Re: 13R requirements for garages

2007-09-19 Thread [EMAIL PROTECTED]
Nancy, I don't interpret it that way. If you notice the garages references in 6.7.3 are all described as being attached, and the commentary you mention in 6.8 refers you back to 6.7.3. There is no reference to detached garages in 13R. PARSLEY CONSULTING Ken Wagoner, SET 760.745.6181 voice

RE: 13R requirements for garages

2007-09-19 Thread Craig.Prahl
Does the Building Code require a residential detached garage to be sprinkled? If not then 13R has no application. Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax

Re: 13R requirements for garages

2007-09-19 Thread Ron Greenman
The easiest way to answer this is to remember that 13R is an installation standard and not a code therefore it can't tell you where sprinklers are required but merely how you do when they are. 6.7.3.1 pretty much says this when it states that if the code would consider the garage to be a separate b

13R requirements for garages

2007-09-18 Thread Jones, Nancy
Is it the intent of 6.7.3 and the commentary for 6.8 in the 2002 edition of 13R to require a detached garage to be protected? Thanks, Nancy Jones Fire Marshal Brentwood, TN ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http:/