gt; and metal in metal and glass cases) and got nowhere.
> >
> >
> >
> >
> >
> >
> >
> > >
> > > On Oct 9, 2020 at 5:20 PM, > sprinklerforum@lists.firesprinkler.org)> wrote:
> > >
> > >
> > >
> > >
d metal in metal and glass cases) and got nowhere.
>
>
>
>
>
>
>
> >
> > On Oct 9, 2020 at 5:20 PM, sprinklerforum@lists.firesprinkler.org)> wrote:
> >
> >
> >
> > Is there any world where a small pharmacy - say 1000 sq ft - could b
Cell : 919-268-7587
> Email : philli...@pyebarkerfire.com
> Web : www.pyebarkerfire.com
>
>
> From: Sprinklerforum on
> behalf of Travis Mack via Sprinklerforum
>
> Sent: Friday, October 9, 2020 8:11:06 PM
> To: sprinklerforum@lists.firesprinkler.org
Cc: travis.m...@mfpdesign.com
Subject: Re: pharmacy
[EXTERNAL]
This is a pharmacy area in a medical office building. There is really no way it
could be less than OH2 that I can see, either.
Travis Mack, CFPS, CWBSP, RME-G, SET
Engineering Manager
MFP Design
3356 E Vallejo Ct
Gilbert, AZ 85298
This is a pharmacy area in a medical office building. There is really no way it
could be less than OH2 that I can see, either.
Travis Mack, CFPS, CWBSP, RME-G, SET
Engineering Manager
MFP Design
3356 E Vallejo Ct
Gilbert, AZ 85298
NEW EXTENSION: 480-505-9271 ext. 700
NEW MOBILE: 480-272-2471
director, author, actor and opera
director (1942-)
On Fri, Oct 9, 2020 at 2:20 PM Travis Mack via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:
> Is there any world where a small pharmacy - say 1000 sq ft - could be
> considered light hazard? The plans show racks for
ere any world where a small pharmacy - say 1000 sq ft - could be
> considered light hazard? The plans show racks for the storage of the meds /
> pill bottles. Dealing with some issues on a pre-engineered job that the FPE
> did it as LH. The problem compounds when the water supp
n.com
Subject: pharmacy
Is there any world where a small pharmacy - say 1000 sq ft - could be
considered light hazard? The plans show racks for the storage of the meds /
pill bottles. Dealing with some issues on a pre-engineered job that the FPE
did it as LH. The problem compounds when the
Is there any world where a small pharmacy - say 1000 sq ft - could be
considered light hazard? The plans show racks for the storage of the meds /
pill bottles. Dealing with some issues on a pre-engineered job that the FPE
did it as LH. The problem compounds when the water supply is very