description of how Sunny Islands work with SunnyBoys, but I am afraid we are 
getting away from my original post that started this and that was:

Since a battery based inverter has a battery charging section and all kinds of software 
control over the charging process when connected to the grid, why does the battery 
charging process go wild when the grid is down and the AC power is being 
backfed from a separate AC coupled inverter.  Also, why do we keep having to field wire 
and program an added power relay or a separate diversion load relay to prevent 
over-charging and destroying an AGM battery bank because the battery charging process 
suddenly has no clue how to charge the battery bank.
  


Because, people are using these inverters in ways they were not really 
meant to be used.   It can be made to work, but the inverter is not 
aware of the battery voltage in this mode

of operation

Actually, another way to look at this is to put the onus on the grid tie 
inverter rather than the battery based inverter, providing the reference 
grid, to
be able to easily turn its power level down.   SMA just happens to have 
a way to do this in a pretty slick way.


 The regular battery based inverter, like the FX or Magnum, etc,  is 
bidirectional.  When the grid-tie inverters voltage gets pushed up
because the battery based inverter has nowhere to put that energy, the 
AC voltage rises and so the DC battery voltage side must rise

as well.

That is, unless some inverter like the SI tells the grid tie inverter to 
lower its output power, the grid tie inverters' voltage will try to rise to
try and sell more power to the grid.But there is no grid when 
the batteries are full, so the grid tie inverters' AC voltage goes out

of UL range, and goes off line.

Yes, the Sunny Island varies frequency which will cause an AC coupled SunnyBoy to be faked out and drop off line to avoid overcharging the battery bank, but it seems to me this is all just software programming, so why can't any inverter manufacturer simply control battery charging no matter where the AC power is coming from? 
Other's could do this too, if they know what Grid-tie inverter is that 
they are tied to and how to control it (like varying frequency).   
SMOP Simple Matter
Of Programming as they say.   That is, ~IF~ the grid-tie inverter can be 
turned down.  This is the best way.   The battery based inverter can not 
use the energy.
It can't just keep the AC voltage at 120V and the battery voltage down 
if the grid tie inverter is trying to raise that AC voltage by trying to 
sell to it.


Otherwise, all the battery based inverter can do is to turn off.  Then, 
of course, the reference for the grid tie inverter goes off, and it must 
wait another

5 minutes after the battery based inverter starts inverting again.

 Why can't grid tie inverters used in an AC coupled application have the software to recognize a full battery condition and stop charging without having to drop off line on an out of limit grid condition and then cycle through the 5 minute wait? 
  


It's because it's not a charger at this point... It's a bi-directional 
inverter.



I am not an electronics engineer, but I don't see where any hardware changes are 
required, just some added software to select during initial setup.  Many of you may not 
deal with battery based systems, but half of our systems are and AC coupled is a great 
way to avoid long low voltage DC wire run losses.   We select generator type from a setup 
menu, how about Press 1 for standard inverter setup, press 2 for AC coupling.
  


It's kind of like when your stomach is full, you have to stop being fed, 
otherwise you get real sick.  (sort of)


boB






Jeff Yago

_
Netscape.  Just the Net You Need.
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


  


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC Coupled Re-visited

2009-10-20 Thread Jeff Yago
Wehave completed several totally different AC coupled systems using different inverters, due to large ground mounted arrays that had to be located a great distance from inverter-battery-generator-grid BAS, which are working just fine even with the mis-match of inverter brands. The SunnyBoy seems to not care what its connected to or how, as it just keeps doing what it does and if a relay cuts off its connection to the grid when the battery voltage goes high then it just waits and re-connects when the grid is back or the battery voltage drops.

