[Sprinklerforum] Re: Elbows in pump suction

2023-07-14 Thread Brett Peters
Also if you look at - 4.15.6.3.3 Elbows and tees with a centerline plane perpendicular to the horizontal split-case pump shaft shall be permitted at any location in the pump suction intake - This says to me that the suction piping could be going up or down and your current configuration sounds like

[Sprinklerforum] Re: Elbows in pump suction

2023-07-14 Thread Hinson, Ryan
ng to automatic fire sprinklers Subject: [Sprinklerforum] Re: Elbows in pump suction Your fire pump testing is allowed to be done at actual system demand if the water supply is not capable of providing water for full flow of the fire pump 14.2.6.2.4 Where the maximum flow available from the water su

[Sprinklerforum] Re: Elbows in pump suction

2023-07-14 Thread Brett Peters
Your fire pump testing is allowed to be done at actual system demand if the water supply is not capable of providing water for full flow of the fire pump 14.2.6.2.4 Where the maximum flow available from the water supply cannot provide a flow of 150 percent of the rated flow of the pump, the fire p

[Sprinklerforum] Re: Elbows in pump suction

2023-07-14 Thread Eric Rieve
: Fpdcdesign Sent: Friday, July 14, 2023 2:07 PM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: Elbows in pump suction Eric, My main question is if the 10 diameter requirement can be split into 2 section or does it have to be one continuous length

[Sprinklerforum] Re: Elbows in pump suction

2023-07-14 Thread matthew.willis1
2:07 PM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: Elbows in pump suction Eric, My main question is if the 10 diameter requirement can be split into 2 section or does it have to be one continuous length? The problem is that the suction press

[Sprinklerforum] Re: Elbows in pump suction

2023-07-14 Thread Fpdcdesign
Eric, My main question is if the 10 diameter requirement can be split into 2 section or does it have to be one continuous length? The problem is that the suction pressure on the pump test goes to 0 psi at 1500 gpm. Based on my calculations, it should be around 17 psi. I kno

[Sprinklerforum] Re: Elbows in pump suction

2023-07-14 Thread Eric Rieve
Todd, Like Brett mentioned, going vertical to eat up pipe length is shown in the annex of NFPA 20, and I’ve seen/used that approach before. When you say there is a problem with the test, is this for a new fire pump installation? Are you not meeting your curve, and if so, are you off by a substa

[Sprinklerforum] Re: Elbows in pump suction

2023-07-14 Thread Brett Peters
If you look at FIGURE A.4.15.6 Right and Wrong Pump Suctions, one of the diagrams does show something similar to what you are proposing. I will be on Holidays from August 12th to 21st, returning to work on Tuesday August 22nd Thanks Brett Peters General Manager Installation & Design Proudline Fi