Based on what, specifically?
Steve
Original message
From: tcfire <tcf...@bellsouth.net>
Date: 12/21/17 5:54 AM (GMT-08:00)
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Corrosion
Seems to make a great argument for nitrogen infusion.
Sent from my Sprint S
Seems to make a great argument for nitrogen infusion.
Sent from my Sprint Samsung Galaxy S7.
Original message From: Steve Leyton
<st...@protectiondesign.com> Date: 12/20/17 8:51 PM (GMT-05:00) To:
sprinklerforum@lists.firesprinkler.org Subject: RE: Corrosion
Th
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Corrosion
I’m relying on Lucas to correct any statement that are just wrong but -
predicting corrosion is a lot like predicting a medical disease. We know a lot
of facts that affect the issue but there’s a SH factor that’s not yet
quantifiable. SH = Stuff
Meeting with them tomorrow to do just that.
Oh Merry Christmas to all!!
Sent from my iPhone
On Dec 20, 2017, at 6:50 PM, Roland Huggins
> wrote:
I’m relying on Lucas to correct any statement that are just wrong but -
predicting
I’m relying on Lucas to correct any statement that are just wrong but -
predicting corrosion is a lot like predicting a medical disease. We know a lot
of facts that affect the issue but there’s a SH factor that’s not yet
quantifiable. SH = Stuff Happens
After seven events, why haven’t they
: Re: Corrosion
Trying to explain to the owner why it's happened seven (7) times on the same
system
has been a problem.
From: Sprinklerforum
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
[mailto:fsl...@msn.com]
Sent: Wednesday, December 20, 2017 4:30 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Corrosion
Trying to explain to the owner why it's happened seven (7) times on the same
system
has been a problem.
From: Sprinklerforum
No but that's good thought
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> on behalf
of Joe Burtell <j...@burtellfire.com>
Sent: Wednesday, December 20, 2017 5:33 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Corro
; *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* Re: Corrosion
>
> Yes, And on the same first section of a 4" bulk main immediately following
> the rise, and after that piece had been replaced. At no more the four feet
> away from it's reflected twin riser com
r 20, 2017 5:22 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Corrosion
Yes, And on the same first section of a 4" bulk main immediately following the
rise, and after that piece had been replaced. At no more the four feet away
from it's reflected twin riser coming off
>
>
> *From:* Sprinklerforum [mailto:sprinklerforum-bounces@lists.firesprinkler.
> org] *On Behalf Of *Scott Futrell
> *Sent:* Wednesday, December 20, 2017 4:12 PM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* RE: Corrosion
>
>
>
> This sender failed our
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Corrosion
This sender failed our fraud detection checks and may not be who they appear to
be. Learn about spoofing<http://aka.ms/LearnAboutSpoofing>
Feedback<http://aka.ms/SafetyTipsFeedback>
Wet or dry?
Scott
Office: (763) 425-1001 x 2
Cel
Wet!
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> on behalf
of Scott Futrell <sco...@ffcdi.com>
Sent: Wednesday, December 20, 2017 5:11 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Corrosion
Wet or dry?
Sco
Wet or dry?
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Mike Hairfield
Sent: Wednesday, December 20, 2017 4:11 PM
To: Sprinkler Forum
Subject: Corrosion
Stainless steel pipe would be suitable
Perhaps copper too.
Nicky Marshall
Branch Manager (Blenheim)
Protech Design
Specialist Fire Protection Consultants
03 579 5577
021 433 488
www.protechdesign.co.nz
skype: nicky-marshall
105A Alabama Rd, Redwoodtown, Blenheim 7201, New Zealand
PO Box 4022,
them?
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Nicky
Marshall
Sent: Wednesday, May 01, 2013 4:28 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Corrosion Resistant Pipe
I'm thinking there could be several steel pipes out there that are
corrosion resistant, either due to alloy or to coating, but I coyuldn't say
in dyna thread would be amomgst them.
On Mon, Apr 29, 2013 at 12:12 PM, Gregory Lindholm greg0...@msn.com wrote:
NFPA 13 - 2013, section 8.3.4.4 states
I am going with the likelihood that there are 5 Gozillionaires following this
list, regardless of definition.
bv
- Original Message -
From: Thom tmcmahon @ firetechinc .com
To: sprinklerforum @lists. firesprinkler .org
Sent: Monday, April 29, 2013 2:50:35 PM
Subject: RE: Corrosion
Good question. We just use S40 for everything DoD.
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris Cahill
Sent: Tuesday, February 15, 2011 1:07 PM
To:
We had this situation at a job we're doing now, and we ended up getting the
MIC testing from Potter, and got galvanic corrosion reports from the water
authority. The EoR accepted the system-wide report, but the water authority
also offered to do a spot test if they needed it. So I would check
Steve
With my previous-previous employer, I remember we had serious issues with
local made cast iron fittings in China, say 2002 - 2005 era.
OSY valves corroded, internal stem u/g valves seized in 12 months or so,
fittings showed accelerated corrosion.
Memory says we then gave it to
I ran into a similar problem with XL pipe while inspecting a leak on
sprig ups and found that the threads were cut to deep, it seemed like
only the sprigs with bad cuts were corroading not any other sprigs.
The system was only a few years old at the time ( more than ten years
ago). I
Steve,
Two suggestions:
- Could it be that the drops are filled with water (due to flushing)
and the branches are dry (due to draining or otherwaise)?
- Could it be that the fittings on top of the drops are warmer than
other fittings in the system (due to rising moist air from the room below)?
out of office 7/13/2009 to 7/20/2009
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org
To Unsubscribe, send an email
I think there is a lab in WA state which specializes in this. I think
their name is MCO?
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
I think your comment number 3 may be part of the problem, based on
what I am hearing. Also, are fittings made in all the way or can they
be? Are the drops threadable thinwall as well?
At 04:51 PM 7/10/2009, you wrote:
I'm trying to get my arms around a really interesting problem at a local
Is the concrete touching the drops or fitting?
Threads an inch above the fitting? wow
Greg McGahan
Operations Manager
Living Water Fire Protection
1160 McKenzie Road
P.O. Box 877
Cantonment, Florida 32533
(850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
g...@livingwaterfp.com
-0868 Fax
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Greg McGahan
Sent: Friday, July 10, 2009 5:19 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Corrosion Issues at Jail
Is the concrete touching
...@livingwaterfp.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve Kowkabany
Sent: Friday, July 10, 2009 4:51 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Corrosion Issues at Jail
(Greg) The concrete
Are we talking about XL? I would guess that the crew that performed the
final cutbacks threaded the pipe too shallow. If the space above ceiling is
plenum space, the leaks may never show themselves below ceiling.
I would be interested to see a fitting cut in half in order to find out
whether
Subject: Re: Corrosion Issues at Jail
I think there is a lab in WA state which specializes in this. I think their
name is MCO?
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send
installed in the cup.
Bobby
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jeff
Hewitt
Sent: Wednesday, April 16, 2008 10:47 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Corrosion Resistant Concealed Sprinkler Plate
We recenly went through
poly sprinkler with wax
touch-up installed in the cup.
Bobby
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jeff
Hewitt
Sent: Wednesday, April 16, 2008 10:47 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Corrosion Resistant Concealed Sprinkler