Re: [RE-wrenches] Solar System Certification

2009-12-21 Thread toddcory
So you can get others to install your designs? I would never touch materials I do not sell, or install a system I did not design... and I am amazed anyone would. Todd On Monday, December 21, 2009 12:56pm, Brian White bri...@eagleroofing.com said: Thanks to all who have posted. To

Re: [RE-wrenches] Link 10 question

2010-01-07 Thread toddcory
There is a bug in the last batch of these meters before they were discontinued by Xantrex. I have heard about this from many others, but Xantrex claimed to know nothing about it... and since the meter is no longer available, you either replace it with an overly complicated (for most customers)

Re: [RE-wrenches] kwh meters

2010-01-28 Thread toddcory
Here is a repost of this information from 20067 Todd Ok, I called Jake and he forwardedme to Brent Carper (253-395-6818) who works in the Puget Sound Energymetering department. I had a long conversation with him about how tometer battery based, grid tied inverters. The form 12s meter

[RE-wrenches] Mitsubishi module needed

2010-02-16 Thread toddcory
Hey folks, I'm looking for a Mitsubishi 185 (black frame if possible) to replace a broken one on a customers rack. Thanks, Todd ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options settings:

Re: [RE-wrenches] single string of batts: must the interc onnects beinverter size cables?

2010-02-22 Thread toddcory
What is a golf cart battery? Todd On Monday, February 22, 2010 12:53pm, R Ray Walters r...@solarray.com said: These are grid tie with battery backup systems. All inspected. Personally, I think that we should have OCP on each series string, but that's a whole nother can o' worms. Most sealed

Re: [RE-wrenches] Fwd: single string of batts: must the interconnects beinverter size cables?

2010-02-24 Thread toddcory
My home system's GVFX3648 maxes out at around 2.8 to 2.9 kW @ 80 degrees F. If I push it harder, it overheats. While they are rated at 3600 watts, they cannot do this continuously with ambient temps above ~40 F. Todd On Wednesday, February 24, 2010 2:25pm, Michael Welch

Re: [RE-wrenches] Source for 24v DC clock timer

2010-02-25 Thread toddcory
I think Backwoods Solar used to carry these. Todd On Thursday, February 25, 2010 10:12am, jason pozner zzyyzz...@gmail.com said: Hi wrenches, Does anyone know a good source for a reliable, reasonably priced 24v DC clock timer 5-10A run off a relay. We are powering heat tape to mitigate a

Re: [RE-wrenches] Transformerless inverters require special plug leads on the PV modules, right?

2010-02-25 Thread toddcory
USE2 Todd On Thursday, February 25, 2010 10:54am, Mick Abraham m...@abrahamsolar.com said: ...and...the next time I buy #10 sunlight resistant wire for making up my own plug extensions...should I buy a more exotic wire type and how do I know what will work? Thanks, Mick Abraham,

Re: [RE-wrenches] GVFX temperatures

2010-02-26 Thread toddcory
elling wattage) runs ~87%.Hope this is helpful.ToddOn Friday, February 26, 2010 9:59am, "Michael Welch" michael.we...@re-wrenches.org said: From: j...@greenhousepc.com toddcory at finestplanet.com writes: How high have the temp counts on your transformer gotten? I'd pay closer attention to the FE

Re: [RE-wrenches] Fwd: GVFX temperatures (was: single string of batts:)

2010-02-26 Thread toddcory
PS I was told the GVFX will NOT back off the power in an overtemp situation. The inverter will just shut down if it gets too hot. Todd On Friday, February 26, 2010 9:59am, Michael Welch michael.we...@re-wrenches.org said: From: j...@greenhousepc.com If the temperatures get out of hand,

Re: [RE-wrenches] Fwd: Re: GVFX temperatures

2010-02-28 Thread toddcory
Thankfully my MX60's software is old enough to still have an option to control it's aux output by current. Anything over 50 amps turns on auxiliary fans. Not sure why Outback eliminated this useful option in more recent upgrades. Todd On Sunday, February 28, 2010 10:00am, Michael Welch

Re: [RE-wrenches] apollo charge controllers

2010-03-18 Thread toddcory
So do the charge controller and amp hour meter communicate so they agree on when the batteries are fully charged? Todd On Wednesday, March 17, 2010 12:02pm, R Ray Walters r...@solarray.com said: We have a couple out in the field. A bit of hassle to upgrade the firmware at first, but Apollo