What I am botheredby is the need to custom design a power relay circuit on each project whichtakes lots of fine-tuning of setpoints to get everything to work correctly. If you have not done one the problem is simple - when you backfeed the AC output from a remote grid-tie inverter "through" the AC side of a battery based inverter, everything works great and the solar AC just passes straight through the sub-panel, back throught the battery inverter, back into the grid. However, when thegrid is down and the battery-inverter is no longer receiving (or sending) power from the grid, for some reason I cannot begin to understand, any AC being fed from the solar inverter goes straight into battery charging with absolutely no limit on charge rate or charge limit, and if you do not add a relay to dis-connect or shut-down the solar inverter you can quickly destroy a bank of AGM batteries if there are no major system loads as it just keeps charging and charging.

I am not an electronics engineer, but if the battery is being charged by the battery charger built into the inverter, I just do not see why the same battery charger suddenly has no clue that the battery is being overcharged when its now receiving AC power from a different source. I think with larger and larger arrays being installed as module costs fall, higher DC array string voltges to reduce wire costs, and more people worried about grid reliability, there would be a good market niche for an inverter that can properly charge a battery bank regardless of which way the AC power comes into the charger section. Whats the problem?

Jeff Yago
DTI SolarNetscape. Just the Net You Need.___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC Coupled Re-visited

2009-10-20 Thread Mick Abraham
Hi, All~

On an AC coupled system as Jeff describes, the battery charge circuitry on
the battery based inverter is not even participating.

A straight pure sine inverter...with no charger function built in...would
also charge the battery if AC coupled to a SunnyBoy with no grid
available. The charge is just the inverter's way of dealing with back EMF.

I agree that better control over that recharge is an important area; I
hope somebody is working on that. It's true that the wild card recharge
only occurs if grid goes away but as Jeff mentions, it only takes a few
times of crummy end of charge management to ruin a nice set of sealed
batteries.

Mick Abraham, Proprietor
www.abrahamsolar.com

Voice: 970-731-4675


On Tue, Oct 20, 2009 at 9:21 AM, Jeff Yago jry...@netscape.com wrote:

 We have completed several totally different AC coupled systems using
 different inverters, due to large ground mounted arrays that had to be
 located a great distance from inverter-battery-generator-grid BAS, which are
 working just fine even with the mis-match of inverter brands.  The SunnyBoy
 seems to not care what its connected to or how, as it just keeps doing what
 it does and if a relay cuts off its connection to the grid when the battery
 voltage goes high then it just waits and re-connects when the grid is back
 or the battery voltage drops.

 What I am bothered by is the need to custom design a power relay circuit on
 each project which takes lots of fine-tuning of setpoints to get everything
 to work correctly.  If you have not done one the problem is simple - when
 you backfeed the AC output from a remote grid-tie inverter through the AC
 side of a battery based inverter, everything works great and the solar AC
 just passes straight through the sub-panel, back throught the battery
 inverter, back into the grid.  However, when the grid is down and the
 battery-inverter is no longer receiving (or sending) power from the grid,
 for some reason I cannot begin to understand, any AC being fed from the
 solar inverter goes straight into battery charging with absolutely no limit
 on charge rate or charge limit, and if you do not add a relay to dis-connect
 or shut-down the solar inverter you can quickly destroy a bank of AGM
 batteries if there are no major system loads as it just keeps charging and
 charging.

 I am not an electronics engineer, but if the battery is being charged by
 the battery charger built into the inverter, I just do not see why the same
 battery charger suddenly has no clue that the battery is being overcharged
 when its now receiving AC power from a different source.  I think with
 larger and larger arrays being installed as module costs fall, higher DC
 array string voltges to reduce wire costs, and more people worried about
 grid reliability, there would be a good market niche for an inverter that
 can properly charge a battery bank regardless of which way the AC power
 comes into the charger section.  Whats the problem?

 Jeff Yago
 DTI Solar


 --
 Netscape.  Just the Net You Need.

