RE: PVC FOR INCOMING SERVICE SUPPLY

2016-03-24 Thread Larry Keeping
l Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of craig.pr...@ch2m.com Sent: March-24-16 2:24 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: PVC FOR INCOMING SERVICE SUPPLY The problem with PVC or any non-metallic pipe is that if the

RE: PVC FOR INCOMING SERVICE SUPPLY

2016-03-24 Thread Craig.Prahl
om: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Parsley Consulting Sent: Thursday, March 24, 2016 11:56 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: PVC FOR INCOMING SERVICE SUPPLY Cesar, If I read your inquiry correctly the data you need is

Re: PVC FOR INCOMING SERVICE SUPPLY

2016-03-24 Thread Parsley Consulting
Cesar, If I read your inquiry correctly the data you need is most likely in FM Global Data Sheet 3-10, in Table 1. It looks as though they don't make a distinction in that data sheet based on the type of occupancy. *Ken Wagoner, SET *Parsley Consulting*** *350 West 9th Avenue, Suite 206 *E

RE: PVC FOR INCOMING SERVICE SUPPLY

2016-03-24 Thread Reed A. Roisum, SET
Cesar, All I could find was in FMDS 3-10... 2.1.2. Fire Service Mains 2.1.2.1 General 2.1.2.1.1 Use Approved underground pipe, joints and fittings for fire service mains. Acceptance of pipe, joints and fittings that are not Approved is based on satisfactory experience and conformity to specific