Re: [RE-wrenches] Schneider Rapid shutdown with 2023 compliance
You said that very nicely Kevin ! If this were for offgrid, I would make the inspector happy and do even more than Kevin suggests after he is gone. Link to RS shutdown https://www.youtube.com/watch?v=wMoVXq4m1wk=10s Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso...@sti.net text 209 813 0060 On 2024-01-02 10:24 am, Kevin Pegg via RE-wrenches wrote: Hi Mac, I've just gone through a couple installations with a similar situation. The hardware you list does work as intended. I had to go through three different suppliers to get all the components. One thing that I didn't find clear in the MPPT RS documentation is when a shutdown is initiated, it shuts __everything__ on the Xanbus network down. All devices go into standby mode. Gen shuts down if running. Power is off. Not just the PV via Tigo modules. Had to develop client instruction sheet as to how to power up after a shutdown. On one hand, I can see why a single point shutdown is desired outcome. But it concerns me that it's vulnerable to abuse. If the whole system shutdown is not desired, the Xanbus connection can be omitted and then RS will be limited to the PV modules only. Kevin From: RE-wrenches On Behalf Of Mac Lewis via RE-wrenches Sent: January-01-24 12:00 PM To: RE-wrenches Cc: Mac Lewis Subject: [RE-wrenches] Schneider Rapid shutdown with 2023 compliance Hello Wrenches, I need to retrofit a Schneider XW+ system with a rapid shutdown system. The owner purchased this equipment about 4-5 years ago but is trying to get it past a very intense inspector. To me, it looks relatively straightforward to get NEC 2023 rapid shutdown compliant using Tigo TS4AF, and adding Schneider's MPPT Disconnect RS and external rapid shutdown initiator. It's a little strange though because it has 2017 NEC compliant all over the documentation but I believe we are good through NEC 2023 because shutdown occurs at a module level and the Disconnect RS can take care of arc-fault monitoring. Does anyone have any documentation for the MPPT Disconnect RS that doesn't specifically call out (only) NEC 2017 compliant? Or if this is not a good approach and is not reliable, I would appreciate your input as well. Cheers! -- Mac Lewis "Yo solo sé que no sé nada." -Sócrates ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org Links: -- [1] http://members.sti.net/offgridsolar/ [2] https://offgridsolar1.com/___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
Re: [RE-wrenches] Schneider Rapid shutdown with 2023 compliance
Hi Mac, I’ve just gone through a couple installations with a similar situation. The hardware you list does work as intended. I had to go through three different suppliers to get all the components. One thing that I didn’t find clear in the MPPT RS documentation is when a shutdown is initiated, it shuts _everything_ on the Xanbus network down. All devices go into standby mode. Gen shuts down if running. Power is off. Not just the PV via Tigo modules. Had to develop client instruction sheet as to how to power up after a shutdown. On one hand, I can see why a single point shutdown is desired outcome. But it concerns me that it’s vulnerable to abuse. If the whole system shutdown is not desired, the Xanbus connection can be omitted and then RS will be limited to the PV modules only. Kevin From: RE-wrenches On Behalf Of Mac Lewis via RE-wrenches Sent: January-01-24 12:00 PM To: RE-wrenches Cc: Mac Lewis Subject: [RE-wrenches] Schneider Rapid shutdown with 2023 compliance Hello Wrenches, I need to retrofit a Schneider XW+ system with a rapid shutdown system. The owner purchased this equipment about 4-5 years ago but is trying to get it past a very intense inspector. To me, it looks relatively straightforward to get NEC 2023 rapid shutdown compliant using Tigo TS4AF, and adding Schneider's MPPT Disconnect RS and external rapid shutdown initiator. It's a little strange though because it has 2017 NEC compliant all over the documentation but I believe we are good through NEC 2023 because shutdown occurs at a module level and the Disconnect RS can take care of arc-fault monitoring. Does anyone have any documentation for the MPPT Disconnect RS that doesn't specifically call out (only) NEC 2017 compliant? Or if this is not a good approach and is not reliable, I would appreciate your input as well. Cheers! -- Mac Lewis "Yo solo sé que no sé nada." -Sócrates ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
Re: [RE-wrenches] Schneider Rapid shutdown with 2023 compliance
Note that the MPPT disco RS works only with Schneider charge controllers. With any other charge controllers you'll need to use Fire Raptors. Specifically the power line type rsd do not work with classic cc. I see no reason why the Schneider units would not meet 2020 or 2023 codes. On Mon, Jan 1, 2024, 1:10 PM Darryl Thayer via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > I had a some way similar experience I used fire raptor and added a relay > to use Raptor signal to shutdown inverter. > > On Mon, Jan 1, 2024, 2:01 PM Mac Lewis via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > >> Hello Wrenches, >> >> I need to retrofit a Schneider XW+ system with a rapid shutdown system. >> The owner purchased this equipment about 4-5 years ago but is trying to get >> it past a *very *intense inspector. >> >> To me, it looks relatively straightforward to get NEC 2023 rapid shutdown >> compliant using Tigo TS4AF, and adding Schneider's MPPT Disconnect RS and >> external rapid shutdown initiator. It's a little strange though because it >> has 2017 NEC compliant all over the documentation but I believe we are good >> through NEC 2023 because shutdown occurs at a module level and the >> Disconnect RS can take care of arc-fault monitoring. >> >> Does anyone have any documentation for the MPPT Disconnect RS that >> doesn't specifically call out (only) NEC 2017 compliant? >> >> Or if this is not a good approach and is not reliable, I would appreciate >> your input as well. >> >> Cheers! >> >> >> >> >> -- >> >> >> >> Mac Lewis >> >> *"Yo solo sé que no sé nada." -Sócrates* >> ___ >> List sponsored by Redwood Alliance >> >> Pay optional member dues here: http://re-wrenches.org >> >> List Address: RE-wrenches@lists.re-wrenches.org >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> There are two list archives for searching. When one doesn't work, try the >> other: >> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org >> >> List rules & etiquette: >> http://www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> http://www.members.re-wrenches.org >> >> ___ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org > > ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
Re: [RE-wrenches] Schneider Rapid shutdown with 2023 compliance
I had a some way similar experience I used fire raptor and added a relay to use Raptor signal to shutdown inverter. On Mon, Jan 1, 2024, 2:01 PM Mac Lewis via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Hello Wrenches, > > I need to retrofit a Schneider XW+ system with a rapid shutdown system. > The owner purchased this equipment about 4-5 years ago but is trying to get > it past a *very *intense inspector. > > To me, it looks relatively straightforward to get NEC 2023 rapid shutdown > compliant using Tigo TS4AF, and adding Schneider's MPPT Disconnect RS and > external rapid shutdown initiator. It's a little strange though because it > has 2017 NEC compliant all over the documentation but I believe we are good > through NEC 2023 because shutdown occurs at a module level and the > Disconnect RS can take care of arc-fault monitoring. > > Does anyone have any documentation for the MPPT Disconnect RS that doesn't > specifically call out (only) NEC 2017 compliant? > > Or if this is not a good approach and is not reliable, I would appreciate > your input as well. > > Cheers! > > > > > -- > > > > Mac Lewis > > *"Yo solo sé que no sé nada." -Sócrates* > ___ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org > > ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org