Re: [RE-wrenches] DC wire sizing

2010-04-09 Thread toddcory
Has anyone included the extra racking costs to add additional modules used to compensate for wire loss? Todd On Friday, April 9, 2010 10:46am, R Ray Walters r...@solarray.com said: All our economic analysis is based on a 20 to 25 year life. Safety first, but then good design is to spend

Re: [RE-wrenches] monitor for SW4048 grit interactive system

2010-04-21 Thread toddcory
A dual system will need two meters... one to keep track of each leg. Outback has details on their web page about how to configure these, or if you like contact me off list for repostings of messages from the last few times this went around. Todd On Wednesday, April 21, 2010 10:08am, Dana

Re: [RE-wrenches] FM60/rectifier for gen charging

2010-04-27 Thread toddcory
Ahh, the old DT kludge. I have done this here at my home because the GFX only has one AC input... grr... so this is a good workaround. As long as you take the 120 or 240 down to ~ 60 volts, you will be fine. My 3 kW xmfr (got used online - very heavy and expensive) has a 240 volt input/outputs

[RE-wrenches] E-meter/Link-10 prescaler

2010-04-27 Thread toddcory
I am looking for any old stock or leads for the now discontinued E-meter/Link-10 prescaler. 0-100 volts. Thanks, Todd ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options settings:

Re: [RE-wrenches] FM60/rectifier for gen charging

2010-04-27 Thread toddcory
Don't you think the transformer is good for isolation? Todd On Tuesday, April 27, 2010 4:26pm, ryan r...@solar4maine.com said: I have done this a couple times. I have done this with a MX60 and a MidNite Classic the beauty with the Classic is you can eliminate the Transformer. I Simply

Re: [RE-wrenches] Solarex module match question

2010-04-29 Thread toddcory
UNLESS you are moving that power any distance. I have a 20+ year old rack of 12, Solarex MSX-60's traveling 200' to the FM60. Wired in two strings of 6, allowed me to drop the wire size considerably! Todd On Thursday, April 29, 2010 1:44pm, R Ray Walters r...@solarray.com said: HI Allan I

[RE-wrenches] var/ power factor

2010-05-14 Thread toddcory
I have a question about my personal home system. It is an Outback battery based grid tie. My digital utility meter is capable of reading var and power factor. So often (like just now) when I read this it is not even close to unity. Today's reading was 1.57 VAR, 56 PF. What is going on here? Am

Re: [RE-wrenches] Help me do the math: amortized cost per amp-hour

2010-06-10 Thread toddcory
I agree with that for floating flooded, wet cell lead antimony batteries... but flooded lead calcium cells are a more appropriate choice for floating banks on grid ties with backup. No cycling is necessary. Todd On Thursday, June 10, 2010 12:32pm, Bell, Steve sb...@sunwize.com said:I also

Re: [RE-wrenches] Interstate UL-16 HC problem

2010-06-30 Thread toddcory
proper absorb times (do the math) Can you talk more about this please. Todd Sent from Finest Planet WebMail. ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options settings:

Re: [RE-wrenches] maximum efficiency module inquiry

2010-07-18 Thread toddcory
Hopefully, they are equally concerned about the energy efficiency of their home... but I be they aren't. Todd On Sunday, July 18, 2010 10:08am, Peter Parrish peter.parr...@calsolareng.com said: Hi Keith, A few que[#] stions: (Q1) How much is your client willing topay for the most

Re: [RE-wrenches] Net AC kW Derate Factor for Xantrex XW inverter and XW opinions

2010-08-24 Thread toddcory
I sell 2.8 kW with 4.5 kW STC going into a GVFX, which is 62% DC - AC efficiency. I can't imagine the XW being worse. Lead calcium wet cells take very little float current and rarely need watering. Todd On Tuesday, August 24, 2010 2:42pm, Jeff Oldham starpowe...@juno.com said: I remain shy

Re: [RE-wrenches] On Demand Heaters for SDHW

2010-09-17 Thread toddcory
repairable unit - you don't have to trash it every seven years (reported national average) My tank is 20 years old now. I change the anode every 3 years. Todd Sent from Finest Planet WebMail. ___ List sponsored by Home Power magazine List

Re: [RE-wrenches] Energy Tax Credits

2010-09-17 Thread toddcory
I recently read on the DSIRE web page that the 30% credit need not be the primary residence. Todd http://www.dsireusa.org/incentives/incentive.cfm?Incentive_Code=US37Fre=1ee=1 Federal Incentives/Policies for Renewables

Re: [RE-wrenches] paralleling amp hour meters on one shunt?

