23 sqft per head in a light hazard corridor should be enough. With 7 psi
you have a 0.66 density. The skylight section is poorly written. We ran
into a project with four 2'x2' skylights two feet apart. The letter of
the standard would require a head in each but we left them out and the
AHJ didn't
You need to discuss the issue with the AHJ but go armed with some
ammo (such as why the 10 ft requirement is there). I did an article
for the NFPA Journal in 2004 discussing just this issue (a copy is on
our web site, link is below).
http://www.firesprinkler.org/techservices/articles/
Excellent! Thank you, Roland.
Margaret
--- Roland Huggins [EMAIL PROTECTED] wrote:
You need to discuss the issue with the AHJ but go
armed with some
ammo (such as why the 10 ft requirement is there).
I did an article
for the NFPA Journal in 2004 discussing just this
issue (a copy