RE: [Repeater-Builder] OT- Dispatcher injured by lightning strike

2010-08-01 Thread Eric Lemmon
Whenever I read a report like this, I have mixed emotions.  I am surprised
that the injury occurred, which is impossible if the facility was properly
designed and islanded in accordance with numerous standards, including NFPA
70, NFPA 780, and the Motorola R56 Manual.  I am also angry that an official
issued the statement that ...the communications system, including its
400-foot radio tower, are grounded in accordance with industry safety
standards.  That official, and the idiots who designed the communications
center, should be fired and/or brought up on criminal charges.

The key to a safe installation at a location with an on-site tower is to
ensure that all utilities pass through a window where a common ground
reference exists.  Ideally, the tower should be right next to the facility,
so that the same ground reference is used for both.  The power transformer
that feeds the control room should be in that room, not hundreds of feet
away, and the secondary neutral of that transformer should be bonded to the
same ground that is used by the telephones, radio system, cable TV,
satellite system, and raised-floor supports.  If executed properly, the
design of the control room creates a Faraday Cage within which all occupants
are safe from injury due to GPR (Ground Potential Rise) from a nearby
lightning strike.  Likewise, all the electronics within the control room are
protected against surge damage.

It is obvious from the news report that the dispatcher was injured because
her headset was at a different potential from her body.  The GPR resulting
from lightning striking the tower led to thousands of volts difference
between the radio control system (the headset) and the floor and counter in
the control room- and the chair she was sitting in.  It is also obvious that
this difference in potential could not exist if the tower and the adjacent
control room were grounded in accordance with industry safety standards.
Some common sense and credible engineering skills are essential elements in
a proper control room design.

Many moons ago (late 60's), I was Chief Engineer at radio station WLRW, a 50
kW FM station at Champaign-Urbana, Illinois.  During my watch, the station
control room was relocated to a building next door.  It was my job to
supervise the cabling installation within the building and to the
transmitter at the base of the tower, which was just over 100 feet away.
All of the remote circuits and network feeds came through a grounding window
that was common with the power and the tower grounding system.  I remember
arguing with the Illinois Power foreman about how we needed a separate
transformer to power the station, and it had to be installed right at the
side of the control room and not in a vault several hundred feet away.  The
value of designing the entire installation to comply with established
industry standards and sound engineering practices was proven many times,
when the tower was struck by lightning during a storm, and no damage or
injury occurred.  Although the station was on automation most of the day, we
had live talent from late afternoon to early morning, and at least one
lightning strike occurred while on-air talent was at the board and wearing
headphones.  The lights blinked, but the board operator felt nothing and the
show went on.

73, Eric Lemmon WB6FLY
  

-Original Message-
From: Repeater-Builder@yahoogroups.com
[mailto:repeater-buil...@yahoogroups.com] On Behalf Of tracomm
Sent: Thursday, July 29, 2010 9:48 PM
To: Repeater-Builder@yahoogroups.com
Subject: [Repeater-Builder] OT- Dispatcher injured by lightning strike

  

A dispatcher was treated for electrical shock on May 2 after lightning sent
a 
power surge through the dispatcher's headset.



http://richmondregister.com/localnews/x1255109983/Lightning-surge-injures-91
1-dispatcher
http://richmondregister.com/localnews/x1255109983/Lightning-surge-injures-9
11-dispatcher 




Re: [Repeater-Builder] OT- Dispatcher injured by lightning strike

2010-08-01 Thread Chuck Kelsey
Care to hazard a guess on the percentage of facilities (radio/tv, two-way) 
that aren't done right?

A few years ago this happened near here - a radio personality wearing 
headphones taken to the hospital following a lightning strike to the tower 
outside the radio station.

Chuck
WB2EDV


- Original Message - 
From: Eric Lemmon wb6...@verizon.net
To: Repeater-Builder@yahoogroups.com
Sent: Sunday, August 01, 2010 11:42 AM
Subject: RE: [Repeater-Builder] OT- Dispatcher injured by lightning strike


 Whenever I read a report like this, I have mixed emotions.  I am surprised
 that the injury occurred, which is impossible if the facility was properly
 designed and islanded in accordance with numerous standards, including 
 NFPA
 70, NFPA 780, and the Motorola R56 Manual.  I am also angry that an 
 official
 issued the statement that ...the communications system, including its
 400-foot radio tower, are grounded in accordance with industry safety
 standards.  That official, and the idiots who designed the communications
 center, should be fired and/or brought up on criminal charges.