2010-10-01 Thread toddcory
Thanks everyone for the feedback on my question! Todd On Friday, October 1, 2010 9:32am, Larry Crutcher la...@starlightsolar.com said: Todd, The shunt is only providing a mV DC signal. In our showroom we have a working display wall of charge controllers and battery monitors (Blue Sky,

Re: [RE-wrenches] Battery capacity testers

2010-10-04 Thread toddcory
I know many on this list disagree, but this sounds SO typical for sealed batteries. It is why I never use em... never! If they are 5 years old, you are probably at the limit of their life. Replace em with flooded lead calciums and your customers (and you) will be happy for 20+ years. my .o2

Re: [RE-wrenches] Battery capacity testers

2010-10-04 Thread toddcory
The battery choice was the decision of the system owner. Since when does the customer make these decisions? Todd On Monday, October 4, 2010 6:36am, North Texas Renewable Energy Inc nt...@1scom.net said:  Todd I've heard the same arguement, as well as its inverse. The battery choice was

Re: [RE-wrenches] Battery capacity testers

2010-10-04 Thread toddcory
Perhaps James @ Surrette can chime in about the cost difference. I do not think flooded lead calciums are much more expensive then flooded lead antimony batteries. Todd On Monday, October 4, 2010 8:00am, jay peltz j...@asis.com said: HI Todd, I agree that the issue is probably dead

Re: [RE-wrenches] Battery capacity testers

2010-10-04 Thread toddcory
Lead cadmium or lead calcium? Again, I do not have the cycle chart handy, but hopefully James can post that. Todd On Monday, October 4, 2010 8:11am, Mark Frye ma...@berkeleysolar.com said: Todd, Can you give us a comparison of lead vs lead cadmium? My understanding is that lead cadmium

Re: [RE-wrenches] Battery capacity testers

2010-10-04 Thread toddcory
When I do a system, the customer is hiring me as the expert. If they want me to do something that won't work well, my reputation is on the line, and so they need to hire someone else. Todd On Monday, October 4, 2010 2:46pm, hol...@sbcglobal.net said:  Since when does the customer make these

Re: [RE-wrenches] Mounting Enphase when using S-5-PV Clamps

2010-10-20 Thread toddcory
I have the same question, only regarding pole mounts. Todd On Wednesday, October 20, 2010 8:06am, benn kilburn b...@daystarsolar.ca said: Mornin, I'm looking at mounting an Enphase M190 system on a standing seam metal roof and was considering using the S-5-PV clamps (as opposed to just the

Re: [RE-wrenches] Battery cell shorting

2010-10-23 Thread toddcory
I have a client right now doing a last ditch heavy equalizing cycle to try to save his 5 year old, 24 volt bank of 8 L-16's. One of the two series strings has a weak cell... so the other string is boiling away. He is charging for 2 hours with 2 hours rest to not overheat the charged cells. Too

Re: [RE-wrenches] NEC 690.74

2010-11-29 Thread toddcory
Did he ask to see the UL sticker on the batteries too? On Monday, November 29, 2010 5:07pm, Philip Boutelle philboute...@gmail.com said: Wrenches, We have a string of batteries being inspected by a local AHJ. In plan-check comments, I was asked to ensure that the flexible cable was

Re: [RE-wrenches] Bobier/Sun Selector LCB-20 PWM-30 Manuals Needed

2011-01-02 Thread toddcory
I don't have a manual, but I do have one of these on the PV direct pump that operates my SHW system. I can identify the wires if you like. Todd On Sunday, January 2, 2011 5:45pm, Exeltech exelt...@yahoo.com said: Hello Wrenches, I need copies of instruction/user's manuals for a Bobier Sun

Re: [RE-wrenches] NABCEP credits and code webinars

2011-01-04 Thread toddcory
Sunwise is having one this Thursday on code approved roof mounts. Todd On Tuesday, January 4, 2011 11:54am, gary easton g...@arp-solar.com said: Hello Wrenches, Anyone aware of webinars coming up approved for NABCEP's code related continuing education credits? Sent from Finest Planet

Re: [RE-wrenches] Barrel Roof Mounting

2011-01-22 Thread toddcory
The old armory building in Ashland, Oregon has a roof like this with PV on it. Do some research and see if you can determine what was done there. From my observation it looked like a classic rail mount system was used. Hope this helps, Todd On Saturday, January 22, 2011 8:40am, Aaron