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC Coupled Re-visited

2009-10-20 Thread Kirpal Khalsa
Greetings..it is my understanding that the Sunny Island coupled with
Sunny Boys is able to taper charge in an AC coupled system as the 2
inverters are able to communicate with each other and the Sunny Island
alters the frequency input of the Sunny Boys and lowers the total output of
the Sunny Boys to match the needs of the battery bankthis is SMA's
method of not using their chargerthey simply alter the amount of
available AC input into the AC to DC converter present in the Sunny
Island.This logic is what encouraged me to select SMA's for an AC
coupled design rather than mixing brands of battery-less and battery based
inverters.in a mixed brand scenario there is no communication other than
an on/off command so no regulation is available.My understanding may be
flawed--please correct me if so
Another way for mixed brands to AC couple and provide some charge control
would be to have an AC dumpload on the AC input side of the battery based
inverter to suck up some of the excess power from the GT inverters so not as
much power is available for battery charging.This dumpload would be
voltage based and in a mixed brand system would add more relays to the
mix...in many cases there may not be that many auxillary outputs available
to connect relays to.
I would like to see more GT inverter companies make compatible battery based
inverters..One idea is for micro inverters to be paired with the battery
based inverters and when less power was needed to facilitate a taper charge
one solar panel at a time could be switched off..effectively providing a
smaller available charge current to help with the taper charging.

-- 
Sunny Regards,
Kirpal Khalsa
NABCEP Certified Solar PV Installer
Renewable Energy Systems
www.oregonsolarworks.com
541-218-0201 m
541-592-3958 o

On Tue, Oct 20, 2009 at 8:34 AM, Mick Abraham m...@abrahamsolar.com wrote:

 Hi, All~

 On an AC coupled system as Jeff describes, the battery charge circuitry
 on the battery based inverter is not even participating.

 A straight pure sine inverter...with no charger function built in...would
 also charge the battery if AC coupled to a SunnyBoy with no grid
 available. The charge is just the inverter's way of dealing with back EMF.

 I agree that better control over that recharge is an important area; I
 hope somebody is working on that. It's true that the wild card recharge
 only occurs if grid goes away but as Jeff mentions, it only takes a few
 times of crummy end of charge management to ruin a nice set of sealed
 batteries.

 Mick Abraham, Proprietor
 www.abrahamsolar.com

 Voice: 970-731-4675


 On Tue, Oct 20, 2009 at 9:21 AM, Jeff Yago jry...@netscape.com wrote:

 We have completed several totally different AC coupled systems using
 different inverters, due to large ground mounted arrays that had to be
 located a great distance from inverter-battery-generator-grid BAS, which are
 working just fine even with the mis-match of inverter brands.  The SunnyBoy
 seems to not care what its connected to or how, as it just keeps doing what
 it does and if a relay cuts off its connection to the grid when the battery
 voltage goes high then it just waits and re-connects when the grid is back
 or the battery voltage drops.

 What I am bothered by is the need to custom design a power relay circuit
 on each project which takes lots of fine-tuning of setpoints to get
 everything to work correctly.  If you have not done one the problem is
 simple - when you backfeed the AC output from a remote grid-tie inverter
 through the AC side of a battery based inverter, everything works great
 and the solar AC just passes straight through the sub-panel, back throught
 the battery inverter, back into the grid.  However, when the grid is down
 and the battery-inverter is no longer receiving (or sending) power from the
 grid, for some reason I cannot begin to understand, any AC being fed from
 the solar inverter goes straight into battery charging with absolutely no
 limit on charge rate or charge limit, and if you do not add a relay to
 dis-connect or shut-down the solar inverter you can quickly destroy a bank
 of AGM batteries if there are no major system loads as it just keeps
 charging and charging.

 I am not an electronics engineer, but if the battery is being charged by
 the battery charger built into the inverter, I just do not see why the same
 battery charger suddenly has no clue that the battery is being overcharged
 when its now receiving AC power from a different source.  I think with
 larger and larger arrays being installed as module costs fall, higher DC
 array string voltges to reduce wire costs, and more people worried about
 grid reliability, there would be a good market niche for an inverter that
 can properly charge a battery bank regardless of which way the AC power
 comes into the charger section.  Whats the problem?