 The key to a safe installation at a location with an on-site tower is to
 ensure that all utilities pass through a window where a common ground
 reference exists.  Ideally, the tower should be right next to the 
 facility,
 so that the same ground reference is used for both.  The power transformer
 that feeds the control room should be in that room, not hundreds of feet
 away, and the secondary neutral of that transformer should be bonded to 
 the
 same ground that is used by the telephones, radio system, cable TV,
 satellite system, and raised-floor supports.  If executed properly, the
 design of the control room creates a Faraday Cage within which all 
 occupants
 are safe from injury due to GPR (Ground Potential Rise) from a nearby
 lightning strike.  Likewise, all the electronics within the control room 
 are
 protected against surge damage.

 It is obvious from the news report that the dispatcher was injured because
 her headset was at a different potential from her body.  The GPR resulting
 from lightning striking the tower led to thousands of volts difference
 between the radio control system (the headset) and the floor and counter 
 in
 the control room- and the chair she was sitting in.  It is also obvious 
 that
 this difference in potential could not exist if the tower and the adjacent
 control room were grounded in accordance with industry safety standards.
 Some common sense and credible engineering skills are essential elements 
 in
 a proper control room design.

 Many moons ago (late 60's), I was Chief Engineer at radio station WLRW, a 
 50
 kW FM station at Champaign-Urbana, Illinois.  During my watch, the station
 control room was relocated to a building next door.  It was my job to
 supervise the cabling installation within the building and to the
 transmitter at the base of the tower, which was just over 100 feet away.
 All of the remote circuits and network feeds came through a grounding 
 window
 that was common with the power and the tower grounding system.  I remember
 arguing with the Illinois Power foreman about how we needed a separate
 transformer to power the station, and it had to be installed right at the
 side of the control room and not in a vault several hundred feet away. 
 The
 value of designing the entire installation to comply with established
 industry standards and sound engineering practices was proven many times,
 when the tower was struck by lightning during a storm, and no damage or
 injury occurred.  Although the station was on automation most of the day, 
 we
 had live talent from late afternoon to early morning, and at least one
 lightning strike occurred while on-air talent was at the board and wearing
 headphones.  The lights blinked, but the board operator felt nothing and 
 the
 show went on.

 73, Eric Lemmon WB6FLY



Re: RE: [Repeater-Builder] OT- Dispatcher injured by lightning strike

2010-08-01 Thread dmurman

Had a similiar problem when I was chief engineer at an AM-FM radio station. The 
antenna tower was within 250 ft of the building. The prior engineer connected a 
copper strap from the automation equipment to one of the tower legs.

Whenever we had a lightning strike on the tower you can see the lightning dance 
across the equipment.  Due to the lightning many time I had to replace parts in 
the automation controller. I finally found the copper strap and removed it from 
the tower. No longer did I get any calls due to lightning causing automation 
equipment failure.  I then got the owner to get an engineering crew to measure 
the tower to ground and found that the original grounding was falling and 
needed to be fixed.

After that no longer had issues either with the FM transmitter or TV 
transmitter at that site.  Also added lightning protestion on the AC coming 
into the building.



David

Aug 1, 2010 03:43:37 PM, Repeater-Builder@yahoogroups.com wrote:

  



Whenever I read a report like this, I have mixed emotions. I am surprised
that the injury occurred, which is impossible if the facility was properly
designed and islanded in accordance with numerous standards, including NFPA
70, NFPA 780, and the Motorola R56 Manual. I am also angry that an official
issued the statement that ...the communications system, including its
400-foot radio tower, are grounded in accordance with industry safety
standards. That official, and the idiots who designed the communications
center, should be fired and/or brought up on criminal charges.