Re: [RE-wrenches] Roofers installing solar = creative, new installation methods

2011-01-28 Thread toddcory
I had a potential customer call me last week saying he had just bought a bunch of panels and those micro chip things (enphase inverters) so he could get a end of the year tax break. He wanted me to come and install it for him. I told him my work includes a comprehensive energy audit to gather

Re: [RE-wrenches] questions about solar charging 72v UPS

2011-02-10 Thread toddcory
I see the FM60 had a 60 volt option. Why not just use a single one at that battery setting for charging the battery bank? Todd On Thursday, February 10, 2011 9:44am, Darryl Thayer daryl_so...@yahoo.com said: Hi all I have attached a PDF of a charging scheme using Outback FM controllers.

Re: [RE-wrenches] Slow clocks

2011-04-04 Thread toddcory
I wasn't going to say anything, but electric clocks off-grid? really??? Todd On Monday, April 4, 2011 6:20pm, Kent Osterberg k...@coveoregon.com said: Kris, Even with generators using an electronic governor, the frequency changes with load. Also while inverters are stable their frequency

Re: [RE-wrenches] Heavy Duty Modules?

2011-04-13 Thread toddcory
Hi Doug, I had a customer's roof mount system break modules this spring after yet another record Mount Shasta snow event. This one brought 8' in 10 days. The situation here was 15 Evergreen 190 watt modules (rated for 80#/sq ft), on a DPW power rail mount, on a 6/12 pitch, comp roof. Ice

Re: [RE-wrenches] irrigation and direct solar

2011-04-17 Thread toddcory
How about looking into a more efficient pump first? Todd On Saturday, April 16, 2011 8:00pm, Darryl Thayer daryl_so...@yahoo.com said: That is 480 x 1.73 x40 A x.8 or 26 kW in the peak of the day, five or 6 big trackers, or about 50 kW of fixed array. ( I assure they want 40 amp

Re: [RE-wrenches] More on AC coupling - SI and SB

2008-11-26 Thread toddcory
What about the new Surrette FC420's? The latest SOLARPRO mag has a tiny blurb on them at the bottom of page 28. Two sets in parallel (630 a/h) would meat your criteria and would perform much better than sealed batteries. I have been beta testing a set here at home and they seem to be doing

Re: [RE-wrenches] A Wrench's computer

2009-04-10 Thread toddcory
I just purchased a MSI U100 netbook and love it. Fast cheap ($350.00). Todd On Friday, April 10, 2009 8:26am, Joel Davidson joel.david...@sbcglobal.net said: Wrenches, Some Wrenches include their notebook computer among their most valued tools. My 2001 IBM T23 notebook has served me well

[RE-wrenches] link-10/e-meter 0-100 prescaler

2009-04-13 Thread toddcory
Does anyone have any link-10/e-meter 0-100 volt prescalers in stock still? If so please contact me off list. Thanks, Todd ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options settings:

Re: [RE-wrenches] sales to-date

2009-05-30 Thread toddcory
Down about 70%. Todd On Saturday, May 30, 2009 11:06am, Marco Mangelsdorf ma...@pvthawaii.com said: Compared to the first five months of last year, how would any of you who care to respond compare your year-to-date sales in 2009? Thanks, marco Marco Mangelsdorf, President 69 Railroad

Re: [RE-wrenches] Separated frames on BP modules

2009-06-15 Thread toddcory
Its ok Nick... I feel the same way. My problems go back to when they bought out Solarex and never issued a recall for all those defective MSX 60's out there. Todd On Monday, June 15, 2009 10:10am, Nick Lucchese ni...@sierrasolar.com said: Oops, this was supposed just go to Andrew. Nick

Re: [RE-wrenches] Kohler 8.5 RES

2009-07-09 Thread toddcory
My dream! I hope someone knows of such a unit, cuz I'd love to know what to recommend to folks. Todd On Monday, July 6, 2009 9:16am, Drake Chamberlin drake.chamber...@redwoodalliance.org said: Thanks to all who have helped with this. The moving target ofgenerator function makes things a bit

Re: [RE-wrenches] Roof Loading request for help

2009-07-09 Thread toddcory
The problem here it about 5 years ago they upped the snow loadrequirements from 40 to 60 p/sf so ANY thing added to the roof needs astructural upgrade. Todd On Tuesday, July 7, 2009 9:59pm, Bill Brooks billbroo...@yahoo.com said: Allan, Check out my website at

Re: [RE-wrenches] Solar Installers Education

2009-07-19 Thread toddcory
Then there are the wholesale internet designers that sell DIY systems. These are usually put together by kids who have never done an installation, and who have completed some training course and design from behind a computer screen. I just hate to see this going on, but for many, this work is

Re: [RE-wrenches] Fwd: Grounding on a glacier??

