pressure relief valve

2009-01-23 Thread douglas hicks
I was called to look a leaking riser. I got on the job site and found a Tyco Model 513 Test and Drain with a pressure relief valve. I think the pressure relief valve is leaking. The main drain outlet is wet and the sight glass is obscured with rust. Their are a total of 5 wet risers, all

pressure relief valve

2009-01-23 Thread å . . . . . . .
douglas hicks if the riser feeds a gridded system, you should not remove the pressure relief valve. if there is a remote inspector´s test, it is possible to suck most of the air out of the system via this valve. If this is done on a cold day, and there are no air pockets in the pipe, then on

RE: Hodgman Sprinklers

2009-01-23 Thread Bobby Gillett
Thanks, we just wanted to show him the cut sheet on that one. We just happened to be here doing repair at the same time he was around and he questioned it. We just happened to be the lucky ones to be in the right place at the right time!? It makes me wonder if the availability of a sprinkler

Re: pressure relief valve

2009-01-23 Thread Cherokeefirepro
Just replace it. Forest Wilson --Original Message-- From: douglas hicks Sender: sprinklerforum-boun...@firesprinkler.org To: sprinkler board ReplyTo: sprinklerforum@firesprinkler.org Subject: pressure relief valve Sent: Jan 23, 2009 2:41 AM I was called to look a leaking riser. I got

1.2 Leg of Remote Area

2009-01-23 Thread å . . . . . . .
i learn more here than most seminars. i welcome getting shot down here, rather on submitted paper. if my ideas get shot down, my reputation will get bruised. i am not my ideas (buddhist kharma notwithstanding) ideas need to make it on their own merit -- regardless of who says it. so with

RE: pressure relief valve

2009-01-23 Thread George Church
You can't just remove them - be serious. If pressure is over the factory setting, then a REPLACEMENT of the 300# adjustable model is available and you crank it down to 200 PSI and end the drip. glc -Original Message- From: sprinklerforum-boun...@firesprinkler.org

Re: pressure relief valve

2009-01-23 Thread vince
Gridded system? From: douglas hicks fire...@eoni.com To: sprinkler board sprinklerFORUM@firesprinkler.org Sent: Friday, January 23, 2009 2:41:35 AM Subject: pressure relief valve I was called to look a leaking riser.  I got on the job site and found a Tyco

Re: pressure relief valve

2009-01-23 Thread douglas hicks
Good morning George. The tag on the pressure relief valve says 175 PSI, I only saw one part number on the Tyco site. The pressure valve did not look adjustable. Douglas Hicks General Fire Equipment Co of Eastern Oregon, Inc - Original Message - From: George Church for...@ptd.net To:

RE: pressure relief valve

2009-01-23 Thread G. Tim Stone
Pressure relief Valves are required on Gridded Pipe Systems only. G. Tim Stone NICET Level III Engineering Technician Fire Protection Sprinkler Design and Consulting Services 117 Old Stage Rd. - Essex Jct., VT. 05452 TEL: (802) 434-2968 Fax: (802) 434-4343

RE: pressure relief valve

2009-01-23 Thread John Denhardt
Not currently but maybe for 2010. John John August Denhardt, P.E. Strickland Fire Protection Incorporated 5113 Berwyn Road College Park, Maryland 20740 Office Telephone Number: 301-474-1136 Mobile Telephone Number: 301-343-1457 FIRE SPRINKLERS SAVE LIVES -Original Message- From:

RE: pressure relief valve

2009-01-23 Thread Jamie Seidl
You can replace with a watts PRV. http://www.watts.com/pro/_productsFull_tree.asp?catId=64parCat=293pid=803ref=2 I put one on a system in my house and had to run it down pretty far to get it to stop relieving at 140 lbs system pressure. The springs see to lose tension over time.

pressure relief valve

2009-01-23 Thread Jay Stough
We had a similar problem with an AGF test drain and learned that the 175 is real accurate. It can start releasing pressure at around 155 to 190. We replaced it with a 190 or 195 psi per their recommendation and the problem was solved. I think they said the accuracy had to do with the spring

RE: pressure relief valve

2009-01-23 Thread George Church
The cheap ones aren't adjustable, preset for about 175. And on our high pressure storage jobs, with working pressure in the 165-185 PSI range, these would p all the time, so we use the 100-300 adjustable ones and adjust them to 200 +/-. If you're wondering why we're comfortable with up to 185,

water test location

2009-01-23 Thread Todd Williams
I did a flow test a couple of days ago on an underground main that had recently been looped. There is a main that feeds a hydrant and sprinklers to the building at the end of the loop. I flowed the hydrant and read the pressures off the first test port on the backflow preventer (before any

RE: water test location

2009-01-23 Thread Dewayne Martinez
I was taught that you had to flow past your gauge hydrant to get the proper results so I would agree with the contractor. Your scenario is like a dead end main with your gauge on the last hydrant if I am interpreting it correctly. -Original Message- From:

