When doing a thumbnail estimate like this, I use Density X Design Area X 1.25
to estimate a flow rate.
So 0.10 X 1500 X 1.25 = 187.5 gpm. Rounding up, 190 GPM (since we're just
estimating) X 30 minutes = 5700 gallons.
For a pump I'd pick something around a 150 gpm rate for this.
Your results
: sprinklerforum@lists.firesprinkler.org
Subject: RE: [EXTERNAL] RE: Pump & Tank Fed From a Well
When you are sizing a tank for scenarios like this, do you size for minimum
required discharge (assuming all heads in remote area operating) or expected
actual discharge (assuming all heads in re
"The bitterness of poor quality remains long after the sweetness of low
price is forgotten."
From: Sprinklerforum On
Behalf Of Kyle.Montgomery
Sent: Wednesday, May 22, 2019 2:09 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: [EXTERNAL] RE: Pump & Tank Fed From a
When you are sizing a tank for scenarios like this, do you size for minimum
required discharge (assuming all heads in remote area operating) or expected
actual discharge (assuming all heads in remote area operating)?
Since we're working with hypotheticals, let's say you design a system to work