2009-07-24 Thread toddcory
Re: [RE-wrenches] Fwd: Grounding on aglacier My understanding is that it saves cost to ground one of theconductors. Then you can use single pole switches, fuses andbreakers. If both of the circuit conductors are 'hot' then youwill need to use double pole everywhere. Why? A single pole switch

Re: [RE-wrenches] Fwd: Grounding on a glacier??

2009-07-25 Thread toddcory
If neither pole is grounded then both must be treated aspotentially hot. Only with regard to the other hot wire. If you do not reference one conductor to ground than the other one will not present any danger unless you are referenced to its mate... as in touching both wires at once.

Re: [RE-wrenches] Solar electric generation system seems to make noeconomic sense

2009-07-28 Thread toddcory
Its apples and oranges comparing coal power prices to renewables. Should a Lexus cost the same as a Kia? Todd On Monday, July 27, 2009 9:05am, Joel Davidson joel.david...@sbcglobal.net said:  All this figuring makes my head ache... I agree with Bob. If someone is willing to pay me to

Re: [RE-wrenches] Power Factor

2009-07-29 Thread toddcory
Power factor on DC? As far as I know, power factor / vars is an AC phenomena where current and voltage are out of phase. Todd On Wednesday, July 29, 2009 5:45pm, Ron Young solarea...@solareagle.com said: Can anyone point me in the direction to find the power factor for Sanyo HIT N 205

Re: [RE-wrenches] utility line voltage issues

2009-08-16 Thread toddcory
My line voltage often runs in the 250 VAC range. My grid tied Outback system used to go off-line when it got much higher than this, so I changed the settings to user and opened the window way up. Problem fixed. Todd On Sunday, August 16, 2009 10:06am, William Korthof wkort...@eesolar.com

Re: [RE-wrenches] Seasonal Adjusters

2009-08-16 Thread toddcory
Those massive pictures could have easily been resized and compressed to less then 100 K each. Todd; On Sunday, August 16, 2009 1:52pm, Bruce Geddes b.ged...@clear.net.nz said: For goodness sake, posting attachements of 2M or so. There was a discussion on this forum some months ago about

Re: [RE-wrenches] Installer's grant

2009-09-01 Thread toddcory
On Monday, August 31, 2009 8:57pm, Bill Brooks billbroo...@yahoo.com said: Roger, Why would a legitimate contractor argue against this reducedincentive (it is not a penalty at all)? This is simply acknowledging the factthat operating a business and providing a long-term system warranty

Re: [RE-wrenches] Installer's grant

2009-09-01 Thread toddcory
We have a local company who sells designed, packaged systems wholesale to the public. IMO, their designs are poor and the quality of the customer installs are equally suspicious. I support incentive and tax credits penalizing this kind of behavior with lower financial support. Todd On

Re: [RE-wrenches] XW6048 parts problem

2009-09-21 Thread toddcory
After swearing off brand X I did a XW system this last spring. The customer needed two AC inputs and unfortunately the GVFX topology still only has one. On the single occasion I called Xantrex to ask how to raise the sell (grid support) voltage the tech support person told me to do what I

Re: [RE-wrenches] Battery Charger

2009-09-28 Thread toddcory
I am curious how you connect a generator to the GVFX? It only has one AC input that us used for the grid. Todd On Monday, September 28, 2009 11:43am, Orion Thornton othorn...@solarips.com said: Wrenches, We recently installed a grid-tie battery backup system usingtwo Outback GVFX 3648

Re: [RE-wrenches] Outback Fware

2009-10-23 Thread toddcory
Thanks for saying that Ray. I also have been a huge Outback fan but have similar frustrations with why some problems have not been addressed, after all these years. The single AC input on the GVFX comes to mind. Todd On Wednesday, October 21, 2009 1:09pm, R Ray Walters r...@solarray.com

Re: [RE-wrenches] AC Coupled Re-visited

2009-10-23 Thread toddcory
So in essence, you had the PV's connected directly to the inverter's DC battery connection point. What did the MPPT charge controller do without the battery as a buffer? Did the efficiency go up on the system without batteries to keep charged? Todd On Wednesday, October 21, 2009 10:12am,

Re: [RE-wrenches] Name that solar module guessing game!