The key to a safe installation at a location with an on-site tower is to
ensure that all utilities pass through a window where a common ground
reference exists. Ideally, the tower should be right next to the facility,
so that the same ground reference is used for both. The power transformer
that feeds the control room should be in that room, not hundreds of feet
away, and the secondary neutral of that transformer should be bonded to the
same ground that is used by the telephones, radio system, cable TV,
satellite system, and raised-floor supports. If executed properly, the
design of the control room creates a Faraday Cage within which all occupants
are safe from injury due to GPR (Ground Potential Rise) from a nearby
lightning strike. Likewise, all the electronics within the control room are
protected against surge damage.

It is obvious from the news report that the dispatcher was injured because
her headset was at a different potential from her body. The GPR resulting
from lightning striking the tower led to thousands of volts difference
between the radio control system (the headset) and the floor and counter in
the control room- and the chair she was sitting in. It is also obvious that
this difference in potential could not exist if the tower and the adjacent
control room were grounded in accordance with industry safety standards.
Some common sense and credible engineering skills are essential elements in
a proper control room design.

Many moons ago (late 60's), I was Chief Engineer at radio station WLRW, a 50
kW FM station at Champaign-Urbana, Illinois. During my watch, the station
control room was relocated to a building next door. It was my job to
supervise the cabling installation within the building and to the
transmitter at the base of the tower, which was just over 100 feet away.
All of the remote circuits and network feeds came through a grounding window
that was common with the power and the tower grounding system. I remember
arguing with the Illinois Power foreman about how we needed a separate
transformer to power the station, and it had to be installed right at the
side of the control room and not in a vault several hundred feet away. The
value of designing the entire installation to comply with established
industry standards and sound engineering practices was proven many times,
when the tower was struck by lightning during a storm, and no damage or
injury occurred. Although the station was on automation most of the day, we
had live talent from late afternoon to early morning, and at least one
lightning strike occurred while on-air talent was at the board and wearing
headphones. The lights blinked, but the board operator felt nothing and the
show went on.

73, Eric Lemmon WB6FLY


-Original Message-
From: Repeater-Builder@yahoogroups.com
[mailto:repeater-buil...@yahoogroups.com] On Behalf Of tracomm
Sent: Thursday, July 29, 2010 9:48 PM
To: Repeater-Builder@yahoogroups.com
Subject: [Repeater-Builder] OT- Dispatcher injured by lightning strike

A dispatcher was treated for electrical shock on May 2 after lightning sent
a 
power surge through the dispatcher's headset.

http://richmondregister.com/localnews/x1255109983/Lightning-surge-injures-91
1-dispatcher
http://richmondregister.com/localnews/x1255109983/Lightning-surge-injures-9
11-dispatcher 





Re: [Repeater-Builder] OT- Dispatcher injured by lightning strike

2010-08-01 Thread Doug Hutchison
What concerns me more than anythingso many experts yet this sort of 
thing still happens...(in many fields)!!!

Hindsight is great!!

D


On 01/08/2010 17:24:18, Chuck Kelsey (wb2...@roadrunner.com) wrote:
  Care to hazard a guess on the percentage of facilities (radio/tv, 
two-way)
 
  that
  aren't done right?
 
  A few years ago this happened near here - a radio personality wearing
  headphones taken to the hospital following a lightning strike to the 
tower
  outside the radio station.
 
  Chuck
  WB2EDV
 
 
  - Original Message -
  From: Eric Lemmon wb6...@verizon.net
  To: Repeater-Builder@yahoogroups.com
  Sent: Sunday, August 01, 2010 11:42 AM
  Subject: RE: [Repeater-Builder] OT- Dispatcher injured by lightning 
strike
 
 
   Whenever I read a report like this, I have mixed emotions. I am 
surprised
   that the injury occurred, which is impossible if the facility was 
properly
   designed and islanded in accordance with numerous standards, including
   NFPA
   70, NFPA 780, and the Motorola R56 Manual. I am also angry that an
   official
   issued the statement that ...the communications system, including its
   400-foot radio tower, are grounded in accordance with industry safety
   standards. That official, and the idiots who designed the 
communications
   center, should be fired and/or brought up on criminal charges.
  
   The key to a safe installation


Re: [Repeater-Builder] OT- Dispatcher injured by lightning strike

2010-08-01 Thread Chuck Kelsey
And I only see it getting worse as everyone 'has' to cut corners/costs.

