I think the factors you have to consider include:

- the number of conductors in the trench,

-are they in a jacketed cable,

-are they separate conductors,

-are they considered "closely bundled",

-what is the distance of the conductor system once it exits the ground before entering a conditioned space, and will it be in conduit.

Chris


On 8/5/2017 5:36 PM, Corey Shalanski wrote:
How should we treat direct burial wires in a trench for ampacity derating purposes?
- Should they be considered "in a raceway or cable"? [NEC 310.15(B)(3)(a)]
- If it is determined that "spacing" must be maintained, what minimum spacing is acceptable/permissible?

I would be interested to hear what means and methods others have used to deal with this issue.

--
Corey Shalanski
Joule Energy
New Orleans, LA


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


--
Christopher Warfel, PE
Entech Engineering, Inc.
401-466-8978

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to