Re: Resi Riser - Character set not allowed

2016-07-21 Thread Bruce Verhei
Caution with silver bullet use. On multistory may not work of air is trapped out on intermediate floors. Match bullet spec to type of vampire. > On Jul 21, 2016, at 11:11, Charles Thurston wrote: > > Hello rongreenman, > > I have seen this before on a large grid with a 20 year old alarm valve

RE: Resi Riser - Character set not allowed

2016-07-21 Thread Mike Henke
The cycling of the flowswitch is caused by air trapped in the system. This is the reason that the current edition of NFPA 13 requires some sort of vent or a remote ITV. Potter has a technical memo on this subject, please see below. Vane type waterflow switches should be tested using the inspecto

Re: Resi Riser - Character set not allowed

2016-07-21 Thread rongreenman .
Tom, Another good idea. The changing pitch at the back flow/riser location would suggest that this could be the, or a cause. One of the weird pattern Febco's but I can't recall which at the moment. On Thu, Jul 21, 2016 at 11:08 AM, Tom Duross wrote: > This happened once to me and it was the ba

Re: Resi Riser - Character set not allowed

2016-07-21 Thread Charles Thurston
Hello rongreenman, I have seen this before on a large grid with a 20 year old alarm valve in it, Air trapped in the grid was the problem, Found a large section where the mains and branch lines had been raised over the drain, Had to run an Auxiliary Drain off the high part to vent air and then a

RE: Resi Riser - Character set not allowed

2016-07-21 Thread Tom Duross
This happened once to me and it was the backflow opening and closing checks, does the pressure change on the gauge? We took out the checks and it worked beautifully, then got both 3# checks and it worked. Silver bullet. If not, then I would agree on trapped air expanding and contracting.

Re: Resi Riser - Character set not allowed

2016-07-21 Thread rongreenman .
I'm seeing a consensus here that the problem has to do with the cushioning effect of air and that eliminating air inside the piping is a good idea. On Thu, Jul 21, 2016 at 10:45 AM, Mark Phillips wrote: > Air Vent up High > > > > *From:* Sprinklerforum [mailto: > sprinklerforum-boun...@lists.fir

Re: Resi Riser

2016-07-21 Thread rongreenman .
Bruce, This is a single story, though high bay, building. But large and expansive. According to the tech he did the test last year and it worked properly. This guy is pretty thorough though without a lot of experience. The previous tech is very suspect (and fortunately no longer in the industry) a

RE: Resi Riser - Character set not allowed

2016-07-21 Thread Mark Phillips
Air Vent up High From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of rongreenman . Sent: Thursday, July 21, 2016 1:15 PM To: sprinklerforum@lists.firesprinkler.org Subject: Resi Riser - Character set not allowed Anyone experienced this before? The original

Re: Resi Riser

2016-07-21 Thread rongreenman .
Ed, The main drain and ITV are combined like a test and drain. And I agree with the air, but it's within the city system as this ITV is about three feet from the DCVA. But lots of bends. UG there is a 4" 90, followed by another five feet later running directly into the DCVA, then three more nineti

Re: Resi Riser

2016-07-21 Thread Bruce Verhei
Ed types faster than I. I've seen a four story office building that would do this indefinitely. Others on the same cluster of buildings would by chance alarm during pressure fluctuations up to five minutes after flow started. (Fitter showed me he could trigger alarm by skilled use of main drai

RE: Resi Riser

2016-07-21 Thread edkvining
I should have added that it is unusual to see the flow switch ahead of the main drain.ain. Sent from my Verizon Wireless 4G LTE smartphone Original message From: "rongreenman ." Date: 07/21/2016 10:15 AM (GMT-08:00) To: sprinklerforum@lists.firesprinkler.org Subjec

RE: Resi Riser

2016-07-21 Thread edkvining
Ron i bet you have a very large system or a multi storage building. You're looking at the effect of a lot of hair in the piping. It is a pretty common experience. One way to avoid it is to fill the system with the ITV open. Usually this will eliminate a lot of the trapped air Sent from m

Resi Riser

2016-07-21 Thread rongreenman .
Anyone experienced this before? The original CSC version of the Tyco rest riser in four inch. http://tyco-fire.com/index_link.php?link=TFP962&_ga=1.123267982.464632162.1469119864 Flow throw the IT port and you can watch the lever in the flow switch move and then, before alarming, move back to th

Re: Small high hazard under dry system

2016-07-21 Thread rongreenman .
To my understanding: Yes and yes. On Thu, Jul 21, 2016 at 9:31 AM, Todd Williams wrote: > Section 11.1.2 permits a higher hazard area within a larger space to be > protected with sprinklers over the hazard and 15 ft beyond. Since nothing > is stated, I assume this can be done with a dry system.

RE: Small high hazard under dry system

2016-07-21 Thread Richard Carr
The total remote area should be increased by 30% but no increase needed for the 15 ft. Richard Carr, SET Branch Manager Cox Fire Protection, Inc 6555 Grace Lane. Jacksonville, Fl. 32205 rc...@coxfire.com 904-781-8227 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On

Small high hazard under dry system

2016-07-21 Thread Todd Williams
Section 11.1.2 permits a higher hazard area within a larger space to be protected with sprinklers over the hazard and 15 ft beyond. Since nothing is stated, I assume this can be done with a dry system. Is a 30% increase in area for the calculation required? Todd G Williams, PE Fire Protection