Chuck
WB2EDV



- Original Message - 
From: Doug Hutchison specialq@ntlworld.com
To: repeater-builder@yahoogroups.com
Sent: Sunday, August 01, 2010 12:53 PM
Subject: Re: [Repeater-Builder] OT- Dispatcher injured by lightning strike


 What concerns me more than anythingso many experts yet this sort of
 thing still happens...(in many fields)!!!

 Hindsight is great!!

 D


 On 01/08/2010 17:24:18, Chuck Kelsey (wb2...@roadrunner.com) wrote:
  Care to hazard a guess on the percentage of facilities (radio/tv,
 two-way)
 
  that
  aren't done right?
 
  A few years ago this happened near here - a radio personality wearing
  headphones taken to the hospital following a lightning strike to the
 tower
  outside the radio station.
 
  Chuck
  WB2EDV
 
 
  - Original Message -
  From: Eric Lemmon wb6...@verizon.net
  To: Repeater-Builder@yahoogroups.com
  Sent: Sunday, August 01, 2010 11:42 AM
  Subject: RE: [Repeater-Builder] OT- Dispatcher injured by lightning
 strike
 
 
   Whenever I read a report like this, I have mixed emotions. I am
 surprised
   that the injury occurred, which is impossible if the facility was
 properly
   designed and islanded in accordance with numerous standards, including
   NFPA
   70, NFPA 780, and the Motorola R56 Manual. I am also angry that an
   official
   issued the statement that ...the communications system, including its
   400-foot radio tower, are grounded in accordance with industry safety
   standards. That official, and the idiots who designed the
 communications
   center, should be fired and/or brought up on criminal charges.
  
   The key to a safe installation


 



 Yahoo! Groups Links









No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 9.0.851 / Virus Database: 271.1.1/3043 - Release Date: 08/01/10 
02:34:00



Re: [Repeater-Builder] OT- Dispatcher injured by lightning strike

2010-08-01 Thread Doug Hutchison
Yup.we are only a number after all!!

D

On 01/08/2010 18:04:12, Chuck Kelsey (wb2...@roadrunner.com) wrote:
  And I only see it getting worse as everyone 'has' to cut corners/costs.
 
  Chuck
  WB2EDV
 
 
 
  - Original Message -
  From: Doug Hutchison specialq@ntlworld.com
  To: repeater-builder@yahoogroups.com
  Sent: Sunday, August 01, 2010 12:53 PM
  Subject: Re: [Repeater-Builder] OT- Dispatcher injured by lightning
  strike
 
 
   What concerns me more than anythingso many experts yet this 
sort of
   thing still happens...(in many fields)!!!
  
   Hindsight is great!!
  
   D
  
  
   On 01/08/2010 17:24:18, Chuck Kelsey (wb2...@roadrunner.com) wrote:
Care to hazard a guess on the percentage of facilities (radio/tv,
   two-way)
   
that
aren't done right?
   
A few years ago this happened near here - a radio personality 
wearing
headphones taken to the hospital following a lightning strike to the
   tower
outside the radio station.
   
Chuck
WB2EDV
   
   
- Original Message -
From: Eric Lemmon wb6...@verizon.net
To: Repeater-Builder@yahoogroups.com
  


Re: [Repeater-Builder] OT- Dispatcher injured by lightning strike

2010-08-01 Thread men...@pa.net
When the expert label starts to get thrown around too much I like to  
quote one of my math teachers in junior high school whose definition  
of expert is worth remembering to deflate any over sized egos.

Ex is a has been and a Spurt is a drop under pressure

Milt
N3LTQ



Quoting Doug Hutchison specialq@ntlworld.com:

 What concerns me more than anythingso many experts yet this sort of
 thing still happens...(in many fields)!!!

 Hindsight is great!!

 D


 On 01/08/2010 17:24:18, Chuck Kelsey (wb2...@roadrunner.com) wrote:
   Care to hazard a guess on the percentage of facilities (radio/tv,
 two-way)
  
   that
   aren't done right?
  
   A few years ago this happened near here - a radio personality wearing
   headphones taken to the hospital following a lightning strike to the
 tower
   outside the radio station.
  
