[Sprinklerforum] Re: [EXTERNAL] Water filled Sprinkler Pipe Condensate issue

2023-08-08 Thread John Denhardt
I have personally installed many wet systems in cooler boxes.  As Craig stated, once the water in the pipe reaches the temperature of the box, I have never seen an issue like this. I would suggest getting the HVAC contractor and their engineer involved.  Something sounds off in their system. John J

[Sprinklerforum] Re: Phantom Flow Location on Subsystem

2023-08-08 Thread Bob Knight
It is added at the point of connection.  So wherever your line connects to the existing system you add an inside hose demand at the most remote point of connection.  Basically, in your case it will be the point that you have connected to the existing grid. /Thank you, Bob Knight, CET III// /*/

[Sprinklerforum] Re: Phantom Flow Location on Subsystem

2023-08-08 Thread Travis Mack
Per 2013, you add at end of new branch line where it touches cross main. Per 2022, you add where new system touches old. Obviously these are paraphrased and you should refer to documents for exact language. I’ve been able to use the new standards as clarification to the older standard language

[Sprinklerforum] Phantom Flow Location on Subsystem

2023-08-08 Thread Anthony Johnson
Hey Y'all, Where should the phantom flow required by 23.4.4.1.1.5 (2013 ed) go when the new calculation are for a new subsystem added on to an existing system. The existing interior system is a grid and the new subsystem is a small antifreeze system. I can add the phantom flow at the most remote br

[Sprinklerforum] Re: [EXTERNAL] Water filled Sprinkler Pipe Condensate issue

2023-08-08 Thread Kyle . Montgomery
Is the whole sprinkler system in the cool area? Or is there a ceiling with drops down to sprinklers into the cooler and the branch lines above in the warm area? If that is the case, then it makes sense that the drops would be colder than the surrounding air and would have condensation issues. I

[Sprinklerforum] Re: [EXTERNAL] Water filled Sprinkler Pipe Condensate issue

2023-08-08 Thread AKS-Gmail-IMAP
It will be a sprinkler system issue. The piping is going to rust from the outside to its inside. The first rust signs may not be visible from below because it can start to happen on the pipe’s top edge which cannot be seen from below. I have seen this happen myself. > On Aug 8, 2023, at 3:22 PM

[Sprinklerforum] Re: [EXTERNAL] Water filled Sprinkler Pipe Condensate issue

2023-08-08 Thread Fpdcdesign
Tim, Craig pretty much nailed it. This is not a sprinkler issue. The HVAC crowd needs to solve this. My concern is why is this a wet system to begin with? Somewhere there is a chiller that is pumping out air a lot colder then 40 degrees to maintain that temperature; probably at roof

[Sprinklerforum] Re: [EXTERNAL] Water filled Sprinkler Pipe Condensate issue

2023-08-08 Thread Brett Peters
Not a sprinkler problem, is a humidity problem, they need to go to their cooler people and figure out how to get rid of the humidity. On Tue, Aug 8, 2023 at 2:22 PM Prahl, Craig wrote: > Walk away from this one. This is not a sprinkler system issue. It’s a > climate control issue. It’s odd th

[Sprinklerforum] Re: [EXTERNAL] Water filled Sprinkler Pipe Condensate issue

2023-08-08 Thread Prahl, Craig
Walk away from this one. This is not a sprinkler system issue. It's a climate control issue. It's odd that a non-flowing system (sprinklers) is sweating. At some point the static water in the piping should acclimate to the room temperature unless there's an issue with heat stratification in t

[Sprinklerforum] Re: Water filled Sprinkler Pipe Condensate issue

2023-08-08 Thread Steve Leyton
I would DEFINITELY not get involved; my take would be that I'm not a mechanical engineer, haven't ever experienced this phenomenon, don't know what's causing it or how to resolve. That said, a couple questions: 1. Is there any insulation at the roof? Is there anything between the piping an

[Sprinklerforum] Re: Water filled Sprinkler Pipe Condensate issue

2023-08-08 Thread John O'Connor
Tim, Is any of the building steel sweating? If not, is this grid system circulating water colder than the interior air temperature. I just cannot fathom why you are getting a condensation issue. John R. O’Connor, SET, RME National Fire Sprinklers, Inc. 2601 Elm Hill Pike, Suite J

[Sprinklerforum] Water filled Sprinkler Pipe Condensate issue

2023-08-08 Thread tstone52
A recently installed wet pipe sprinkler system protecting 25’ high rack storage of Class 3 Commodity. The warehouse is kept cool between 40° & 45° F. (aging Cheese). The Sprinkler system is a Grid Pipe with branch line piping installed about 12”+ down below the roof deck. The pipes sweat profusely

[Sprinklerforum] Re: [EXTERNAL] Re: Sprinklers in column enclosures

2023-08-08 Thread Prahl, Craig
The omission of a requirement does not create a requirement. You can never prove a negative. I’ve had this argument before with someone saying I had to prove something wouldn’t happen. It’s just not possible. Does the code say I have to do it? Does the code address this particular occurrenc

[Sprinklerforum] Re: [EXTERNAL] Re: Sprinklers in column enclosures

2023-08-08 Thread Ron Greenman
I hate to solve technical problems that aren't really problems by adding cost to a jib but if the BI is not going to budge change the wood framing design around the columns to steel and you have a non-combustible concealed space. Or if already framed go with Chris' suggestion. I once had an AHJ war

[Sprinklerforum] Re: [EXTERNAL] Re: Sprinklers in column enclosures

2023-08-08 Thread Fpdcdesign
The building is built of steel columns and main beams but the rest of the structure (joists, trusses, floors, other framing) is wood. I don’t have the details of what the construction is at the floor around the column. The problem with asking the BI to show where the Code sa

[Sprinklerforum] Re: [EXTERNAL] Re: Sprinklers in column enclosures

2023-08-08 Thread Prahl, Craig
I can’t see how you could shoe-horn this into resembling a chase since a chase typically penetrates floors and creates a shaft. This column does not penetrate floors, does it? Why would this not be the same condition as an exterior column but just on the interior? What is the logic behind omi

[Sprinklerforum] Re: Sprinklers in column enclosures

2023-08-08 Thread Chris Dorn
Shove it full of insulation and presto! You have non-combustible enclosed blind space which is not required to be protected. Chris Dorn From: Fpdcdesign Sent: Tuesday, August 8, 2023 9:10 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: Spri

[Sprinklerforum] Re: Sprinklers in column enclosures

2023-08-08 Thread Fpdcdesign
Ken, I totally agree with you. However, we are dealing with an NFPA 13 fundamentalist. If it’s not specifically written there, it is wrong. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (tel:860-535-2080) (ofc) 860-554-7054 (

[Sprinklerforum] Re: Sprinklers in column enclosures

2023-08-08 Thread Ken Wagoner
Todd, Although I agree that the space you're discussing is not actually a "pipe chase" or an "exterior column" I view this as a circumstance where -13 does not directly address the issue at hand.  I submit that a "pipe chase" comes the closest to describing what is taking place. So, I looked

[Sprinklerforum] Re: Sprinklers in column enclosures

2023-08-08 Thread Fpdcdesign
This phase of the project was designed using 2013 but the next phase will be using 2019. The argument from the BI is that it is not a pipe chase nor an exterior column. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (tel:860-535-