Re: [RE-wrenches] DC Disconnect for first responders

2023-02-20 Thread Brian Mehalic via RE-wrenches
480.7 is Disconnect Methods, and addresses different scenarios and voltages (A) is for batteries "with a voltage over 60 volts dc" requiring a disconnect accessible to and within sight of the battery (B) is in regards to 1- and 2-family dwellings, and doesn't specify a voltage, just that an

Re: [RE-wrenches] DC Disconnect for first responders

2023-02-20 Thread James Jarvis via RE-wrenches
Did they ever explain why they were requiring it on a nominal 48 volt system? NEC 480.7(B) (from memory, I think that is the right article) says it is for nominal voltage of 60 volts or higher. IE your 48 volt system is exempt. Jay pointed this out on February 3rd. -James Jefferson Jarvis APRS

[RE-wrenches] DC Disconnect for first responders

2023-02-20 Thread William Miller via RE-wrenches
Friends: Here is how this resolved for my upcoming project: I submitted a request to the building department to waive the requirement for a DC disconnect. I based the justification on the need to keep a pressure pump for the fire sprinklers and a fire alarm operational. I will supply an