2009-10-23 Thread toddcory
My first modules had that kind of JB cover. Hoxan was the manufacturer. Do I win? Todd On Thursday, October 22, 2009 2:59pm, Mick Abraham m...@abrahamsolar.com said: Set the dials on the Wayback Machine, Wrenches! The modules which I wish to identify had bright blue polycrystal square cells,

Re: [RE-wrenches] Sync problem

2009-10-30 Thread toddcory
Hey Drake, Did you look in the mate warning/error menus to check voltage/frequency? Todd On Thursday, October 29, 2009 4:25pm, drake.chamber...@redwoodalliance.org said: Hello Wrenches, I was under the impression that he Honda EU series of inverter generators could synchronize with the

Re: [RE-wrenches] Outback-Honda Sync problem

2009-10-31 Thread toddcory
There is also the option of converting the genny's AC output to DC and running it through an MX60 as a rather rube goldberg way to interface a genny with a GFX inverter. I did this at home and it works great. Todd On Saturday, October 31, 2009 8:06am, Tump t...@hughes.net said: Drake I

Re: [RE-wrenches] SW 4024 now grid tie

2009-11-17 Thread toddcory
Here is an old 2001 posting from Bill Brooks... William, Marco, and Jeff C., Here is the method I found to be most effective: INVERTER SETUP (MENU 9) set to SELL BATTERY CHARGING (MENU 10) set ABSORPTION TIME to 0:00 on both machines. set MAX CHARGE AMPS to 1 amp on both machines. BATTERY

Re: [RE-wrenches] concord batteries

2009-11-30 Thread toddcory
As someone who has been doing off grid systems since 1985 I can say from experience, ALL sealed batteries are CRAP... especially in off grid applications. They are too fragile and do not last. Todd On Sunday, November 29, 2009 5:48pm, Conrad Geyser conr...@cape.com said: In the vein of us

Re: [RE-wrenches] Strings and series of batteries

2009-12-03 Thread toddcory
I am sure the reason for using gloves with grease is lithium based grease stinks like 90 weight. Who wants that on their hands? Todd On Thursday, December 3, 2009 1:21am, R Ray Walters r...@solarray.com said: I was just picking up on where everybody is located. The cold weather boys like

Re: [RE-wrenches] Battery Automatic Watering

2009-12-10 Thread toddcory
On grid or off grid Joel? If grid tied /w battery backup, use lead calcium wet cells. They only need watering about every 18 months. Todd On Wednesday, December 9, 2009 6:14pm, Joel Davidson joel.david...@sbcglobal.net said: Wrenches, We installed 48 each IBE 1-85N-15 cells (24 in series

Re: [RE-wrenches] Battery Automatic Watering

2009-12-10 Thread toddcory
I do not have these an any customer's systems yet. The data comes from my Surrette evaluation/beta test bank. All my future battery based/grid ties will get these though. Todd On Thursday, December 10, 2009 10:19am, jay peltz j...@asis.com said: HI Todd, Given the super long time between

Re: [RE-wrenches] Battery Automatic Watering

2009-12-10 Thread toddcory
Well said Jeff... like with auto genny starting systems... if the customer is not willing to be involved with flying their system, only insisting on some auto-pilot system... a crash is inevitable. Watering the batteries is an opportunity for the customer to be more involved with their system.

Re: [RE-wrenches] Battery Automatic Watering

2009-12-11 Thread toddcory
Not to take this thread too far into the land of metaphors, but I'm sure everyone knows that by the time a vehicle's oil pressure light comes on, severe engine damage has already been done. My point is, most of our current earthly problems are because people do not want to be bothered with

[RE-wrenches] installs/installers..

2011-05-07 Thread toddcory
Ahem, yes... right here in Mount Shasta. Thanks guys. Todd On Saturday, May 7, 2011 12:34pm, R Ray Walters r...@solarray.com said: Even a bad solar installer isn't going to use cut up extension cords; that install was DIY or a knowledgable inebriated neighbor. I lived in the backwoods

[RE-wrenches] pole mounts

2011-07-26 Thread toddcory
Wrenches, Fact or fiction: Adding concrete to the inside of a pole mount pipe makes it stronger. Thanks, Todd Sent from Finest Planet WebMail. ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options

[RE-wrenches] SIlicon energy modules

2011-07-27 Thread toddcory
Have you installed these Alex? I have specified them for a upcoming, local, grid-tied system here in heavy snow country because there is no frame to peel off from ice dams. The mounting system looks highly complicated/confusing. Can you (or any other list members who have worked with these)

Re: [RE-wrenches] SIlicon energy modules

2011-07-28 Thread toddcory
So I have to get factory training to install these??? It will be on a ~4/12 comp roof. Todd On Wednesday, July 27, 2011 10:34pm, Alex Cozine acdc.coz...@gmail.com said: Yes I have installed these modules. Yes they do have a proprietary racking system. To buy these modules I

Re: [RE-wrenches] Grounding system for a shack on a frozen lake?