   Chuck
   WB2EDV
  
  
   - Original Message -
   From: Eric Lemmon wb6...@verizon.net
   To: Repeater-Builder@yahoogroups.com
   Sent: Sunday, August 01, 2010 11:42 AM
   Subject: RE: [Repeater-Builder] OT- Dispatcher injured by lightning
 strike
  
  
Whenever I read a report like this, I have mixed emotions. I am
 surprised
that the injury occurred, which is impossible if the facility was
 properly
designed and islanded in accordance with numerous standards, including
NFPA
70, NFPA 780, and the Motorola R56 Manual. I am also angry that an
official
issued the statement that ...the communications system, including its
400-foot radio tower, are grounded in accordance with industry safety
standards. That official, and the idiots who designed the
 communications
center, should be fired and/or brought up on criminal charges.
   
The key to a safe installation


 



 Yahoo! Groups Links








RE: [Repeater-Builder] OT- Dispatcher injured by lightning strike

2010-08-01 Thread Doug Hutchison
Yup...thats just what I mean...experts.bah humbug!!

D

On 01/08/2010 19:44:48, Eric Lemmon (wb6...@verizon.net) wrote:
  That is so true! When you add corporate ego to the mix, things get
  really
  murky. A case in point: Back in the mid-eighties, one very large and
  well-known computer equipment manufacturer was contracted to install 
some
  facility monitoring equipment at Space Launch Complex Six at Vandenberg
  AFB,
  a site that was to be (until the Challenger disaster) the west-coast
  Space
  Shuttle launch pad. The monitoring equipment was divided into two major
  pieces, on separate floors of the Launch Control Center and about 200
  feet
  apart. From the moment the system was energized, a number of data
  channels
  had 60 Hz common-mode noise corrupting the data on the RS-422
  circuits.
 
  My crew was attempting to investigate the noise issue, when we 
discovered
  that the
  supplier's technicians had deliberately floated the upstairs
  cabinets by using insulating washers and plastic sheets to avoid 
contacting
  any grounded facility items such as embedded rebar. When advised by 
our AHJ
  (Authority Having Jurisdiction) inspector that the installation violated
  Article 250 of the NEC, the manufacturer's
  engineer explained that this was
  the way his company did these installations, and-
  here's the corporate ego
  part- they had been doing%2


Re: [Repeater-Builder] OT- Dispatcher injured by lightning strike

2010-08-01 Thread Chuck Kelsey
Often times it's a well-meaning individual that simply doesn't understand 
(like me - LOL) and there are plenty of inspectors out there that don't know 
either. The corporate reasons for doing things wrong speak for themselves. 
Life is full of mis-information.

Chuck
WB2EDV


- Original Message - 
From: Doug Hutchison specialq@ntlworld.com
To: repeater-builder@yahoogroups.com
Sent: Sunday, August 01, 2010 3:26 PM
Subject: RE: [Repeater-Builder] OT- Dispatcher injured by lightning strike


 Yup...thats just what I mean...experts.bah humbug!!

 D

 


Re: [Repeater-Builder] OT- Dispatcher injured by lightning strike

2010-08-01 Thread AA8K73 GMail

n5sx...@charter.net wrote:
  
 
 I must admit that I don't see the problem with the sensitive equipment 
 not finding ground thru the floor! In the 1980 I have some telephone 
 central offices built by TRW. Each of the equipment racks were mounted 
 on thick plastic sheets, and the mounting bolts were inserted thru 
 insulating shoulder washers. Each equipment rack had a dedicate home 
 run ground back to the main central office ground buss plate. All 
 worked well, with no lightning problems. Some many years later I was 
 still working for the same telephone company when I was asked to go back 
 to that office to see why the new equipment addition would not work. It 
 was needed badly as the C.O. was out of lines and needed this expansion 
 to work. A quick inspection showed that the new equipment had been 
 mounted directly to the concrete floor with out the insulation kit. I 
 had the CO crew there help jack the rack up and slide a rubber floor mat 
 under it for temporary insulation. We verified that the ground strap was 
 correctly installed, and when we returned that equipment cabinet to 
 service , it came up and worked fine. The equipment installer was forced 
 to return at night to correct his problems. So not everything should be 
 chassis grounded to the floor.
 Jeff