On Apr 25, 2011, at 1:35 PM, IPA nsfdc...@gmail.com wrote:
Question about 13D pressure tanks:
1.) I have a 13D system where the owner would like to go with a well and
pressure tank installation for their sprinkler domestic water. The 13D
Handbook (2007) states
With regard to this reference, think of 13 as annex material. 13D clearly
establishes that you can take the water supply from any approved source, and
that tanks, pumps, etc. do NOT have to be listed.
(The foregoing is my personal opinion only.)
Congratulations Cecil! And best wishes to
Here ya loud and clear. However the IBC commentary states the following;
IBC Commentary (Pg 10-135); (CAPS for EMPHASIS)
In general, only PORTIONS of the BUILDING SERVICE SYSTEMS THAT SERVE THE
EXIT ENCLOSURE are allowed to penetrate the exit enclosure
We all know that the commentary is not the