 Jeff Yago
 DTI Solar


 --
 Netscape.  Just the Net You Need.

 

Re: [RE-wrenches] AC Coupled Re-visited

2009-10-20 Thread Jeff Yago
it is my understanding that the Sunny Island coupled with Sunny Boys is able to taper charge in an AC coupled system as the 2 inverters are able to communicate with each other and the Sunny Island alters the frequency input of the Sunny Boys and lowers the total output of the Sunny Boys to match the needs of the battery bank

Kirpal Khalsa
-
Yes, if we usea Sunny Island AC coupled with a SunnyBoy we would not have the batterycharging problem, but remember, the SunnyBoy is 240 VAC and the Sunny Island is 120VAC which I also find is just has expensive to match up by having to installan external step-down transformer so I still feel inverter manufacturers are missing an opportunity to provide a needed product feature that nobody is providing..

Jeff Yago
DTI SolarNetscape. Just the Net You Need.
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC Coupled Re-visited

2009-10-20 Thread Phil Undercuffler
Kirpal,


You’ve got it summed up pretty well, although I would add that you need to
use RS485 cards and cabling between the SBs and the SI Master to get
regulated charging – the comm. allows the SI to send a handshake to the SB,
telling the SB to go into “off grid” mode and accept wider voltage and
frequency swings whenever the grid is not present.   Kent sums up this
control mechanism very succinctly below.


The biggest challenge when mixing brands is dealing with the 300 second
timeout after grid disturbance (what I call 5 minute PWM) make for less than
ideal system operation.  There needs to be a better way to regulate power
than kicking the string inverter offline.



Imagine, say, a 7kW array pumping energy into the home on a beautiful sunny
day.  The grid goes down, but the battery based inverter (BB) picks up the
slack and the grid-tied batteryless inverter (GT) stays online.  Home is
drawing less power than the array’s output (~6kW worth), and the batteries
are full.  Battery voltage hits the regulation voltage, and the BB inverter
(or the voltage controlled switch) activates a relay to open the circuit to
the GT inverter, effecting a blackout on that circuit.  Suddenly the BB
inverter and the battery bank is hit with the full 6kW of load.  The
batteries are a little undersized because that was the easiest portion of
the system to cut costs on, and they’re a little old and dried out from
years of sitting in an uncooled garage, so their voltage sags under the
load.  The voltage controlled switch senses the drop, and closes the relay
to the GT.  However, the GT has to stay offline for another 299 seconds and
the battery voltage continues to fall…..



I’ve been worried about just this scenario for some time, especially as
systems age.  Therefore, I’ve been suggesting to anyone interested in using
mixed brands of inverters (or those who don’t want to use RS485
communications with SB/SI combos) that they strongly consider installing a
diversion load and controller capable of absorbing at least the majority of
the expected surplus energy.  A blackout relay can be used as a secondary
control mechanism.  I think that this is going to provide the most reliable
operation, ultimately.



To answer the question about number of inverters, the SMA 5048U supports
parallel operation of up to 4 inverters on a single phase system, up to 4
inverters on a split-phase system, or three inverters on a 3-phase system --
all connected to one battery bank.  The PV can come through any number of SB
inverters, but they would all be connected to the same protected load panel
served by the SI.  This is one cluster.  The rule of thumb John Berdner
passed along years ago was up to 2kW of PV for every 1kW of SI.  If you can
break the load into multiple clusters, the system can be any size -- you
just run multiple clusters side by side independently.  If the loads can't
be separated, then you need to look at using the Multi-cluster box, but
that's not yet Listed or even technically available in the US.  But if the
job is *really *that big, you're playing in a whole 'nother ballpark.
Definitely not the job to take on for your first battery based project.





