: Dormitory Bunk Beds
Tim,
I think it is addressed clearly in 8.5.5.3.2 which states that
Sprinklers shall not be required under obstructions
that are _not_ fixed in place such as conference tables. (emphasis
mine) I would think you could make an
excellent case that bunk beds are not fixed
Leyton
Protection Design Consulting
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John
Drucker
Sent: Wednesday, February 27, 2008 6:23 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Dormitory Bunk Beds
Tim,
I have to agree with the group. Where
, February 27, 2008 8:39 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Dormitory Bunk Beds
Thank you for the feedback concerning the moveable bunk beds. You
reiterated what I already new. The one thing we have to keep in mind is
even though we may not be able to place the sprinkler over the point
Tim,
I think it is addressed clearly in 8.5.5.3.2 which states that
Sprinklers shall not be required under obstructions
that are _not_ fixed in place such as conference tables. (emphasis
mine) I would think you could make an
excellent case that bunk beds are not fixed in place. I agree that
8.5.5.3.2 Sprinklers shall not be required under obstructions that are
not fixed in place such as conference tables.
Paul J. Pinigis, P.E.
Chief Life Safety Engineer
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of G. Tim
Stone
Sent: Tuesday, February
Tim:
I ran into this several years back doing a retrofit for a fraternity or dorm
(can't remember) for ASU. We were req'd to put the HSW under the upper
bunk. We put the head guards on to try to protect it some. It was all
exposed.
I don't recall hearing any issues where the kids set the
Movable furniture such as Conference tables are referenced and sprinklers
would not be required under them.
Brian Harris
FDFP INC.
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of G. Tim Stone
Sent: Tuesday, February 26, 2008 4:05 PM
To:
Of
[EMAIL PROTECTED]
Sent: Tuesday, February 26, 2008 4:17 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Dormitory Bunk Beds
Tim,
I think it is addressed clearly in 8.5.5.3.2 which states that
Sprinklers shall not be required under obstructions
that are _not_ fixed in place
Sprinklers below bunk beds? At some point we need to use some reason
here. That's probably the reason it isn't specifically addressed.
Otherwise what's next, sprinklering in dresser drawers?
Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500
]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Tuesday, February 26, 2008 3:17 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Dormitory Bunk Beds
Tim,
I think it is addressed clearly in 8.5.5.3.2 which states that
Sprinklers shall not be required under obstructions
that are _not_
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mike
Brown (TECH- GVL)
Sent: Tuesday, February 26, 2008 4:31 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Dormitory Bunk Beds
Years ago I made all of the arguments that I see you making and the old