l Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of craig.pr...@ch2m.com
Sent: March-24-16 2:24 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: PVC FOR INCOMING SERVICE SUPPLY
The problem with PVC or any non-metallic pipe is that if the
om: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Parsley Consulting
Sent: Thursday, March 24, 2016 11:56 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: PVC FOR INCOMING SERVICE SUPPLY
Cesar,
If I read your inquiry correctly the data you need is
Cesar,
If I read your inquiry correctly the data you need is most likely
in FM Global Data Sheet 3-10, in Table 1. It looks as though they don't
make a distinction in that data sheet based on the type of occupancy.
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*E
Cesar,
All I could find was in FMDS 3-10...
2.1.2. Fire Service Mains
2.1.2.1 General
2.1.2.1.1 Use Approved underground pipe, joints and fittings for fire service
mains. Acceptance of pipe, joints
and fittings that are not Approved is based on satisfactory experience and
conformity to specific