2011-08-09 Thread toddcory
If the DC AC float from the ground, your clients will effectively be insulated from any current path unless they were to somehow touch both conductors simultaneously. Many countries do not reference one of their current carrying conductors to ground. Many people feel this is safer. You would

Re: [RE-wrenches] mechanical vs. electronic kwh meter

2011-08-12 Thread toddcory
I successfully litigated (with help from the PUC) our local utility company (PPL) for requiring a $500.00 fee (which violated the CA net metering law) to replace the bi-directional analog meter with a dual register digital one. I had a certification from the analog meter manufacturer stating

Re: [RE-wrenches] Large, off grid

2011-08-19 Thread toddcory
Yes... and we finally get the second AC input we have wanted for so long... the price? $13,000.00... wow Todd On Friday, August 19, 2011 2:35pm, Jeff Oldham starpowe...@juno.com said: Yes it does! From the Solar, Wind and Hydro powered office of Jeff Oldham/Regenerative SOLutions

[RE-wrenches] new outback inverter

2011-08-23 Thread toddcory
Wrenches, I posted an absurd price of $13K for the new Outback Radian inverter (GS 8048) a couple of days ago. It turns out that was a retail price for an installed system that I quickly googled. A more accurate price is around $6K. I am looking forward to wrench reviews of this new product.

Re: [RE-wrenches] Electric boiler usage?

2011-08-27 Thread toddcory
What was their previous heating source? Calculate the BTU's consumed from that source and convert that to kWh. If it was resistance electric previously look at the winter increase from the summer baseline on the old utility bills. Todd On Saturday, August 27, 2011 6:05am, Jesse Dahl

Re: [RE-wrenches] battery cycle life, US Battery

2011-09-17 Thread toddcory
What about the 2 volt L-16 versions? Has anyone had success with them for larger banks? I work alone and HUPs are too heavy to lift on my own... however 24, L-16's in one series string would be a hell of a battery bank too. Todd On Friday, September 16, 2011 1:03pm, Ray Walters

Re: [RE-wrenches] Heavy batteries

2011-09-18 Thread toddcory
My favorite technique is getting the customer to take one of the two handles while I take the other... but in a pinch, yes... I carefully life these alone. They do seem to get heavier as I get older... lol Todd On Sunday, September 18, 2011 10:31am, William Miller

Re: [RE-wrenches] evergreen modules

2011-09-21 Thread toddcory
I had a customer with the same need this spring... and we were able to get them through Evergreen. With the bankruptcy on now, that might be more difficult, but worth contacting them. I am sure they have the modules you need... just getting them to sell them to you (considering the business

Re: [RE-wrenches] High Temp Batteries

2011-09-22 Thread toddcory
Have you considered a burried, underground vault? We did this with broadcast equipment when I did that work years ago and it worked great at moderating high/low temp swings. Todd On Thursday, September 22, 2011 8:35am, Chris Daum ch...@oasismontana.com said: Dear Wrenches: I have

[RE-wrenches] ground

2011-09-29 Thread toddcory
Does anyone know if it is ok to use the rebar in a pole mount foundation as a ufer ground? I need to ask the inspector too, but thought I'd ask here first. Todd Sent from Finest Planet WebMail. ___ List sponsored by Home Power magazine List

[RE-wrenches] federal tax credit

2011-11-10 Thread toddcory
Wrenches, I got the following information from a customer who ran the federal tax credit by her accountant. As a double check... is this correct? Thanks, Todd My accountant wrote: The taxpayer claiming the credit must be the owner of the home. The value of these credits adjust

Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-11-16 Thread toddcory
I digress but... the best battery for grid tie with backup is not lead antimony, but lead calcuum. Surrette makes these too and they use next to no water and have a much longer warrantied life. Todd On Wednesday, November 16, 2011 6:52pm, Jeff Yago jry...@dtisolar.com said: No

Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-11-17 Thread toddcory
Hi Mark, I have been grid tied (zero energy since 2004) for 15 years. I used to live off grid before I moved here to this home 17 years ago. Todd On Thursday, November 17, 2011 12:36pm, Mark Frye ma...@berkeleysolar.com said: Todd, I thought you were totally off-grid. Mark

Re: [RE-wrenches] Convert Grid Tie SW4048 to Backup System; Add New Inverter, AC Coupled

2011-11-20 Thread toddcory
On Sunday, November 20, 2011 9:32am, Joel Davidson joel.david...@sbcglobal.net said: Wrenches, I answered Richard off-list, but other wrenches may find this information about old SW4048s and batteries useful. The SW4048 is a solid machine. We've been using one since 1998 and have

Re: [RE-wrenches] Shell SQ165-PC - SolarWorld SQ165-PC

2011-11-24 Thread toddcory
Contact Solarworld to see if they will sell you a couple of the 165's from their warranty replacement stash. I did this recently with some SQ80's I needed. They were pleasant to deal with and had what I needed (that no one else had). Todd On Thursday, November 24, 2011 11:41am,

Re: [RE-wrenches] Gross PV production meter options

2011-12-06 Thread toddcory
treat this as you would treat metering a standard non battery system. the KV2 meters are for combining the local consumption with the selling to the grid. a standard, single direction counting kWh meter in series with the 240 v grid tie will do what you want. todd On Tuesday, December

Re: [RE-wrenches] Gross PV production meter options

2011-12-06 Thread toddcory
no, he said he only wanted to meter what was being sold to the grid... not what was sold to the grid plus local consumption (which is the only way to measure total PV production). btw austin international (they have a new name now) has cheaper meters., todd On Tuesday, December 6,

Re: [RE-wrenches] System Performance | Battery Based Grid Tie

2011-12-20 Thread toddcory
that's a nice conservative estimate for input STC kWh to sold kWh jeremy as far as charge controller kWh to sold kWh, my OB 3648 runs in the ~87% range todd On Tuesday, December 20, 2011 3:00pm, All Solar, Inc. allso...@scswifi.net said: Wrenches, I am looking for advice and or

Re: [RE-wrenches] System Performance | Battery Based Grid Tie

2011-12-20 Thread toddcory
85% of STC kWh or PTC kWh? todd On Tuesday, December 20, 2011 5:44pm, Wayne Irwin wa...@pureenergysolar.com said: Wrenches, I am looking for advice and or comments on system performance from a Grid Tied battery back up system. Is 65% efficiency fair as far as what goes back to the

Re: [RE-wrenches] DC to AC derate

2012-01-04 Thread toddcory
I consistently see 87% DC kWh to sold kWh with my Outback system. (don't forget to also consider the usual STC to PTC derating) Todd On Wednesday, January 4, 2012 3:01pm, All Solar, Inc. allso...@scswifi.net said: Wrenches, Once again I am trying to size a grid tie w/battery system

Re: [RE-wrenches] DC to AC derate

2012-01-04 Thread toddcory
ps i forgot to add i am using a bank of lead calcium wet cells which have a much lower standby loss than lead antimony. todd On Wednesday, January 4, 2012 8:16pm, toddc...@finestplanet.com said: I consistently see 87% DC kWh to sold kWh with my Outback system. (don't forget to also

Re: [RE-wrenches] DC to AC derate

2012-01-05 Thread toddcory
to my knowledge the balancing transformer cannot be used with a grid tie. are you using two outback kvc2 meters for recording the ac sell kWh? (each 120 volt leg needs one.) todd On Thursday, January 5, 2012 1:33pm, Ray Walters r...@solarray.com said: I have a related question to

Re: [RE-wrenches] 110Vac LED resistance to weak grids in developing world

2012-02-09 Thread toddcory
i have some personal experience with led light bulbs. i put them outside because the cfl floodlights are very s-l-o-w to warm up to full brightness. 1) leds are still slightly less efficient (lumens per watt) than cfl's 2) led light bulbs (2 different brands) throw out an ungodly amount of

Re: [RE-wrenches] Interstate L-16 vs Trojan L-16REB

2012-02-15 Thread toddcory
I've been happy with Trojan batteries. They do say that they need up to 100 cycles to reach full capacity. so what does this mean for grid ties/battery back-up? todd Sent from Finest Planet WebMail. ___ List sponsored by Home Power magazine