RE: residential heads in a 13 system

2008-01-29 Thread Greg McGahan
It appears the general consensus is that you can not mix the res heads with a room calc method. There was not a response from committee members regarding the difference in compartment and one hour rated rooms. We used QR heads and the room method but I disagree in principal because of the rating

RE: Max Ceiling Heights

2008-01-29 Thread Brian Harris
Craig, Thanks for the input, the manufacturer just called me back and said they have no limitations on the heads I'm using, I had him send me that in an email which I will forward to the AHJ. Brian Harris FDFP INC. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On

Re: Max Ceiling Heights

2008-01-29 Thread Ed Vining
So how about showing the AHJ the listings for the K14's and the listing for those being used. Yes sir, where there are height restrictions for sprinklers like those K 14's it is shown in the listing. There are no such restrictions on the ones we are using. Ed Joe Hankins [EMAIL

grace periods

2008-01-29 Thread geraldine . cirelli
We in fire protection are seeking a solution for grace period/ flexibility for the maintenance, testing and inspection of the fire systems. With the sheer number of systems it is almost impossible to schedule testing/inspections with a rigid frequency that does not allow flexibility. NFPA

RE: Interior chair lift

2008-01-29 Thread art
If the shaft is noncombustible and the car is noncombustible then you don't need a head in the shaft IMHO. For hydraulic equipment a head to protect the sump is in order. Art @ ATCO Fire -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of George Church Sent:

RE: Max Ceiling Heights

2008-01-29 Thread Brian Harris
Ah, 55' is what I was thinking, I knew I remembered that from somewhere! Thanks for all the input forumites Brian Harris FDFP INC. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Mike Brown (TECH- GVL) Sent: Tuesday, January 29, 2008 11:29 AM To:

RE: Max Ceiling Heights

2008-01-29 Thread Ray Vance
There is technically no limit on the height at which most sprinklers can be utilized. The more usual situation is when a specific sprinkler has a specific listing limiting its usage to a certain height. The number your memory is serving to you comes from the Life Safety Code and references a

RE: Max Ceiling Heights

2008-01-29 Thread Chappell, Carl
What we deal with here in Las Vegas are the local amendments to the codes and NFPA 13. When a ceiling height is between 25 and 50 feet above the floor below quick-response sprinklers with a minimum K-factor of 11.2 is required. Once a ceiling height exceeds 50 feet a fire protection engineer has

RE: Headline: More Fires in Las Vegas

2008-01-29 Thread Craig.Prahl
Unless the Mob was behind it, or there's some unidentifiable body in the midst, sad to say, there's just not enough drama to make the headlines. But we're glad to hear the news regardless. Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500

Re: Max Ceiling Heights

2008-01-29 Thread Joe Hankins
Sprinklers aren't rated for building height in and of themselves, as the maximum height it depends on a lot of factors. So long as the sprinklers are listed for the NFPA 13 design you are using, that's all you need. For example, K14 ESFRs are limited to 32 ft. buildings at 50 psi, but can go

Headline: More Fires in Las Vegas

2008-01-29 Thread Ken Miller
Ok, maybe I overstated the headline. But the fact is that yesterday (Monday) we had two more fires in Las Vegas. Both Saved by Sprinklers! Where is the national/world news reporting on these? Yes we issued an official news release for both. As we all know, these stories will be burried on the

residential heads in a 13 system

2008-01-29 Thread Travis Mack, SET
Was there any general concensus to Greg's question about if you need to calc 4 residential sprinklers in a 13 application since we are applying the 0.10 density. It seems that QR heads would be the better choice since you can do room design and only calculate 1-2 heads in most compartments.

High Density Shelving

2008-01-29 Thread Mike Hairfield
Does anyone know how to protect a room with high density mobile shelving? There is a 2 foot clearance between the deflectors and top of the shelving. Mike Hairfield Nicholson Sprinkler Corporation ph 804-353-1822 fax 804-358-9047 Thanks!___

Sprinkler Zones for Horizontal Exit Building

2008-01-29 Thread bill . brooks
A single use structure has been divided into 3 buildings because of occupancy and construction type issues related to the IBC. Horizontal exits are provided and this means the building cannot be evacuated simultaneously using the stair widths available. Question - Are separate sprinkler zones

13 residential obstructions

2008-01-29 Thread Todd Williams - FPDC
I am working on a modification to an existing system in a residential occupancy. The design basis for the system is NFPA 13 (2002) Section 11.2.3.5 (4 residential sprinkelrs, 0.10 density). In the revision, the architect has added soffits and drop ceiling areas in certain rooms. As an example,

RE: Pipe life

2008-01-29 Thread George Church
Was the bulk of the claim in damage to product, BI, pipe replacement? Glc Inquiring minds need to know :) -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Top Myers Sent: Tuesday, January 29, 2008 12:50 AM To: sprinklerforum@firesprinkler.org Subject: RE:

RE: 13 residential obstructions

2008-01-29 Thread A.P.Silva
Can you cover the room with a single sidewall sprinkler installed flush with the bottom of the soffits/bulkheads? Use a residential sprinkler listed for upto 12 inches below the ceiling. The flow for the 0.1 density might still be greater than the listed flow for 12 inches below the ceiling. Tony

RE: Max Ceiling Heights

2008-01-29 Thread Mike Brown (TECH- GVL)
Hi There are no restrictions in NFPA 13 for Standard Spray Sprinklers. The ceiling limitations are for storage sprinklers like ESFR. The old NFPA 101 Life Safety used to allow you to eliminate sprinklers in atriums above 55 feet in height. There have been times when this has been questions in