Phil Undercuffler

Director, Battery-based and Off-grid

Distribution Sales Group

*Conergy*

*Our World Is Full of Energy*

1730 Camino Carlos Rey Suite 103

Santa Fe, NM  87507

p.undercuff...@conergy.us

Direct | 505.216.3841

Toll Free | 888.396.6611 x4841

Fax | 505.473.3830

www.conergy.us



Phil Undercuffler






On Tue, Oct 20, 2009 at 1:38 PM,
re-wrenches-requ...@lists.re-wrenches.orgwrote:

 Send RE-wrenches mailing list submissions to
re-wrenches@lists.re-wrenches.org

 To subscribe or unsubscribe via the World Wide Web, visit

 http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org
 or, via email, send a message with subject or body 'help' to
re-wrenches-requ...@lists.re-wrenches.org

 You can reach the person managing the list at
re-wrenches-ow...@lists.re-wrenches.org

 When replying, please edit your Subject line so it is more specific
 than Re: Contents of RE-wrenches digest...

 When responding to posts within the Digest, be sure to restore the Subject:
 line to the original, and please edit out any extraneous lines from the
 quoted message.

 Today's Topics:

   1. Re: AC Coupled Re-visited (Walt Ratterman)


 -- Forwarded message --
 From: Walt Ratterman wratter...@sunenergypower.com
 To: glenn.b...@glbcc.com, 'RE-wrenches' 
 re-wrenches@lists.re-wrenches.org
 Date: Tue, 20 Oct 2009 12:37:04 -0700
 Subject: Re: [RE-wrenches] AC Coupled Re-visited

 Glenn:



 This is correct on the battery bank separation.



 You don’t split out the battery banks until you reach a “cluster”.  For
 example, one three phase setup is a cluster.  If you have two, three-phase
 setups – you have two clusters – and two battery banks.



 And…I think if you check through the charging parameters, you will find

Re: [RE-wrenches] AC Coupled Re-visited

2009-10-20 Thread Allan Sindelar
Phil,

Good advice. Assuming 48V and a large system, what would you use as a
diversion load and controller in this application? As I understand it, this
would be a DC diversion load, such as a wind gennie air heater, that would
be gradual, resistive, and noncritical for occasional use in this rare
scenario.

 

Thank you.

 

Allan Sindelar

al...@positiveenergysolar.com

NABCEP Certified Photovoltaic Installer

EE98J Journeyman Electrician

Positive Energy, Inc.

3201 Calle Marie

Santa Fe, New Mexico 87507

505 424-1112

www.PositiveEnergySolar.com http://www.positiveenergysolar.com/ 

Kirpal, 

The biggest challenge when mixing brands is dealing with the 300 second
timeout after grid disturbance (what I call 5 minute PWM) make for less than
ideal system operation.  There needs to be a better way to regulate power
than kicking the string inverter offline.

Imagine, say, a 7kW array pumping energy into the home on a beautiful sunny
day.  The grid goes down, but the battery based inverter (BB) picks up the
slack and the grid-tied batteryless inverter (GT) stays online.  Home is
drawing less power than the array's output (~6kW worth), and the batteries
are full.  Battery voltage hits the regulation voltage, and the BB inverter
(or the voltage controlled switch) activates a relay to open the circuit to
the GT inverter, effecting a blackout on that circuit.  Suddenly the BB
inverter and the battery bank is hit with the full 6kW of load.  The
batteries are a little undersized because that was the easiest portion of
the system to cut costs on, and they're a little old and dried out from
years of sitting in an uncooled garage, so their voltage sags under the
load.  The voltage controlled switch senses the drop, and closes the relay
to the GT.  However, the GT has to stay offline for another 299 seconds and
the battery voltage continues to fall...

I've been worried about just this scenario for some time, especially as
systems age.  Therefore, I've been suggesting to anyone interested in using
mixed brands of inverters (or those who don't want to use RS485
communications with SB/SI combos) that they strongly consider installing a
diversion load and controller capable of absorbing at least the majority of
the expected surplus energy.  A blackout relay can be used as a secondary
control mechanism.  I think that this is going to provide the most reliable
operation, ultimately.

Phil Undercuffler

Director, Battery-based and Off-grid

Distribution Sales Group

Conergy 

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org