ugust 9, 2022 1:33 PM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> sprinklerforum@lists.firesprinkler.org>
> *Subject:* [Sprinklerforum] Re: ESFR Question
>
>
>
> NFPA 13 12.3 - elevation change of at least 2'-0 and above an aisle with a
&
] Re: ESFR Question
Now that I looked at §12.3(3) it supports that the extension of the higher
demand from an upper level to a lower level isn't required, if that ceiling
change is located an aisle of 2' in depth on either side.
For the record, Bruce - what is the concern re
Now that I looked at §12.3(3) it supports that the extension of the
higher demand from an upper level to a lower level isn't required, if
that ceiling change is located an aisle of 2' in depth on either side.
For the record, Bruce - what is the concern regarding QR sprinklers?
They're not req
Can I assume that this elevation change would serve the same purpose as a draft
curtain or would one still be needed?
Bruce
From: Brett Peters
Sent: Tuesday, August 9, 2022 1:33 PM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: ESFR
NFPA 13 12.3 - elevation change of at least 2'-0 and above an aisle with a
minimum of 2'-0 of clearance to each side of the center of the aisle.
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.