Re: Flow Test Residual and Pitot The Same?

2013-12-18 Thread rongreenman .
Very possible but unlikely to be accurate. What we find in the land of super pressure is the so little of the energy available being used to move water through a 2 1/2" hole I have seen residual drops so small as to be unmeasurable on the gauges we use. The way to get accurate numbers is to demand

Re: Abrasive Blasting Operation

2013-12-18 Thread Todd - Work
Goes back to my thought about clean room heads from earlier. Concealed head with a gasket Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT www.fpdc.com 860-535-2080 (ofc) > On Dec 18, 2013, at 6:13 PM, "Cahill, Christopher" > wrote: > > Can you use concealed heads? That w

RE: Abrasive Blasting Operation

2013-12-18 Thread Cahill, Christopher
Can you use concealed heads? That way the plate takes a beating and is easily replaced without risking the head. Leave them with a case of covers it rather cheap. I did it once. Chris Cahill, PE* Senior Fire Protection Engineer Burns & McDonnell 8201 Norman Center Drive Bloomington, MN 55437

RE: Flow Test Residual and Pitot The Same?

2013-12-18 Thread Mark A. Sornsin, P.E.
Correct me if I'm wrong - I was a C+ student in college after all - but I believe it is possible to have a residual the same as the Pitot, but highly unlikely. In order for it to happen, you must convert all the energy (pressure) in the system to velocity, with no measurable losses. In the cas

RE: Flow Test Residual and Pitot The Same?

2013-12-18 Thread Brad Casterline
there is an elevation difference of 7'-11" between the two hydrants? -Original Message- From: Cahill, Christopher [mailto:ccah...@burnsmcd.com] Sent: Wednesday, December 18, 2013 4:44 PM To: sprinklerforum@lists.firesprinkler.org Subject: Flow Test Residual and Pitot The Same? I have a f

RE: Abrasive Blasting Operation

2013-12-18 Thread Jeremy Frazier
Unless you can apply the requirements of IBC 2009 903.3.1.1.1 (2) I would have to say you are stuck putting sprinklers in it. As far as how to sprinkler it, It seems the need to protect it from mechanical damage and the need to suppress the fire are contradictory. Other than a head guard, yo

RE: Flow Test Residual and Pitot The Same?

2013-12-18 Thread John O'Connor
Chris, With any flow test on plans or in specs we receive, we check that the pitot (resulting in GPM via chart or formula) is not one and the same. If so, we immediately suspect a single fire hydrant test. Without the residual, the static and gpm are meaningless. It is indeed possible for the 20

Flow Test Residual and Pitot The Same?

2013-12-18 Thread Cahill, Christopher
I have a flow test report showing the residual and pitot pressure being the same. 60 static, 20 residual with a 20 pitot on a 2.5" opening for 750 gpm. I talked to the contractor and they described doing it correctly, two hydrants one static/residual, one flowing. I don't believe it's possible

RE: Abrasive Blasting Operation

2013-12-18 Thread Forest Wilson Fire Sprinkler Contractor
For clarification,  only cellophane bags are permitted.  The common sandwich bags are not cellophane and not acceptable for covering a sprinkler with.  Forest Wilson Fire Sprinkler Contractor 937-736-0425 Notice: This message is confidential. It may also be privileged or otherwise protected by

RE: Abrasive Blasting Operation

2013-12-18 Thread Craig.Prahl
How long is someone going to direct the blast at a sprinkler? If you were using fusible link sprinklers, it would take a deliberate and lengthy action of directing a discharge from the blast nozzle at the sprinkler before it would fail. Have you ever tried to accidently knock the element out

RE: Abrasive Blasting Operation

2013-12-18 Thread Jim Kettler
That was primarily my question - how do we keep them from activating a sprinkler via the spray from the blaster. Jim -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd - Work Sent: Wednesda

Re: Abrasive Blasting Operation

2013-12-18 Thread Todd - Work
Don't forget that the paper/cellophane bags are designed to protect against solvents adhering to sprinklers, not impact. You need to ask if they are going to provide sufficient protection from mechanical damage. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT www.fpdc.com 8

RE: Abrasive Blasting Operation

2013-12-18 Thread Taylor, Galen
Roland, I guess I don't know poly from cellophane. My statement was clearly misleading... NFPA 33 Standard for Spray Application Using Flammable or Combustible Materials 2011 Edition, Section 9.4.7.1 states: "Sprinklers shall be permitted to be covered only by cellophane bags having a thicknes

Re: Abrasive Blasting Operation

2013-12-18 Thread Roland Huggins
we use to use sandwich bags all the time. We've tightened that up by adding text to the annex of 25 pointing out that a cellophane bag is allowed but a sandwich bag is a plastic bag (a poly family) with a bad end result. A.5.4.1.8.1 Typical sandwich bags purchased in a grocery store are genera

RE: Abrasive Blasting Operation

2013-12-18 Thread Taylor, Galen
Jim, I would think walnut shells to be a better blasting media for the purpose to protect precision machined surfaces, but they're probably using steel to achieve more "tooth" for the corrosion resistant coating they apply next. Nevertheless, to protect sprinkler heads from accumulating "media

Re: Abrasive Blasting Operation

2013-12-18 Thread Todd Williams
Not much will survive a direct blast, but a clean room head might give you reasonable protection. Include inspecting the cover plates on the 25 inspection. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 www.fpdc.com > On Dec 18, 2013, at 11:37 AM, Jim Kettle

RE: Abrasive Blasting Operation

2013-12-18 Thread Jim Kettler
E) All of the above. The plant refinishes large industrial parts and reapplies corrosion resistant coatings. Agreed that they should be not blasting the ceiling, but that seems nearly impossible to prevent. Jim -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.or

RE: Abrasive Blasting Operation

2013-12-18 Thread Craig.Prahl
What are they blasting for, to remove paint or finishes or rust or ? The sprinklers would be a the ceiling of the booth, the operator shouldn't be shooting blasting media at the ceiling. Craig L. Prahl, CET Fire Protection Group Lead CH2MHILL Lockwood Greene 1500 International Drive Spa

Abrasive Blasting Operation

2013-12-18 Thread Jim Kettler
We have a facility installing a large new abrasive blasting booth. The booth uses steel grit/shot. Is there a requirement for the fire sprinkler system to be extended into the booth? If so, how are the sprinklers protected? It used solely for abrasive blasting - the spray finishing operations a