[Sprinklerforum] Re: Sizing of pipe below obstructions

2022-08-23 Thread Brett Peters
Here is how I see the argument If you pipe the sprinkler with a smaller diameter line then that sprinkler has to be part of your hydraulic calculation (arguably you could just switch to the sprinkler below the obstruction and remove the sprinkler above the obstruction, as you are not required to

[Sprinklerforum] Re: Sizing of pipe below obstructions

2022-08-23 Thread Fpdcdesign
What I have is an ESFR system where i need to add a single sprinkler in 2 locations under ducts. 23.4.4.7.3.1 states that sprinklers under obstructions do not need to be included in hydraulic calculations. 23.4.4.7.3.2 states that if the sprinklers are under obstructions are piped

[Sprinklerforum] Re: Sizing of pipe below obstructions

2022-08-23 Thread Derrek Crigler
NPFA 13 2016 23.4.4.7.3.2 From: Fpdcdesign Sent: Tuesday, August 23, 2022 9:30 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: Sizing of pipe below obstructions Brett, any specific reference for that? On Aug 23, 2022 at 12:21 PM,

[Sprinklerforum] Re: Sizing of pipe below obstructions

2022-08-23 Thread Fpdcdesign
Brett, any specific reference for that? > > On Aug 23, 2022 at 12:21 PM, mailto:br...@proudline.ca)> > wrote: > > > > Typically non storage sprinkler supplied with 1" > Storage type sprinkler supplied with same size as branch line (typical for > ESFR

[Sprinklerforum] Re: Sizing of pipe below obstructions

2022-08-23 Thread Brett Peters
Typically non storage sprinkler supplied with 1" Storage type sprinkler supplied with same size as branch line (typical for ESFR sprinklers) Thanks Brett Peters General Manager Installation & Design Proudline Fire Protection Services Ltd. br...@proudline.ca 780 490 7602 office ext 202 780 490

[Sprinklerforum] Re: Sizing of pipe below obstructions

2022-08-23 Thread Matthew J Willis
Nothing showing up? Same as branch above? R/ Matt Matthew J. Willis, CWBSP Rapid Fire Protection, Inc. 600 E. Carlson St. Suite AB | Cheyenne, WY. 82009 Office (307) 426-4077 ext. 404 Direct (307) 316-6630 Cell (605) 391-2733 [cid:image001.png@01D8B6D8.8DF7AD40] From: Fpdcdesign Sent:

[Sprinklerforum] Sizing of pipe below obstructions

2022-08-23 Thread Fpdcdesign
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (tel:860-535-2080) (ofc) 860-554-7054 (tel:860-554-7054) (fax) 860-608-4559 (tel:860-608-4559) (cell) _