resurrecting an old system

2013-11-20 Thread Todd - Work
I am working with a company that bought a building where the sprinkler system had been turned off about 10 years ago. The fire department is requiring that a system be turned on. The existing system was fed from a pump taking suction from a pond (disconnected and removed). There has been some

RE: resurrecting an old system

2013-11-20 Thread RFletcher
Do an air test, fix the obvious stuff that's broken, buy a new pump and flush/test the existing pipe with water. An air test will get most big leaks it's pretty hard to find little pin hole leaks using air if it is a large volume system. My 2 cents. Ron F -Original Message- From:

RE: Location of foam system valve room on 2nd floor - permitted?

2013-11-20 Thread Craig.Prahl
Scott, you understand my concerns. Unfortunately this is a challenging client and you better have any requirement opinion backed up with documentation otherwise it's just an opinion for what that's worth. Craig L. Prahl, CET Fire Protection Group Lead CH2MHILL Lockwood Greene 1500

RE: Location of foam system valve room on 2nd floor - permitted?

2013-11-20 Thread Scott A Futrell
Do they have maintenance personnel that can assist you? I really have had the same problem, but when you get the guys that have to work on it involved they can provide some welcome support. Good luck. Scott   (763) 425-1001 Office (612) 759-5556 Cell -Original Message- From:

RE: resurrecting an old system

2013-11-20 Thread Scott A Futrell
I like the replace it all option... How old is the system to start with? You need to replace all the sprinklers, if some have popped you don't know how many others may be damaged. What about gaskets in grooved couplings? Is the water supply now equal to the original pump and pond? If not, pipe

Misc storage and QR sprinkler deduction

2013-11-20 Thread Todd - Work
I am working on a school project where there is a basement that will be used for storage (3300 sqft, 13 ft ceiling). I am basing my design on 10 ft high storage of miscellaneous stuff, which I am calling Class IV. This would be a 0.20/1500 sprinkler density, which is the same as the requirement

RE: Location of foam system valve room on 2nd floor - permitted?

2013-11-20 Thread Mark A. Sornsin, P.E.
Just to reiterate Scott's point: Maintenance is huge and his examples are extremely valid. We were once painted into a corner on our first foam job many years ago. The foam tanks were put on a mezzanine above the risers. But we ensured there was plenty of room on the mezzanine for bladder

Re: resurrecting an old system

2013-11-20 Thread Todd - Work
The owner wants to re-use the system and we have to prove to him that it needs to be replaced, if it does. I'm thinking after a physical inspection and air test, it would tell us if we have something that could be used or not. The building is approximately 30 ft to the peak and 25 to the hip

RE: Misc storage and QR sprinkler deduction

2013-11-20 Thread Brad Casterline
Todd, Since occupancy classifications are based on quantity and/or combustibility and expected rates of heat release, uhhh...??? -Original Message- From: Todd - Work [mailto:t...@fpdc.com] Sent: Wednesday, November 20, 2013 8:45 AM To: sprinklerforum@lists.firesprinkler.org Subject: Misc

RE: Misc storage and QR sprinkler deduction

2013-11-20 Thread Ed Kramer
Todd, take a peek at 13.2.2 (2) (2013 edition). Ed Kramer Lawrence, KS -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd - Work Sent: Wednesday, November 20, 2013 8:45 AM To:

RE: Location of foam system valve room on 2nd floor - permitted?

2013-11-20 Thread Craig.Prahl
Ok just to follow up with the outcome. Had our meeting with the client, explained access issues and Code requirement of Approved access. Our 2nd foam room will be at grade level in one of two decent locations. They may even push Process guys out of the way for this FP system. That's a huge

RE: resurrecting an old system

2013-11-20 Thread Forest Wilson Fire Sprinkler Comtractor
I would air test first but I think you will need the water test to find leaks   Sent from my Galaxy S®III Original message From: Scott A Futrell sco...@ffcdi.com Date: 11/20/2013 9:06 AM (GMT-05:00) To: sprinklerforum@lists.firesprinkler.org Subject: RE: resurrecting an

Re: Location of foam system valve room on 2nd floor - permitted?

2013-11-20 Thread rongreenman .
Push Like button now. On Wed, Nov 20, 2013 at 7:24 AM, craig.pr...@ch2m.com wrote: Ok just to follow up with the outcome. Had our meeting with the client, explained access issues and Code requirement of Approved access. Our 2nd foam room will be at grade level in one of two decent

RE: resurrecting an old system

2013-11-20 Thread Mike Hill
You are on the right track. Test and repair as needed, then flush. I had a similar situation in an aircraft hangar about 15 years ago. System froze and there were lots of issues. The occupant's first indication of a problem was falling debris, broken fittings. We went in and fixed the obvious

RE: resurrecting an old system

2013-11-20 Thread John O'Connor
Mike, I would respectfully urge flushing prior to full 200# test, simply because this system contains mud and other debris, that could, still in place, allow pinhole leaks to remain undetected. Flush to eliminate debris that could be allowing a successful pressure test. Once flushed, the system

Re: Misc storage and QR sprinkler deduction

2013-11-20 Thread ParsleyConsulting
Todd, I completely agree with Ed. 13.2.1 (5) would let it qualify as miscellaneous storage, and use Table 13.2.1, and Figure 13.2.1. 13.2.2 (2) tells you that the same, except you can apply Chapter 11 for OH 1 2, and EH 1 2 So, if you apply 13.2.2(2), and Table 13.2.1, class

RE: Misc storage and QR sprinkler deduction

2013-11-20 Thread John Denhardt
As long as you are in Chapter 13, Chapter 11 modifiers apply as applicable. John It should be recognized that the above is my opinion as a member of the NFPA 13 Technical Committee on Sprinkler Discharge Criteria, and has not been processed as a formal interpretation in accordance with the

RE: resurrecting an old system

2013-11-20 Thread John Denhardt
I would suggest a slightly modified approach. Test and repair as needed until tight. Flush and then retest. You really need to flush and retest due to the leaks that might be uncovered after proper flushing. I agree with Scott on cost. Given the total cost in the end, it might be wiser for

RE: resurrecting an old system

2013-11-20 Thread Matt Grise
The other benefit to the owner with replacement is a warranty. If the system is patched back together, then it could end up being a source of constant headaches and expense if leaks start to show up. Replacing the system could end up being a faster option depending on how many rounds of