Re: High Density Shelving

2008-01-29 Thread Tom Wellen
What about the reference that can be found in the NFPA 13 Handbook commentary in Section 8.14.9 in the 2002 ed. and 8.15.9 in the 2007 ed.? Tom Wellen AFSA Technical Services On Jan 29, 2008, at 7:41 AM, Mike Hairfield wrote: Does anyone know how to protect a room with high density mobile

RE: High Density Shelving

2008-01-29 Thread Jim Davidson
Mike You can find protection information on mobile shelving units in the following documents: 1. Fire Protection Study, Mobile Compact Shelving Fire Tests, Archives II, Gage-Babcock Associates, Dated June 1990. 2. Full Scale Fire Tests of Sprinklered Mobile Shelving Units for

Max Ceiling Heights

2008-01-29 Thread Brian Harris
Forum, I just got back some comments from the local AHJ on a project we are doing and he's asking me to verify that the heads we are using are rated for ceilings over 30'. I've spoke with the manufacturer and he said he doesn't have anything on min./max. ceiling heights. If memory serves me isn't

RE: Max Ceiling Heights

2008-01-29 Thread Craig.Prahl
Certain types of sprinklers have specific limitations and they are usually listed as such, typically those designated for storage occupancies. Most Control Mode sprinklers don't list any restrictions and so far I haven't been able to find anything in NFPA stating an NFPA imposed restriction.

3 alarm Fire @ Monte Carlo now in las vegas - applied to wildland fires

2008-01-29 Thread å... ....
this strategy (interior sprinklers to fight exterior fires) was proposed by myself and a few others as a mitigation against wildland fires to the San Diego city council in the aftermath of the wildland fires there about 5 years ago. Automatic sprinklers work better than most people realize, not

Re: 13 residential obstructions

2008-01-29 Thread Thom McMahon
While I also remember Chris saying this he also pointed out that there where AHJ's that will not use common sense when Appling the standards. When I look at your bathroom and soffit situation I look for a Residential head listed for 12 down from the ceiling. Spaced properly between your

RE: 13 residential obstructions

2008-01-29 Thread Ed Kramer
This thread reminds me of a dilemma I tussled with last week. In regards to residential sidewalls, section 8.10.7.1.2 (02) says not to install residential sidewalls within 8' of a light or similar obstructions. It doesn't provide any exceptions, such as the light being only 4 deep and the

RE: 13 residential obstructions

2008-01-29 Thread Todd Williams - FPDC
I was at the jobsite today and the architect happened to be there. I explained the situation and he said the ceiling heights were arbitrarily chosen and the difference was 1 foot because 'that was even'. He claimed the soffits were for recessed lighting, but the high point of the ceiling is

RE: grace period

2008-01-29 Thread Craig.Prahl
It would be at the discretion of whomever you are accountable to as far as submission of reports. If you submit reports to a local AHJ or Underwriter I would contact them and ask how stringently you need to follow the frequencies established in NFPA 25. I doubt that in a 365 day cycle a day or

grace period

2008-01-29 Thread geraldine . cirelli
NFPA 25 establishes inspection, testing and maintenance frequencies. A grace period is not considered. Due to the large number and variety of fire systems throughout our site, these frequencies cannot be met on a rigid schedule. For example an Annual test is performed, does that mean the

RE: 13 residential obstructions

2008-01-29 Thread A.P.Silva
Addendum to my previous posting. I didn't mean directly below the soffit/bulkhead. If the soffits are only on two or even three sides, this will work. If they are on all four walls (assuming a rectangular room), then it won't. Tony -Original Message- From: [EMAIL PROTECTED]

RE: 13 residential obstructions

2008-01-29 Thread Greg McGahan
I believe Roland and others interpret pockets to be greater than 12 deep. I also believe common sense MUST be used in some cases and 3 sprinklers in a 90 sqft bathroom would probably not make a significant improvement of life safety or property protection in my humble opinion based on many

RE: 13 residential obstructions

2008-01-29 Thread George Church
A friend of mine pointed out that I erred and confused two guys at NFPA in my last post. James Lake took Chris Dubay's chair as staff liason with #13 (along with other duties, of course). Dr. John Hall is NFPA's assistant vice president of Fire Analysis and Research. I apologize for the

High Density Shelving Message-ID: [EMAIL PROTECTED] Content-Type: text/plain; charset=iso-8859-1

2008-01-29 Thread Sima_Zlotnikova
Mike, you might find some usable information in Annex of NFPA 909. Sima Zlotnikova This e-mail and any attachments are confidential. If you receive this message in error or are not the intended recipient, you should not

Re: 13 residential obstructions

2008-01-29 Thread Todd Williams - FPDC
Installing a sidewall would be a pain in the extreme lower back. At 03:44 PM 1/29/2008, you wrote: While I also remember Chris saying this he also pointed out that there where AHJ's that will not use common sense when Appling the standards. When I look at your bathroom and soffit situation I

RE: High Density Shelving

2008-01-29 Thread bill . brooks
This guidance is from the GSA PBS P100 criteria: Track Files General. A track file uses a single aisle to give access to an otherwise solid group of open-shelf files. Access is gained by moving shelf units on rollers along a track until the proper unit is exposed. Special Requirements. Track

Re: grace period

2008-01-29 Thread Ron Greenman
Geraldine, If I'm not mistaken isn't your email address the Savannah River Site and didn't you all just come out with some new guidelines for yourself? What does your AHJ say? And finally at least something to hang your hat on: Look in NFPA 25-1.3 1.3A-2007 ed. which allows alternatives. If you