You probably will not have much competition in bidding.
Get an inventory of the chemicals (Safety Data Sheets or simple listing)
identifying the chemicals to be:
stored,
used in closed containers,
used in the open.
Find out the storage configuration, the use configurations, operating
ig.pr...@ch2m.com
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Gregory Lindholm
Sent: Tuesday, December 27, 2016 2:49 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Insecticides, Fungicides & Herbicides [EXTERNAL]
We have been asked to quote a
2016 3:46:55 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Insecticides, Fungicides & Herbicides [EXTERNAL]
There issue appears to be discharged sprinkler water tainting by the
insecticides, and then containing and cleaning the water run-off.
If proper containment (e.g. diking,
y sight when
> things go wrong.
>
>
>
> Matt Grisé
>
>
>
>
>
> *From:* Sprinklerforum [mailto:sprinklerforum-bounces@lists.firesprinkler.
> org] *On Behalf Of *Todd Williams
> *Sent:* Tuesday, December 27, 2016 1:51 PM
> *To:* sprinklerforum@lists.firesprinkle
There issue appears to be discharged sprinkler water tainting by the
insecticides, and then containing and cleaning the water run-off.
If proper containment (e.g. diking, trench drains, slope to catch basin) is
provided, this may be an opportunity to bid on a low competition job
without much extra
y sight when things go wrong.
Matt Grisé
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Todd Williams
Sent: Tuesday, December 27, 2016 1:51 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Insecticides, Fungicides & Herbicides
Ask them
Ask them to have an FPE evaluate the protection requirements for the
occupancy. If this is a design build deal, I wouldn't go near it.
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
via Newton Mail
[https://cloudmagic.com/k/d/mailapp
We have been asked to quote a sprinkler system that has some stuff that says
things like:
Class A Fire Extinguishers Only, or
Do Not Use Water, or
Do Not Use Water Jets For Extinguishing, use Power, Sand or Carbon Dioxide
They list IBC Classifications of H-3 or H-4.
What do we do with this