Re: Stage's

2008-04-24 Thread Garth W. Warren
It will also require either a fire-rated curtain or proscenium sprinklers. There is actually a lot more to that. It will also require a fire-rated curtain "that is always kept down in the closed position except for rehearsals and performances" OR proscenium sprinklers. Keep the expensive fi

RE: Stage's

2008-04-23 Thread Todd Williams - FPDC
, April 23, 2008 8:54 AM To: sprinklerforum@firesprinkler.org Subject: RE: Stage's It will also require either a fire-rated curtain or proscenium sprinklers. Steve Leyton Protection Design & Consulting -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Beh

RE: Stage's

2008-04-23 Thread Mark Sornsin
EMAIL PROTECTED] -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Gary Stites Sent: Wednesday, April 23, 2008 5:04 PM To: sprinklerforum@firesprinkler.org Subject: RE: Stage's Can some please define: Legitimate Stage Stage Platform Thank you Gary S

RE: Stage's

2008-04-23 Thread Gary Stites
- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton Sent: Wednesday, April 23, 2008 8:54 AM To: sprinklerforum@firesprinkler.org Subject: RE: Stage's It will also require either a fire-rated curtain or proscenium sprinklers. Steve Leyton Protection Design & C

RE: Stage's

2008-04-23 Thread Steve Leyton
orum@firesprinkler.org Subject: RE: Stage's It's a stage, curtains, the whole works Brian Harris FDFP INC. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Matthew J. Willis Sent: Wednesday, April 23, 2008 9:31 AM To: sprinklerforum@firesprinkler.o

RE: Stage's

2008-04-23 Thread Steve Kowkabany
ston Sent: Wednesday, April 23, 2008 10:33 AM To: sprinklerforum@firesprinkler.org Subject: RE: Stage's Below are notes from a large church that we are doing. They came from the engineer. The stage is over 1000 sqft but less than 50' front to back. The said this keeps them form h

RE: Stage's

2008-04-23 Thread Andy Johnston
om: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of David Autry Sent: Wednesday, April 23, 2008 9:52 AM To: sprinklerforum@firesprinkler.org Subject: RE: Stage's Maybe your thinking, a regular stage over 1000 sq.ft. and all legitimate stages are required to have a 1 1/2" hose on bo

RE: Stage's

2008-04-23 Thread Brian Harris
Bingo, that's it, I was just reading 101. Thanks Brian Harris FDFP INC. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of David Autry Sent: Wednesday, April 23, 2008 9:52 AM To: sprinklerforum@firesprinkler.org Subject: RE: Stage's Maybe you

RE: Stage's

2008-04-23 Thread John Drucker
Sent: Wednesday, April 23, 2008 10:03 AM To: sprinklerforum@firesprinkler.org Subject: RE: Stage's Then perhaps the number you are trying to remember is 1000 Sq. Ft.? If it is over 1000, then the standpipe starts.. R/ Matt Matthew J. Willis Living Water Fire Protection, LLC. 1160 McKenzie

RE: Stage's

2008-04-23 Thread Matthew J. Willis
] - >-Original Message- - >From: [EMAIL PROTECTED] - >[mailto:[EMAIL PROTECTED] On - >Behalf Of Brian Harris - >Sent: Wednesday, April 23, 2008 8:39 AM - >To: sprinklerforum@firesprinkler.org ----- >Subject: RE: Stage's - > - >I

RE: Stage's

2008-04-23 Thread Matthew J. Willis
ECTED] - >-Original Message- - >From: [EMAIL PROTECTED] - >[mailto:[EMAIL PROTECTED] On - >Behalf Of Ray Vance - >Sent: Wednesday, April 23, 2008 8:51 AM - >To: sprinklerforum@firesprinkler.org - >Subject: RE: Stage's - > - &

RE: Stage's

2008-04-23 Thread Joe Powell
IBC would require hose valves in a stage in excess of 1000 s.f. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris Sent: Wednesday, April 23, 2008 8:56 AM To: sprinklerforum@firesprinkler.org Subject: Stage's I'm working on a school that has a p

RE: Stage's

2008-04-23 Thread David Autry
1-9659 402-471-3118 fax www.sfm.ne.gov -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris Sent: Wednesday, April 23, 2008 8:39 AM To: sprinklerforum@firesprinkler.org Subject: RE: Stage's It's a stage, curtains, the whole works B

RE: Stage's

2008-04-23 Thread Reed Roisum
If a water curtain is required for the proscenium opneing the design criteria is in 11.3.3. Reed A. Roisum Fire Protection Technician NICET Level III   Ulteig Engineers, Inc. 3350 38th Avenue South Fargo, ND 58104-7079   Direct Number: 701.280.8580 Mobile: 701.212.8810 Main Office: 701.280.8500

RE: Stage's

2008-04-23 Thread Brian Harris
It's a stage, curtains, the whole works Brian Harris FDFP INC. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Matthew J. Willis Sent: Wednesday, April 23, 2008 9:31 AM To: sprinklerforum@firesprinkler.org Subject: RE: Stage's Is it a

RE: Stage's

2008-04-23 Thread Ray Vance
- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Matthew J. Willis Sent: Wednesday, April 23, 2008 9:31 AM To: sprinklerforum@firesprinkler.org Subject: RE: Stage's Is it a stage or a Platform? R/ Matt Matthew J. Willis Living Water Fire Protection, LLC. 1160 McKenzie

RE: Stage's

2008-04-23 Thread Brian Harris
ehalf Of [EMAIL PROTECTED] Sent: Wednesday, April 23, 2008 9:26 AM To: sprinklerforum@firesprinkler.org Subject: Re: Stage's What are your applicable codes? There are special considerations for stages in IBC, NFPA 101, NFPA 5000 . . . smoke control, roof vents, and other items. What i

RE: Stage's

2008-04-23 Thread Matthew J. Willis
Is it a stage or a Platform? R/ Matt Matthew J. Willis Living Water Fire Protection, LLC. 1160 McKenzie Rd. PO Box 877 Cantonment, FL. 32533 850-937-1850 Voice 850-937-1852 Facsimile [EMAIL PROTECTED] - >-Original Message- - >From: [EMAIL PROTECTED] - >[mailto:[EMAIL PROTE

Re: Stage's

2008-04-23 Thread Andrew . Weisfield
PROTECTED] 04/23/2008 10:14 AM Please respond to sprinklerforum@firesprinkler.org To cc Subject Re: Stage's there are also requirements in 101 and 1. Garth - Original Message - From: "Brian Harris" <[EMAIL PROTECTED]> To: Sent: Wednesday, April 23, 2008 8:5

Re: Stage's

2008-04-23 Thread Garth W. Warren
there are also requirements in 101 and 1. Garth - Original Message - From: "Brian Harris" <[EMAIL PROTECTED]> To: Sent: Wednesday, April 23, 2008 8:56 AM Subject: Stage's > I'm working on a school that has a pretty big stage, I could have sworn I > read something about special consider