BULLSEYE. Except for the small percentage of owners that hire a knowledgable
consultant, you have to visit the Smithsonian to see the ONE certification
otherwise completed.
Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives
Dallas, TX
h
I sit corrected. I was looking at 14.1. I've never seen one. Something no
one
enforces.
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
[https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2]
On Tue, Jan 5,
ssage-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Todd Williams
Sent: Tuesday, January 05, 2016 2:27 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Locker Rooms (who prepared the Owner's Certificate)
I believe the language in 1
Look at 4.3. IT is a SHALL be provided by the owner or their representative.
Having said that, I doubt that 1% of the jobs get it beforehand.
Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org
ts.firesprinkler.org
Subject: Re: Locker Rooms (who prepared the Owner's Certificate)
I believe the language in 13 says the Owner's Certificate should (not
shall) be
used. It is also in 2002 and I have never seem one.
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
8
I believe the language in 13 says the Owner's Certificate should (not
shall) be
used. It is also in 2002 and I have never seem one.
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
[https://cloudmagic.com/k/d/mail
"What about the Owner's Certificate required by 4.3 in the 2007 edition and for
all editions since then? Has anyone checked this document to see what the
declared use of the space is? Why does the sprinkler contractor always seem to
take on the responsibilities of others?"
Because - at least
rinkler.org] On
Behalf Of Bill Brooks
Sent: Tuesday, January 05, 2016 10:20 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Locker Rooms (who prepared the Owner's Certificate)
What about the Owner's Certificate required by 4.3 in the 2007 edition and for
all editions since then?
ailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Steve Leyton
Sent: Tuesday, January 05, 2016 12:41 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Locker Rooms
And my comments were in tacit support of your perspective, based on
historical performance. You are much more in touch wit
Sent: Tuesday, January 5, 2016 11:41 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Locker Rooms
And my comments were in tacit support of your perspective, based on historical
performance. You are much more in touch with what the good people of Lake
Oswego are going to do (or n
forum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Smith, David
Sent: Tuesday, January 05, 2016 9:36 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Locker Rooms
I understand (& support) your perspectives and was simply trying to answer
Todd's question of
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of aaron rohr
Sent: Monday, January 04, 2016 9:13 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Locker Rooms
Really,
Ask him if he wants all cabinets to be covered by OH1? Do you think the heads
are listed for closed compartments? Is
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Locker Rooms
Valid point for an engineer of record to ponder during the A/E design. But if
nothing is stated to a bidding contractor other than the space will be locker
rooms, than nothing should be inferred other than a standard, light hazard,
ineer |
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 |
http://www.kfiengineers.com
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Smith, David
Sent: Tuesday, January 5, 2016 10:01 AM
To: sprinklerforum@lists.firesprinkler.o
|
http://www.kfiengineers.com
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Smith, David
Sent: Tuesday, January 5, 2016 10:01 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Locker Rooms
I have seen portions of
m...@ci.oswego.or.us
300 B Avenue | PO BOX 369 Lake Oswego OR 97034
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Todd Williams
Sent: Monday, January 04, 2016 4:20 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Lock
Really,
Ask him if he wants all cabinets to be covered by OH1? Do you think the heads
are listed for closed compartments? Is NFPA 13 intended to cover every space?
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.fir
We sometimes protect the locker rooms as OH I when it is a school because they
often store items in there over the summer break. I have had a couple of AHJ's
ask for this.
Sent from my iPhone
> On Jan 4, 2016, at 6:20 PM, Todd Williams wrote:
>
> Storage of what?
>
> Todd G Williams, PE Fir
Storage of what?
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
[https://cloudmagic.com/k/d/mailapp?ct=pi&cv=6.0.64&pv=8.2]
On Mon, Jan 4, 2016 at 6:45 PM, sprinklerforum@lists.firesprinkler.org
wrote:
We have
@lists.firesprinkler.org
Subject: RE: Locker Rooms
Have always seen them as light hazard as well, and never had that design
basis questioned before.
Steve Leyton
Original message
From: James Crawford
Date: 1/4/2016 3:46 PM (GMT-08:00)
To: sprinklerforum@lists.firesprinkler.org
Have always seen them as light hazard as well, and never had that design basis
questioned before.
Steve Leyton
Original message
From: James Crawford
Date: 1/4/2016 3:46 PM (GMT-08:00)
To: sprinklerforum@lists.firesprinkler.org
Subject: Locker Rooms
We have always protected