Test connection for forward flow testing of backflow

2010-07-26 Thread Craig.Prahl
Just trying to get a consensus, Got a backflow in a building at the riser location, what is the preferred type of connection at the wall which would allow for forward flow testing? Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene 1500

RE: Test connection for forward flow testing of backflow

2010-07-26 Thread Fletcher, Ron
Main drain. Ron Fletcher Aero Automatic Phoenix, AZ -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of craig.pr...@ch2m.com Sent: Monday, July 26, 2010 5:32 AM To: sprinklerforum@firesprinkler.org;

RE: Test connection for forward flow testing of backflow

2010-07-26 Thread Richard Carr
HOSE VALVES. Richard Carr, SET Design Manager Associated Sprinkler Co., LLC 336.373.3901 ext 217 richa...@associatedsprinkler.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of craig.pr...@ch2m.com

Re: Test connection for forward flow testing of backflow

2010-07-26 Thread Charles Thurston
Hello Craig, Fire pump test header for sizes over 2, Otherwise the main drain Monday, July 26, 2010, 8:31:34 AM, you wrote: Just trying to get a consensus, Got a backflow in a building at the riser location, what is the preferred type of connection at the wall which would allow for forward

RE: Test connection for forward flow testing of backflow

2010-07-26 Thread lamarvaughn
The way I have handled this if the system demand is more than the main drain can handle is to provide a valved discharge,onto a paved area or splash block,calculated to a size to give an equivilent flow to the system demand.Sounds like a pain but I haven't found any other way. Lamar Vaughn,SET

RE: Test connection for forward flow testing of backflow

2010-07-26 Thread Reed Roisum
What if you don't have a fire pump and the system demand is more than what can be flowed out of the main drain (BTW, how do you measure the flow out of the main drain?) We typically spec a 2 1/2 single outlet (size and # of outlets dependent on the system demand), flush-type test connection

RE: Test connection for forward flow testing of backflow

2010-07-26 Thread George Church
you could simply leave a single FHV if that's suffieient for your flow; if you start getting in to needing multiples, we'd stick a valved outlet on it and when the test is performed, install a piece of 8 we have with 6- 2.5 FHVs, run the test, take it home for the next time we need to flow a fire

Residential Sprinklers on a dry System

2010-07-26 Thread Mike Hairfield
Here is the problem Have a dry pipe system where a portion of the building is rated R and the remainder is A B. Recently TYCO has come out with residential dry pendent sprinkler for residential systems. OK now here is my question What have you contractors' done in the past in

Big Ass Fans

2010-07-26 Thread Brian Harris
Does anybody have any experience using Big Ass Fans and ESFR heads? I have a Fire Marshall questioning the use of the (2) in the same warehouse. Brian Harris Design Engineer First Defense Fire Protection 11957 Ramah Church Road Huntersville NC 28078 br...@firstdefensefire.com

RE: Residential Sprinklers on a dry System

2010-07-26 Thread Matt Grise
The residential dry pendant is approved for dry pipe systems! Matt Grisé PE*, LEED AP Sales Engineer Alliance Fire Protection *Licensed in KS MO 913.888.0647 ph 913.888.0618 f 913.927.0222 cell www. AFPsprink.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Residential Sprinklers on a dry System

2010-07-26 Thread Mike Hairfield
The residential area is a conditioned space above and below the ceiling, why can't we use residential pendents on return bends? Mike From: m...@afpsprink.com To: sprinklerforum@firesprinkler.org Date: Mon, 26 Jul 2010 13:36:35 -0500 Subject: RE: Residential Sprinklers on a dry System

RE: Residential Sprinklers on a dry System

2010-07-26 Thread Steve Leyton
...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field) __ Information from ESET NOD32 Antivirus, version of virus signature database 5315 (20100726) __ The message was checked by ESET NOD32 Antivirus

RE: Big Ass Fans

2010-07-26 Thread Steve Leyton
) __ Information from ESET NOD32 Antivirus, version of virus signature database 5315 (20100726) __ The message was checked by ESET NOD32 Antivirus. http://www.eset.com __ Information from ESET NOD32 Antivirus, version of virus signature database 5315 (20100726

Ammonia quenching system

2010-07-26 Thread Fletcher, Ron
Anyone have experience with an ammonia quenching systems? Ron Fletcher Aero Automatic Phoenix, AZ ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical

RE: Ammonia quenching system

2010-07-26 Thread Craig.Prahl
EXTREME amounts of water to knock it down if you go that route. There are several methods of handling mitigation but no specific design criteria, mostly industry recommendations. You need to check with local Haz Mat responders, owner's insurance underwriter, as well as other interested AHJ's

RE: Big Ass Fans

2010-07-26 Thread Matt Grise
Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field) __ Information from ESET NOD32 Antivirus, version of virus signature database 5315 (20100726

Re: Big Ass Fans

2010-07-26 Thread tom poisal
...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.orgto%3asprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field) __ Information from ESET NOD32 Antivirus, version of virus signature database 5315 (20100726

Re: Test connection for forward flow testing of backflow

2010-07-26 Thread cherokeefire...@aol.com
The Sprinkler Age magazine has an article about this with pictures of various options in last months edition. Forest Wilson Cherokee Fire Sent from my Verizon Wireless Phone - Reply message - From: George Church for...@ptd.net Date: Mon, Jul 26, 2010 11:27 am Subject: Test connection