Hi Ray,
The stand-alone diagram calls out the PV system disconnect right after the
PV system DC circuits and prior to the point of common coupling with the
batteries and the stand-alone inverter. Yes, you are correct a controller
or DC to DC converter is not shown in the this diagram or the
Hi Rebekah;
Thanks for pointing out the changes to the diagrams. I especially
appreciate Note (2). /The PV system disconnect in these diagrams
separates the PV system from all other systems./
That seems simple enough for defining the boundaries of RSS, until you
think about off grid, and
Hi everyone,
I strongly recommend looking at the figures that were added in NEC 2017 at
the beginning of Article 690 in 690.1(b).
What they show is equipment that is part of the PV system (to the left of
the PV system disconnect called out in the diagrams), and equipment that is
not part of the
For GT using Solar edge or Enphase, its not so hard to comply, but If
you are looking at off grid systems, it's not just someone's opinion,
its $1,000s of dollars extra to comply with 690.12. It also results in a
system that is less reliable, which is less safe off grid where lives
depend on
e
Sent: Monday, April 16, 2018 12:04 AM
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] Location of DC disconnect vis-a-vis rapid shutdown
exemption
Thanks Darryl.
I guess I can add that I am in CA and so looked only at the 2014. I also looked
at the 2017 article. Man, I have
Hey y'all, I'm going to disagree about the NEC getting "worse and worse
when it comes to PV," (see disconnect and grounding requirements, for
instance!), but as with previous posters, that's just an opinion.
Regarding location - the 2014 version had very little to say about the
location of any
Thanks Darryl.
I guess I can add that I am in CA and so looked only at the 2014. I also
looked at the 2017 article. Man, I have to say, my impression remains
that really starting with 2008 the code has just gotten worse and worse
when it comes to PV, but that is just me.
Not really sure
I think the code says Outside readily accessible,
On Sun, Apr 15, 2018 at 12:22 PM, Mark Frye wrote:
> Folks,
>
> As I recall, an inverter and it's integrated DC disconnect need only be
> placed in an accessible location. I am thinking of putting an inverter high
> up