I have 18” wide concrete beams extending 24” from the bottom of the deck on 7’-0” centers.
NFPA-13 (2016) 8.6.4.1.2 Obstructed Construction (5)* Installed with deflectors of sprinklers under concrete tee construction with stems spaced less than 71⁄2 ft (2.3 m) on centers, regardless of the depth of the tee, located at or above a horizontal plane 1 in. (25 mm) below the bottom of the stems of the tees and complying with Table 8.6.5.1.2. A.8.6.4.1.2(5) For concrete joists spaced less than 3 ft (900 mm) on center, the rules for obstructed construction shown in 8.6.4.1.2 apply. For concrete tee construction with stems spaced less than 7 ft 6 in. (2.3 m) on center, the sprinkler deflector can be located at or above a horizontal plane 1 in. (25 mm) below the bottom of the stems of the tees. This includes sprinklers located between the stems. [See Figure A.8.6.4.1.2(5).] I am getting caught up in semantics with the wording. Would a concrete beam be interpreted the same as a concrete tee? Am I allowed to install the deflectors above one-inch below the bottom of the beam in accordance with Table 8.6.5.1.2 as I would be if they were concrete tees, or will pocket protection be required? Sincerely; Jackie "JW" Ward; SET 1-405-240-7076 jw...@firetrol.net<mailto:jw...@firetrol.net> NICET IV Cert. No. 104187 Victaulic Vortex Integrator Firetrol Protection Systems 108 NW 132nd Street; Oklahoma City, OK 73114 405-752-2330 Ext. 10230 Fax:405-752-2297 License No: AR-FSS-162, LA-F415, OK-863 & 302, TX - ECR-1751432, ACR-1751168, SCR-G-0292 [cid:image001.png@01DA5B6B.185D7FE0][Firetrol Oklahoma City BACK] [cid:image003.png@01DA5B6B.185D7FE0]
_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org