RE: water test location

2009-01-23 Thread Todd Williams
The problem is that you have the loop, then the hydrant, then the lead-in to the sprinkler system, then the end of the main. No other realistic way to do it. At 10:36 AM 1/23/2009, you wrote: I was taught that you had to flow past your gauge hydrant to get the proper results so I would agree

RE: Boat Storage

2009-01-23 Thread Jim Davidson
When working for a client with similar type of boat rack storage, we looked at using High Expansion Foam when reviewing with the manufacturer of the foam equipment and concentrate the manufacturers noted that high ex foam is not listed for the protection of boats in racks. Same problem with

RE: water test location

2009-01-23 Thread G. Tim Stone
Todd, Under those conditions you are justified to set up the way you described in you earlier email. I have had to set up gages inside existing building in the past. I believe your reading will still provide an accurate picture of the municipal system. G. Tim Stone NICET Level III Engineering

Re: Boat Storage

2009-01-23 Thread Roland Huggins
There are several items mentioned I'd likely to comment on. 1. As soon as someone shows me a hangar that stacks their planes in racks, I'll consider it as a starting point. 2. Fire modeling is not a useful tool for defining SUPPRESSION criteria. 3. Many racks also provide the roof

Re: pressure relief valve

2009-01-23 Thread Roland Huggins
the 2010 edition expanded this from just gridded systems to all wet- pipe systems Roland On Jan 23, 2009, at 3:41 AM, å... wrote: if the riser feeds a gridded system, you should not remove the pressure relief valve. ___ Sprinklerforum

RE: water test location

2009-01-23 Thread George Church
Obviously having two hydrants does not prohibit running a flow test accurately. What you did makes perfect sense and should give accurate flow and pressure data. Ask the contractor what he would do if he had a private tank, fire pump, a single hydrant and the sprinklered building as an

RE: Boat Storage

2009-01-23 Thread Matthew J. Willis
last racked marina fire I heard about could be seen from 20 miles away. Whrah Roland I would like to add to this.. Most of the pictures of the damage I found on these were taken from the air. Some of the secondary effects were across the bays, water not building type. R/ Matt Matthew J.

RE: water test location

2009-01-23 Thread Jim Johnston
Todd, I have never heard of testing this way, I have always used a minimum of two hydrants. On a looped system if you have the manpower or water usage isn't an issue use three hydrants taking the pressure readings from the middle hydrant. Do you have access to NFPA 291, this has some good

RE: water test location

2009-01-23 Thread George Church
Maybe I have Friday-it is, but what possible difference could it be to reading pressure at a point whether your gauge is attached to a hydrant, city side of a BFP as Todd did, or a hose bib on a house with another faucet cracked open to prevent their BFP from being closed? Its accurate measurement

RE: water test location

2009-01-23 Thread Dewayne Martinez
George, I thought that if you did not flow past your gauge hydrant that your residual reading would be off. Have I been wrong all these years? -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church

RE: pressure relief valve

2009-01-23 Thread Thom McMahon
Watts 530-C is adjustable. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf

RE: water test location

2009-01-23 Thread Thom McMahon
The best way I know of to accurately run this test is to flow a hyd. On one side of the loop main to the sprinkler system and gauge another hyd. On the other side of the sprinkler system conn. to the loop main. _A___T___B__ Where A is the flow hyd. Where B is

RE: Boat Storage

2009-01-23 Thread Thom McMahon
The message here is, DON'T GET TOO CLOSE! Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: water test location

2009-01-23 Thread George Church
You're not affected by the velocity pressure of the water going past your hydrant, that'd introduce errors -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Dewayne Martinez Sent: Friday, January 23, 2009 12:52

RE: water test location

2009-01-23 Thread Thom McMahon
Per edition 5 of the American Mutual Insurance Alliance Simplified water supply testing In testing a water system at a sprinklered plant, sometimes we can note the residual pressure from a gauge at the base of the nearest riser. This is not recommended as standard practice, but may be used when

RE: water test location

2009-01-23 Thread Todd Williams
Per edition 5 of the American Mutual Insurance Alliance Simplified water supply testing In testing a water system at a sprinklered plant, sometimes we can note the residual pressure from a gauge at the base of the nearest riser. This is not recommended as standard practice, but may be used when

RE: water test location

2009-01-23 Thread Ed Kramer
I'm with George on this one. The water doesn't care what piping configuration is used to connect the static/residual gauge to the system - be it a hydrant or a sprinkler riser. The 2nd hydrant is most common because (normally) it's the most convenient. I've had to do exactly as you described

RE: water test location

2009-01-23 Thread Ed Kramer
When taking the static/residual reading from a sprinkler riser, I think the effective point (the point the calcs should be taken back to) is the point where the non-flowing water meets the flowing water. If the public water main is looped, this would be where the sprinkler line ties into the