Negative. It can still be connected to the fire pump and be a manual wet standpipe. It only becomes an automatic standpipe if/when the fire pump and water supply is sufficient for the standpipe to operate properly without the fire department providing flow/pressure through the FDC.
And, although the answer to Brian’s initial question seems kind of obvious, you might be surprised to find out how many reviewers/AHJs/etc see a fire pump on a project and immediately assume that it has to be sized for the standpipe demand (automatic standpipe). I’ve definitely gone through the “it has a fire pump, therefore it must be an automatic standpipe” dance a time or two. -Kyle M From: Anthony Johnson <mountainfirepr...@gmail.com> Sent: Thursday, June 8, 2023 8:01 AM To: Discussion list on issues relating to automatic fire sprinklers <sprinklerforum@lists.firesprinkler.org> Subject: [EXTERNAL] [Sprinklerforum] Re: Manual Wet Standpipe & Pump Yes, the answer is in your question since a manual wet standpipe requires a fire truck. If you were to connect the standpipe to the pump it would no longer be a manual wet standpipe - it would be an automatic wet standpipe. [https://s-install.avcdn.net/ipm/preview/icons/icon-envelope-tick-green-avg-v1.png]<https://urldefense.com/v3/__http:/www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail__;!!Ba8_KKAT!JWSRjTmQDT51PJNQHkfXckv0QZuX55Lu5qjtKHPF7PpKMy8Ob_ndzgDTSUuFvxaWsNstlJED9isfdLfJ_L6K2r1ASURuww$> Virus-free.www.avg.com<https://urldefense.com/v3/__http:/www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail__;!!Ba8_KKAT!JWSRjTmQDT51PJNQHkfXckv0QZuX55Lu5qjtKHPF7PpKMy8Ob_ndzgDTSUuFvxaWsNstlJED9isfdLfJ_L6K2r1ASURuww$> On Thu, Jun 8, 2023 at 7:19 AM Brian Harris <bhar...@bvssystemsinc.com<mailto:bhar...@bvssystemsinc.com>> wrote: If a building has manual wet standpipes and a fire pump could the pump be sized to meet the system demand of the sprinklers only since the fire truck will be providing the demands of the standpipe? Brian Harris, CET BVS Systems Inc. bvssystemsinc.com<https://urldefense.com/v3/__http:/bvssystemsinc.com/__;!!Ba8_KKAT!JWSRjTmQDT51PJNQHkfXckv0QZuX55Lu5qjtKHPF7PpKMy8Ob_ndzgDTSUuFvxaWsNstlJED9isfdLfJ_L6K2r2xZoZ_mA$> Phone: 704.896.9989 Fax: 704.896.1935 _________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.com/v3/__https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org__;!!Ba8_KKAT!JWSRjTmQDT51PJNQHkfXckv0QZuX55Lu5qjtKHPF7PpKMy8Ob_ndzgDTSUuFvxaWsNstlJED9isfdLfJ_L6K2r0JoGk3ew$> To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>
_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org